Anyone have experience with these "solar assisted" air conditioner/mini split?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • neweclipse
    Solar Fanatic
    • Aug 2015
    • 118

    #16
    Originally posted by bcroe

    No doubt there is an exception somewhere. COP of course IS NOT on the label, but can
    often be found with a little research. I would not risk buying some energy inefficient unit,
    that refused to admit (because they are so bad) what the performance numbers were.

    Just maybe, you could figure them out for yourself by comparing power input and BTU out.
    1 KWH = 3412.142 BTU Bruce Roe
    Let's pretend this is a consumers conversation and leave out the upper level engineering facts.

    Low SEER=Bad...High SEER=Good... ...runs there about 13 up to 37 currently...COP does pretty much the same too as for Low to High, from 1 going up never surpassing 3 maybe???

    (S)EER will get a consumer were he needs to be...anybody so inclined can have at it, and go nuts with their math and text books.
    Last edited by neweclipse; 07-12-2019, 01:29 PM.

    Comment

    • neweclipse
      Solar Fanatic
      • Aug 2015
      • 118

      #17
      If one wants to hit the real high COP like say 6 plus, then look at solar assisted ground source heat pumps another form of geothermal.(SGSHP)
      But I'm afraid that will bring out the math and text books...
      Last edited by neweclipse; 07-12-2019, 02:09 PM.

      Comment

      • bcroe
        Solar Fanatic
        • Jan 2012
        • 5209

        #18
        Ha I remember my 1972 AC was 8 SEER, last I heard still in service on a very light load. Geo thermal
        was the obvious electric winner way back. Fine for a clean sheet brand new build. I looked at it a lot
        in 2014, but it would be difficult to fit into this hilly homestead. The the cost was large, there was no
        opportunity for DIY style savings, and it would take the rest of my life working to get the lawn repaired
        back to the way it was. There is an additional problem, the thermal sink is limited, and it can freeze up
        and quit on a long, cold winter. Then you are back to resistance heating, your SEER in the dumpster.
        A sink big enough to entirely avoid this doubles the cost again. And there is the plumbing issue of
        fluids and maintaining all those pipes, which will not last a lifetime.

        When the current mini splits came out, they offered solutions to a whole list of my problems. They could
        compete directly with geo thermal efficiency, and with my DIY input were far cheaper, could be tested
        and then increased in total capacity, in installments. They will never freeze the ground solid, and my
        latest claims heat to - 25F outside. I really liked decentralizing HVAC, so a single failure (like my blower
        motor I replaced this month) cannot leave me in desperate straits. There are more advantages, also
        some minor negatives will be described another time.

        I noted some dual powered units listed a COP well above the 4 I look for. This I see as a rating
        standardization problem. They are not using an amazing compressor to get a COP of 6, they are
        comparing BTU out to line power in and ignoring the panel power input. Not a fair rating. Bruce Roe

        FurnBlower.JPG
        Last edited by bcroe; 07-12-2019, 03:45 PM.

        Comment

        • J.P.M.
          Solar Fanatic
          • Aug 2013
          • 15015

          #19
          Originally posted by neweclipse
          This thread title is air conditioning and mini-splits...all mini-splits are NOT heat pumps either.

          No consumer Label for an air conditioner or A/C only mini-split will revel a listed C.O.P., but engineers sure would get a chub if the label did.

          That about sums that up...
          Of course a consumer label won't show a C.O.P. - it's not required by law, so they don't bother. But C.O.P. was around a longtime before all the dumbed down EER came on the scene and was quite adequate until people got stupid. You want reality in comparing efficiency of HVAC equipment use C.O.P. , multiply by 3.412 for EER if it makes you feel better and don't waste time with SEER which is simply no more than smoke & mirrors.

          Comment

          • neweclipse
            Solar Fanatic
            • Aug 2015
            • 118

            #20
            Originally posted by bcroe
            Ha I remember my 1972 AC was 8 SEER, last I heard still in service on a very light load. Geo thermal
            was the obvious electric winner way back. Fine for a clean sheet brand new build. I looked at it a lot
            in 2014, but it would be difficult to fit into this hilly homestead. The the cost was large, there was no
            opportunity for DIY style savings, and it would take the rest of my life working to get the lawn repaired
            back to the way it was. There is an additional problem, the thermal sink is limited, and it can freeze up
            and quit on a long, cold winter. Then you are back to resistance heating, your SEER in the dumpster.
            A sink big enough to entirely avoid this doubles the cost again. And there is the plumbing issue of
            fluids and maintaining all those pipes, which will not last a lifetime.

