Tricky to accomplish since morning and evening will always see a drop in current.
So what can I expect to happen if I power a resistive DC load on a non-MPPT CC when the current drops, assuming I have matched the DC heater resistance (impedance) as you suggest?
Tgriff: Have you considered going back to a 24VAC T-stat energizing the coil of a power relay which would switch your DC voltage?
As BRoe said, there are some pretty robust power relays but they are AC coil. I just don't believe those SSR's are going to last no matter what the rating says.
You may need one power relay per PV panel b/c the following are only rated up to 28VDC:
https://www.automationdirect.com/adc...ad-pr40_series)
As for Solar Thermal, it works great if the system is designed properly and maintained well; most systems I've seen are neither.
i would recommend a DrainBack system to avoid many headaches associated with high temp and high pressure.
Control is the tricky part. Resol controllers are very reliable.
So what can I expect to happen if I power a resistive DC load on a non-MPPT CC when the current drops, assuming I have matched the DC heater resistance (impedance) as you suggest?
Tgriff: Have you considered going back to a 24VAC T-stat energizing the coil of a power relay which would switch your DC voltage?
As BRoe said, there are some pretty robust power relays but they are AC coil. I just don't believe those SSR's are going to last no matter what the rating says.
You may need one power relay per PV panel b/c the following are only rated up to 28VDC:
https://www.automationdirect.com/adc...ad-pr40_series)
As for Solar Thermal, it works great if the system is designed properly and maintained well; most systems I've seen are neither.
i would recommend a DrainBack system to avoid many headaches associated with high temp and high pressure.
Control is the tricky part. Resol controllers are very reliable.