Third time lucky posting this, so I'll be very brief.
I have a system controlled by a TR0301 (Steca?)
It's supposed to kick in when the panel is 8K (same as 8C?) warmer than the tank, and stop pumping when the difference falls to 4K (or the target temp is reached).
It mostly works, apart from the 8K/4K temp difference. Instead, it seems to switch on and off very rapidly while the temperature is 4K different, i.e. while the panel is first warming up in the morning. Sometimes the switching on/off is happening every second or two, which is going to break the pump sooner or later.
Is this a fault? There are no fault indications, and the rest of the system seems to work fine.
Any ideas?
Thanks.
I have a system controlled by a TR0301 (Steca?)
It's supposed to kick in when the panel is 8K (same as 8C?) warmer than the tank, and stop pumping when the difference falls to 4K (or the target temp is reached).
It mostly works, apart from the 8K/4K temp difference. Instead, it seems to switch on and off very rapidly while the temperature is 4K different, i.e. while the panel is first warming up in the morning. Sometimes the switching on/off is happening every second or two, which is going to break the pump sooner or later.
Is this a fault? There are no fault indications, and the rest of the system seems to work fine.
Any ideas?
Thanks.