            When the current mini splits came out, they offered solutions to a whole list of my problems. They could
            compete directly with geo thermal efficiency, and with my DIY input were far cheaper, could be tested
            and then increased in total capacity, in installments. They will never freeze the ground solid, and my
            latest claims heat to - 25F outside. I really liked decentralizing HVAC, so a single failure (like my blower
            motor I replaced this month) cannot leave me in desperate straits. There are more advantages, also
            some minor negatives will be described another time.

            I noted some dual powered units listed a COP well above the 4 I look for. This I see as a rating
            standardization problem. They are not using an amazing compressor to get a COP of 6, they are
            comparing BTU out to line power in and ignoring the panel power input. Not a fair rating. Bruce Roe

            Your application is admirable, but your horror stories are just that...horror stories. There are many geo system out there working flawlessly but then nobody "Chirps" about any of that...
            Been a DIY GSHP guy for 25 years. It's pretty simple with a drilled water well and a drain field for discharge. Ground water has none of your negative talking points. It's referred to as a "Pump and Dump" system and the pipes are never an issue. Ground water with it's constant temperature will beat any outdoor air temperature for COP...cannot pump heat that is NOT there...

            Comment

            • NochiLife
              Member
              • Jun 2019
              • 63

              #21
              Originally posted by bcroe
              I noted some dual powered units listed a COP well above the 4 I look for. This I see as a rating
              standardization problem. They are not using an amazing compressor to get a COP of 6, they are
              comparing BTU out to line power in and ignoring the panel power input. Not a fair rating. Bruce Roe
              Could you please clarify the difference between "line power in" and "panel power input"?
              I understand that "SEER" ratings are rather baseless, as "seasons" change based on where you're located. Conversely, an EER is based on "power used" vs "work done" (then there's the fun of BTU/W EER ratings vs. W/W EER ratings, with vastly different numbers). I am aware that the power usage at the rated output is generally less than the MAXIMUM possible power usage (is that what you mean by "panel power input"?), but most mini-split units can also produce more than their rated BTU/hr (at a significant loss of efficiency).

              Comment

              • bcroe
                Solar Fanatic
                • Jan 2012
                • 5209

                #22
                Originally posted by neweclipse


                Your application is admirable, but your horror stories are just that...horror stories. There are many geo system out there working flawlessly but then nobody "Chirps" about any of that...
                Been a DIY GSHP guy for 25 years. It's pretty simple with a drilled water well and a drain field for discharge. Ground water has none of your negative talking points. It's referred to as a "Pump and Dump" system and the pipes are never an issue. Ground water with it's constant temperature will beat any outdoor air temperature for COP...cannot pump heat that is NOT there...
                I had no intention of discussing a pump and dump system. I have little knowledge of
                them, do not approve of the idea, it was NOT offered to me in 2014 for my own well and
                septic, not sure it is even legal here, but saw one a few miles from here. My comments
                are on closed loop fluid systems only. And what COP have you seen over 25 years?

                Heat is everywhere there is matter. Bruce Roe
                Last edited by bcroe; 07-12-2019, 10:15 PM.

                Comment

                • bcroe
                  Solar Fanatic
                  • Jan 2012
                  • 5209

                  #23
                  Originally posted by NochiLife

                  Could you please clarify the difference between "line power in" and "panel power input"?
                  I understand that "SEER" ratings are rather baseless, as "seasons" change based on where you're located. Conversely, an EER is based on "power used" vs "work done" (then there's the fun of BTU/W EER ratings vs. W/W EER ratings, with vastly different numbers). I am aware that the power usage at the rated output is generally less than the MAXIMUM possible power usage (is that what you mean by "panel power input"?), but most mini-split units can also produce more than their rated BTU/hr (at a significant loss of efficiency).
                  By dual powered Mini Splits, I was referring to those with some combination of
                  solar panel power input, AC line input, and battery such as 48V input.

