Electrical shock with wet panels
  • marcland
    • Feb 2015
    Hi all,
    I am an integrator of Solar panels.
    I had problems in 2 of my installations with getting shocked when touching the PV module glass when this one is wet and I am touching another surface.
    I would like to know if any one else had a similar problem and if this is normal.
    I would like to add that modules are grounded in the frame and in the negative pole,
    That is why you got shocked.
      Can you upload a line drawing that shows your grounding scheme? What kind of inverter is being used? At what point in the installation are you getting shocked? Ungrounded systems would be safer, but only newer inverters are designed to operate that way.
      • marcland
        • Feb 2015
        Hi,
        This happened in a system with SMA back up with SB and SI.
        The SB is 4000TL. Modules are grounded with normal grounding from the structure.
        Electrical wiring is protected with DC surges arresters.
        That happens only on when touching the glass not frame or other parts. It is like the electricity jumping through the glass. Electricity comes even through the water up to the hand.
          It is not possible for surge arrestors to protect any wiring.
            Why would you ground the DC- of this inverter? From the manual:
            6.4.2 Conditions for the DC Connection
            The inverter is transformerless
            and has no galvanic isolation.
            Therefore, the inverter may only be
            operated with ungrounded PV arrays.
              Wet glass can have electrical leakage along the conductive water path, dry glass is an insulator. But the bigger question is how it's happening. The DC connectors should be sealed, and not allow any leakage. This then indicates maybe the glass/frame seal is bad, and the moisture conducting from there. That would be VERY bad, and cause early panel failure.
              Another test, is to get a Neon light based tester, and see if the current is DC (one side of the bulb lights) or AC (both elements light) There is a chance that Induced AC is appearing on the panels - are there high voltage powerlines in the neighborhood ? I could on dry days, get a tingle from my car, when working on it, induced from the power lines across the street:ViewInstall_c.jpg
                If there is a conductive path from DC to ground, whether it was put there intentionally or it occurs by a bad glass seal and water providing continuity to the frame, shouldn't that trigger the inverter's GFDI?
                  Yes if it is wired correctly to code. That is what it is there for.
                    • 5209
                    The "GFI" detector in my inverters requires over 1A of leakage current for any response.
                    That is way beyond a safe level for personal. GFIs for people trigger at 0.005 A or less.
                    If you are getting a tickle from panels, there may indeed be faulty insulation there. But
                    as for my own hide, I always assume there is a fault and keep myself isolated from any
                    active elements of the system. Bruce Roe
                      Yeah, your Fronius's design doesn't give the same level of ground fault detection that the transformerless SMA's can achieve. A 30 mA change in current, or 100 mA absolute current, is enough to trigger it. Here is one of the presentations that discusses it from when the product was being launched.
                        • 5209
                        The Fronius perform well, but their Ground Fault technology is crude. I see it as quite
                        adequate for equipment faults, but not for people. That isn't an unusual situation in
                        powerful systems.
                        Detecting .030A DC before startup isn't so difficult. Detecting DC leakage in operation
                        is much more difficult, unlike the .005A AC detectors for people. I really wonder what
                        is the practical limit given that a huge array of outdoor equipment is going to have
                        leakage at some level?
                        Now I will need to set up an experiment to see just what my systems leakage is. I will
                        ground one terminal through a shunt (1K ohm resistor) and measure the shunt voltage,
                        then try it again grounding the other terminal instead. Will do East and West systems.
                        Bruce Roe
                          SolarEdge uses a detection technique similar to SMA, and also chose a 30 mA delta current as the trip threshold. This is a value in operation, not a start-up check. They report that changes as low as 15 mA may trip in some systems. Their default absolute level is 300 mA, but it can be set as low as 100 mA.
                            100 ma is considered lethal.
                              The amount of time exposed matters. The 30 mA delta trip level is what is designed for human safety. If your point is that the 1 A fuses on the Fronius and other grounded transformer based inverters will not prevent lethal fault current, I fully agree!