Pls help! Solar system dead for 2 months and nobody will help

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • oregon_phil
    Solar Fanatic
    • Jan 2019
    • 497

    #16
    otherchuck , we want to get to the point where you can describe the problem in a series statements that will help you and company C figure out root cause to your problem.

    For example.

    On January 1, 2018, Company A installed a 25 LG NeonR,LG350Q1C-A5 with P370 optimizers in a ground mount array 50 feet from my house. The 25 solar panels are installed as two strings, to a SolarEdge SE7600H inverter which is located at the ground mount array. Company A then ran AC wire from the inverter to my garage electrical panel with 40amp circuit breakers.

    On January 1, 2022, Company B removed SE 7600H inverter and installed a new SE7600H-USSNBBL14 inverter with LG Chem Resu 12 batteries. Company B moved the location of the inverter from the ground mount array to the exterior of my house. The LG Chem batteries (Date codes/serial numbers) are located next to the new inverter also on the exterior of my house.

    On November 22,2022, the system installed by Company B stopped working. The inverter shows a red LED and SetApp reports fault code 342.

    I understand all the statements above are false. You can start filling in the blanks.

    You want to figure out what you had, what you have now and what changed between then and now.
    Last edited by oregon_phil; 01-07-2023, 07:12 PM. Reason: Forgot to add problem timeline

    Comment

    • otherchuck
      Junior Member
      • Dec 2022
      • 21

      #17
      OP here again,

      davidcheok's comments were certainly illuminating. So Company B is on the hook for the whole system, even if the ground fault is in the panels which Company A installed 4 yrs ago (and which seem to have been installed in a competent fashion, though by now there may have been some glitch, but maybe only something like a loose connection)? The terse response we got got from Company B at first...basically "Not our fault, contact the guys who installed the panels"...seemed like they were pretty sure they were not responsible for faults in the system if they originated in panels that they didn't install.

      Thanks for all the support. Remarkably helpful forum! Before getting a third party to look into this, we will wait until (and I hate to have to add this but..."if") we have some discussion with CALSSA about all this. That might be a couple weeks, but I will report back.

      Otherchuck

      Comment

      • davidcheok
        Member
        • Dec 2022
        • 99

        #18
        Originally posted by otherchuck
        OP here again,

        davidcheok's comments were certainly illuminating. So Company B is on the hook for the whole system, even if the ground fault is in the panels which Company A installed 4 yrs ago (and which seem to have been installed in a competent fashion, though by now there may have been some glitch, but maybe only something like a loose connection)? The terse response we got got from Company B at first...basically "Not our fault, contact the guys who installed the panels"...seemed like they were pretty sure they were not responsible for faults in the system if they originated in panels that they didn't install.

        Thanks for all the support. Remarkably helpful forum! Before getting a third party to look into this, we will wait until (and I hate to have to add this but..."if") we have some discussion with CALSSA about all this. That might be a couple weeks, but I will report back.

        Otherchuck
        Company B is not 'on the hook' either. You are. B would be responsible for any issues arising from faults from the battery and inverter install but they cannot be responsible for the array installation. A good installer would have checked and doubled checked the array for issues first before installing the battery and inverter but since you said it was working for about 10 months, its unlikely there were any issues upon implementation. IMHO any rectification to the system now is a billable job. Any competent and certified installer can do the job of rectification but IMHO it should be company B since they were the ones who still hold responsibility of warranty of the battery/inverters otherwise you will be repeating the same problem. The moment B accepts the job to fix it, then they would assume responsibility of the entire system (up to a certain period as per T&C) when they get paid for it.

        Comment

        • otherchuck
          Junior Member
          • Dec 2022
          • 21

          #19
          OP here,

          Thank you so much for the clarification. Got it this time.

          Otherchuck

          Comment

          • mustardjo
            Member
            • Jan 2022
            • 31

            #20
            We are in a similar situation with a "barely performing system" and a company that will do nothing to help. We have filed a complaint with the Attorney General. If enough dissatisfied customers in Calif. do this perhaps Calif. Attorney General will take action...as the AGs in other states are doing to prevent this type of misrepresentation and fraud. We also filed a complaint with Calif. State Contractor's License Board. This is taking a long time. But ESP has been under investigation and we suspect their will be violations against them. Good Luck...we know how frustrating and maddening this is.

