The NEC rule 705.12-3 states "The sum of 125% of the power source(s) output circuit current and the rating of the overcurrent device shall not exceed the ampacity of the busbar!''
Fair enough with buts! If the added current is located opposite the end of where the bus bars connect to the main breaker, the direction of the current flowing into the bus bar will be opposite in direction of that originating from the main breaker. Those currents are opposite (negatively adds) to that originating from the main breaker.
I believe the rule is fine, it is the interpretation that is faulty. As to a 40 ampere breaker, supposedly the maximum size for solar currents connecting to your 200 ampere panel. It only depends on where in the panel it is connected,
Fair enough with buts! If the added current is located opposite the end of where the bus bars connect to the main breaker, the direction of the current flowing into the bus bar will be opposite in direction of that originating from the main breaker. Those currents are opposite (negatively adds) to that originating from the main breaker.
I believe the rule is fine, it is the interpretation that is faulty. As to a 40 ampere breaker, supposedly the maximum size for solar currents connecting to your 200 ampere panel. It only depends on where in the panel it is connected,