                  I expect the equipment to deliver the efficiency rating at maximum power, and
                  somewhere approaching the rating at lessor output. I do NOT expect more BTU
                  delivery than the output rating, keep in mind more BTUs are moved at the load
                  in heat mode than in cooling mode. Bruce Roe
                  Last edited by bcroe; 07-13-2019, 10:37 AM.

                  Comment

                  • NochiLife
                    Member
                    • Jun 2019
                    • 63

                    #24
                    bcroe Thanks for the clarification; I fully understand now. Using solar power does not magically increase the efficiency of the unit.

                    Comment

                    • Gilligan
                      Member
                      • Nov 2013
                      • 53

                      #25
                      Originally posted by NochiLife
                      bcroe Thanks for the clarification; I fully understand now. Using solar power does not magically increase the efficiency of the unit.
                      I'm not doubting what you are saying but YMGI says something else. I honestly don't know anything about any of this so I'm not saying anything one way or another, just presenting what I'm reading.
                      Attached Files

                      Comment

                      • bcroe
                        Solar Fanatic
                        • Jan 2012
                        • 5209

                        #26
                        Originally posted by Gilligan
                        I'm not doubting what you are saying but YMGI says something else. I honestly don't know anything about
                        any of this so I'm not saying anything one way or another, just presenting what I'm reading.
                        That is just another example of what I said before. Look at all SEER with no panels, they are fixed
                        numbers. But the last one is all over a range, because the panel power they are NOT COUNTING
                        can vary so much. Then look above at EER, there is no line for panels, because the COP really
                        does not care where the energy comes from.

                        Not a true picture, better standard methods needed. Bruce Roe

                        Comment

                        • NochiLife
                          Member
                          • Jun 2019
                          • 63

                          #27
                          That little set of details proves the point by bcroe. Notice that they do NOT give you an EER for "with solar panels." SEER ratings are completely subjective, so what's a smidge of fudging the numbers?

                          Basically, SEER/EER is calculated by measuring the AC power draw vs BTU out. The problem is, they are NOT factoring in the power generated by the solar panels, and thusly, it appears like the air conditioner can be very efficient.
                          BUT...if you are paying for electric, and want to reduce your electric bill by using a "solar assisted" air conditioner, this is exactly what you want to get, and it will give you the equivalent of up to 40 SEER. If you do not have any solar at the moment, this might be a great way to "wet your feet" and whet your appetite for more solar, as you literally only need the air conditioner, and a couple of (properly rated) solar panels. (Note, however, that it will not function without AC power, even in full sun. Much like most grid-tie systems.)

                          To be technical, the air conditioner is not actually achieving 40 SEER...but if we ignore the power generated by the solar panels (leaving it out of the calculation), it can under full sun appear to be a 40 SEER unit. Interpretation of statistics is pretty much everything; if the solar power was factored into the equation, the SEER would not have such an extreme range (SEER 20 without, and up to SEER 40 with).

                          Comment

                          • Gilligan
                            Member
                            • Nov 2013
                            • 53

                            #28
                            So do you guys think it makes sense to get one of these systems and dedicate some panels to it.

                            VS.

                            Get a grid tie inverter and feed the system (even without net metering, as my system wouldn't be big enough to roll anything back yet) and get regular mini-splits with inverters?

                            I feel like the cost savings in the these (not needing an inverter) is attractive.

                            But then there is the waste of energy from the PV panels if I oversize it like I would probably do, so that even on cloudy days most of the energy is coming from the PV panels.

                            Comment

                            • bcroe
                              Solar Fanatic
                              • Jan 2012
                              • 5209

                              #29
                              Originally posted by Gilligan
                              So do you guys think it makes sense to get one of these systems and dedicate some panels to it.

                              VS.

                              Get a grid tie inverter and feed the system (even without net metering, as my system wouldn't be big enough to roll anything back yet) and get regular mini-splits with inverters?

                              I feel like the cost savings in the these (not needing an inverter) is attractive.

                              But then there is the waste of energy from the PV panels if I oversize it like I would probably
                              do, so that even on cloudy days most of the energy is coming from the PV panels.
                              My feeling is net metering is the best deal, no power wasted, and night backup. But
                              if you cannot arrange net metering, this will allow some savings, or take a lot of strain
                              off batteries. Bruce Roe