            Comment

            • Mike 134
              Solar Fanatic
              • Jan 2022
              • 423

              #21
              Since it's a ground mount don't tough anything but take a good hard look at all the wiring. Squirrels and mice love to chew the insulation off to use in their nests. Might find a burn mark where the wire touches the metal frame. All fixable by any decent electrician.

              Comment

              • otherchuck
                Junior Member
                • Dec 2022
                • 21

                #22
                OP here again, with a an update so sad it is almost hilarious.

                Filed a complaint with CALSSA around Jan 6th, but never got a response; no surprise here as I presumed they were a "do nothing" public relations arm of the solar power industry. Eventually got a guy from Company A to come out and check.

                Not sure what I said in this forum before but...to review...but Company A (original solar panels installers a few yrs ago) seems the lesser villain here. Primary villain here appears to be Company B, who installed batteries and new inverter a year or so ago. Company B, it turns out (wish we had known this before!), apparently has a particularly bad 'customer service' reputation in an industry famous for appalling 'customer service'. When the system went down in mid-November 2022, Company B said "Not our fault; anything before inverter we installed is Company A's responsibility." Okay, lets keep that claim in mind as we review the evidence included here.

                Company A representative drove an hr to our house and figured out the problem in about a nanosecond. See photos. First photo is the junction box as installed by Company A; wiring entry points at left and right of box, no problems for a few yrs. When Company B put in batteries, they put a wiring entry point into top of junction box. Uh oh. Where we live in southern California, USA, yes, its true, we barely get any rain. But we do get some. When company A rep came out, he removed the faceplate of the junction box and water poured out (second photo). It has been full of water for a few months (see third photo).

                So, courtesy of Company B's workmanship, the junction box that says "CAUTION SOLAR CIRCUIT" was full of water for a few months. I will repeat that with your permission: The junction box that says "CAUTION SOLAR CIRCUIT" was full of water for a few months. Hazardous at all? And yet Company B is licensed to install solar equipment in the State of California? Could my dog (a relatively bright Australian Shepherd) also get such a license? I am not a huge fan of gov't regulation of various industries, but...c'mon!...if ever there was an industry that deserved hardcore state regulation, it has got to be the solar power industry, right? I will be filing a complaint with another presumptuously "Do nothing" contractor's license agency (for California), and when I went to their site I noticed something telling: There is one button you click for all possible contractors licenses (minus one); so that portal was for pool contractors, auto repairs, plumbers, almost everybody. And there was a separate portal dedicated to just one type of contractor: Solar. Customer service so vile, they get there own complaint button. How is there not a class action suit brewing (or is there?)!

                Company A rep sent sharply worded communication with photos to Company B but we have had no response from Company B and don't expect one. Pretty sure they will say what they have said before: If the problem is before the inverter, its not our fault.

                Otherchuck

                PS: Any lawyers want a piece of this? Seems like an easy winner

                solar jbox orig.jpgemptied jbox v1.jpgdestroyed wiring jbox.jpg

                Attached Files

                Comment

                • DanS26
                  Solar Fanatic
                  • Dec 2011
                  • 981

                  #23
                  All of this because a weep hole was not drilled......jeez. Thanks for the update.

                  Whatever can go wrong.....will go wrong.

                  Rookie mistake totally avoidable.
                  Last edited by DanS26; 02-01-2023, 08:39 PM.

                  Comment

                  • davidcheok
                    Member
                    • Dec 2022
                    • 99

                    #24
                    Originally posted by otherchuck
                    OP here again, with a an update so sad it is almost hilarious.


                    Company A representative drove an hr to our house and figured out the problem in about a nanosecond. See photos. First photo is the junction box as installed by Company A; wiring entry points at left and right of box, no problems for a few yrs. When Company B put in batteries, they put a wiring entry point into top of junction box. Uh oh. Where we live in southern California, USA, yes, its true, we barely get any rain. But we do get some. When company A rep came out, he removed the faceplate of the junction box and water poured out (second photo). It has been full of water for a few months (see third photo).


                    solar jbox orig.jpgemptied jbox v1.jpgdestroyed wiring jbox.jpg
                    Correct way to connect to the junction box should be from underneath, not sides and especially not above. I suggest having that redone properly and resealed.

