  • inetdog
    Super Moderator
    • May 2012
    • 9909

    #16
    Originally posted by Wy_White_Wolf
    The inverter numbers as listed are grid tie only.

    WWW
    This one isn't:

    He also mentioned that there is a Sunny Boy inverter coming out which will provide power during outages, but only when the sun is out. It is a Sunny Boy 4000tl-us inverter
    SunnyBoy 3000 US, 18 BP Solar 175B panels.

    Comment

    • Wy_White_Wolf
      Solar Fanatic
      • Oct 2011
      • 1179

      #17
      Originally posted by inetdog
      This one isn't:
      But if you look at the systems he quoted that is not the inverter listed

      Comment

      • oakhilltop
        Junior Member
        • Oct 2012
        • 6

        #18
        Originally posted by Wy_White_Wolf
        But if you look at the systems he quoted that is not the inverter listed
        Just to clear things up.
        In one of my posts I said this.
        "He also mentioned that there is a Sunny Boy inverter coming out which will provide power during outages, but only when the sun is out. It is a Sunny Boy 4000tl-us inverter"

        I inquired about the upcoming inverter running the well pump, and the installer replied with
        "Depending on the needed inputs of the pump, the solar array in theory could power it. It sounds like it will be a dedicated outlet that will be powered when the grid is down."

        I had also asked if the pump needed a small buffer of batteries but he didn't address that issue. I don't think the installer wants to think much about any usage while the grid is down. Other than using the new inverter. So, I am on my own, or I may get a few more quotes from other installers. I have been debating whether to remove some trees for solar. I think we are going to remove them. We have been considering doing some of them even if we don't install PV panels. And I have a tree guy coming to do some other work in a few weeks. Once the trees are down, I can confirm that we qualify for the rebates. And if we do, I can pursue getting more quotes.

        Comment

        • inetdog
          Super Moderator
          • May 2012
          • 9909

          #19
          Originally posted by oakhilltop
          Just to clear things up.
          In one of my posts I said this.
          "He also mentioned that there is a Sunny Boy inverter coming out which will provide power during outages, but only when the sun is out. It is a Sunny Boy 4000tl-us inverter"

          I inquired about the upcoming inverter running the well pump, and the installer replied with
          "Depending on the needed inputs of the pump, the solar array in theory could power it. It sounds like it will be a dedicated outlet that will be powered when the grid is down."

          I had also asked if the pump needed a small buffer of batteries but he didn't address that issue. I don't think the installer wants to think much about any usage while the grid is down. Other than using the new inverter. So, I am on my own, or I may get a few more quotes from other installers. I have been debating whether to remove some trees for solar. I think we are going to remove them. We have been considering doing some of them even if we don't install PV panels. And I have a tree guy coming to do some other work in a few weeks. Once the trees are down, I can confirm that we qualify for the rebates. And if we do, I can pursue getting more quotes.

          So far, I don't think there is enough information available from SMA to answer your questions. Another forum post, from someone who had seen the prototype at a show, indicated that the power from the backup outlet was "limited". How that compares as an absolute number or a percentage of the rated grid tie output is unclear.
          My biggest concern for your case, other than the continuous power output would be the surge capacity of the backup mode. Can it handle the high starting current surge for your pump motor. No idea yet what the answer to that will be.

          I think that your installer is, like the rest of us, working from incomplete information and is unwilling to go out on a limb about what might work.
          SunnyBoy 3000 US, 18 BP Solar 175B panels.

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #20
            I think you will need batteries to supply the pump starting surge, or a huge PV array that will not "collapse" when the inverter needs to start the pump.
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • inetdog
              Super Moderator
              • May 2012
              • 9909

              #21
              Originally posted by inetdog
              So far, I don't think there is enough information available from SMA to answer your questions. Another forum post, from someone who had seen the prototype at a show, indicated that the power from the backup outlet was "limited". How that compares as an absolute number or a percentage of the rated grid tie output is unclear.
              A post from an SMA employee indicates that it is a separate 12Amp 120 volt output, same on all three of the inverters rather than proportional to the size of the basic inverter.
              No word on surge capability yet.
              SunnyBoy 3000 US, 18 BP Solar 175B panels.