                    What's important here is the issue is resolved. Lessons learnt. Enjoy the working system.

                    Comment

                    • Mike 134
                      Solar Fanatic
                      • Jan 2022
                      • 423

                      #25
                      Thanks for returning to the forum and posting the resolution to your troubles

                      Comment

                      • peakbagger
                        Solar Fanatic
                        • Jun 2010
                        • 1566

                        #26
                        I agree thanks to the OP for the update. I hope we helped?

                        I wonder if there is licensing board in CA that would be interested in photos.

                        It's not just rookies, I was involved with combined heat and power project installed in industrial plant last year. Sprinkler lines, steam lines, hot and cold water lines all running in the ceiling above the controls cabinet (Gasketed FRP enclosure). They ran conduit down through the top with mechanical bushings (not watertight). A line let loose above the enclosure and soaked the interior of the panel including the PLC and all the IO along with several "brains" for field installed transmitters. Once dried out most of the PLC started working but any warranty is null and void. The replacement components which used to be off the shelf are now backordered a year>

                        Comment

                        • azdave
                          Moderator
                          • Oct 2014
                          • 778

                          #27
                          Originally posted by otherchuck
                          PS: Any lawyers want a piece of this? Seems like an easy winner
                          Lawyers? How much money you got to burn? They won't really be interested unless someone was killed or injured.

                          My recommendation is get it fixed and let it go. You don't need that stress in your life and besides, it's highly unlikely it will ever be resolved to your full satisfaction. Why keep dragging it out since you already know you will get little traction from further complaints. I seriously doubt anyone in authority over these installers is going to get excited about some moisture in a splice box that caused a ground fault. They will give you lip service at best.

                          Dave W. Gilbert AZ
                          6.63kW grid-tie owner

                          Comment

                          • MGE
                            Solar Fanatic
                            • Feb 2013
                            • 152

                            #28
                            OP glad you wound out the problem, or the cause of it hopefully.

                            Im sure it doesn't need to be said but drill a small weep hole in the bottom and properly check ALL fittings penetrating into the j-box and make sure they have the proper sealing devices if needed.

                            Looks like a raintite fitting is used for the EMT on the top, maybe the hole is improperly sized allowing water to enter.

                            Quick fix is replace that box with a WP 2 gang box with the correct sized hubs and reconnect and make sure cover is secure and your good to go.
                            You could drill a small hole in that too but probably not necessary.

                            I would check EVERY box or connection in this entire system.
                            One mistake could be more.

                            Comment

                            • davidcheok
                              Member
                              • Dec 2022
                              • 99

                              #29
                              I think that pipe on the side that goes underground may have water inside. If the box was full of water, the excess would have gone down into that pipe. If and when you get the box done up, may want to dig that pipe out and make sure its dry.

                              Comment

                              • otherchuck
                                Junior Member
                                • Dec 2022
                                • 21

                                #30
                                OP again.

                                Yes, davidcheok, you are correct about water in the pipe coming from the junction being filled with water (see photo). The guy from Company A discovered this when he was out here, but my wife tells me (I wasn't home) he didn't seemed worried about this (tho he was worried about the flooded junction box). Should I remove that water? Any idea how I can do that?

                                My wife handles most communication with these people because she is far more diplomatic than I am (I am 'bad cop' and she is 'good cop'). But she did send out a sternly worded email yesterday, and in response, Company B said they will send someone out on Feb 10th. I am inclined to assume they will cancel that appointment, but in the event they do send someone out, I would love to be armed with as much relevant "safety code" info as possible. For instance, if they say "Oh, its okay to leave standing water in that pipe," I would love to be able say "Really? Because Section 3.1.4, subsection D of California's solar installation safety codes says the wires should not be submerged indefinitely in water."

                                So if any of y'all here who are conversant with relevant safety codes (including type of junction box and where wires may enter), please PLEASE feel free to arm me with all kinds of relevant info I can share with Company B, who I feel certain will otherwise hope to skip by with another crap job. I presume codes vary by state, but since I live in California, I presume our applicable safety codes are as strict or more strict than any other states.

                                Otherchuck

                                water in pipe smaller.jpg
                                Attached Files