    Mixing different gauge solar panel cables..

    I have a problem. Being completely new to solar power, I have already made my first big mistake. And I haven't even received all of my components yet !
    Any way, I ordered a solar panel, extension cables and a charge controller ( all from different sellers ). After I received my panel, I came to find out the panel has 12AWG output cables with MC4 connectors attached to them. The extension cables, which should arrive any day, are 10AWG cables with MC4 connectors on one end only. Can these extension cables be used with this panel, or did I just totally waste $50 on cables I can't even use? The cables are non-returnable.
    I know I could buy another solar panel that has 10AWG output cables on it, but being completely new to solar energy I would rather not attempt a multi-panel system until I get a lot more experience with solar energy systems. Also, I don't have the money for another panel AND another set of extension cables ( to work with the panel I already bought ). I believe I can swing the cost of another set of cables, if I absolutely have to.
    Thanks for any help in this matter.
  • peakbagger
    Solar Fanatic
    • Jun 2010
    • 1566

    #2
    Dont worry about it. Unless you have multiple panels in series you are nowhere near the amperage capacity of the cables. There are online calculators for amperage.

    The typical installer buys one extension cable with connectors on both ends and then cuts it in half. You most likely paid for the privilege of someone cutting it in half for you. Unless you specified a connector setup, they will send you one male and one female extension cable.

    Make sure you get the polarities right and I hope you arent planning to tie into the grid with the setup you bought unless you go legit and get a permit. Power companies get quite grumpy about that and usually the low cost "grid tie " inverters arent certified for grid tie applications in the US.

    Comment

    • ReaderOfEyes
      Junior Member
      • Jun 2012
      • 3

      #3
      Mixing different gauge solar panel wires......

      My only concern in this matter is whether or not the two different gauge cables can be connected together and run to my controller without messing up the solar panel or the controller. I don't know if you can run a 10 gauge wire off of a 12 gauge wire without messing anything up or causing a voltage loss or anything like that.
      I don't know if it matters, but the panel is a 100W with short circuit amperage of like 5.89A.
      Also, I don't intend to use this as a grid-tie system. I want it for powering some lights and small tools in a building that has no electric service.
      Thanks for any further advice.
      Have a great day.
      Last edited by ReaderOfEyes; 06-01-2012, 09:50 AM. Reason: Added some information.

      Comment

      • Ian S
        Solar Fanatic
        • Sep 2011
        • 1879

        #4
        Originally posted by ReaderOfEyes
        My only concern in this matter is whether or not the two different gauge cables can be connected together and run to my controller without messing up the solar panel or the controller. I don't know if you can run a 10 gauge wire off of a 12 gauge wire without messing anything up or causing a voltage loss or anything like that.
        I don't know if it matters, but the panel is a 100W with short circuit amperage of like 5.89A.
        Also, I don't intend to use this as a grid-tie system. I want it for powering some lights and small tools in a building that has no electric service.
        Thanks for any further advice.
        Have a great day.
        For the system setup you describe, I can see no problem with using the 10 gauge extension wires with the 12 gauge coming off the panel. The gauge or wire thickness is important in determining the amperage the wire can handle. 12 gauge wire can easily handle 6 A.

        Comment

        • Naptown
          Solar Fanatic
          • Feb 2011
          • 6880

          #5
          The # 10 cables you bought are absolutely fine. Bigger than may be necessary but will only improve performance (OK maybe very slightly)
          As long as the connectors click together which they will as both are MC4 you are good to go.
          NABCEP certified Technical Sales Professional

          [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

          [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

          [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

          Comment

          • ReaderOfEyes
            Junior Member
            • Jun 2012
            • 3

            #6
            Mixing different gauge solar panel cables....

            Thanks for the help, everyone. Now I can stop worrying about the cables and go back to being anxious to try out the system, after I get the rest of my components.
            I appreciate the information a lot.

            Comment

            • Aussiemike
              Solar Fanatic
              • Mar 2017
              • 137

              #7
              I know this is old but it also interests me and I would love to hear it further explained.
              Just to exaggerate what if you had a run of 30 feet of 6AWG and a run of 5 feet of 12AWG.
              Is there a formula to let me know the max amp for this line?
              Do I just assume the whole 35 feet is 12 AWG?
              Cheers Mike

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                The max amp, is 20A, because that's what 12ga is rated for. For ohmic electrical loss, you add the resistance from the 6ga & 12ga lengths
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • Aussiemike
                  Solar Fanatic
                  • Mar 2017
                  • 137

                  #9
                  Thanks Mike.
                  So effectively the 6AWG is completely wasted.

                  Comment

                  • NewBostonConst
                    Solar Fanatic
                    • Nov 2018
                    • 113

                    #10
                    The six awg will be more efficient over a long distance so you are gaining there and that is common...yes, Mike is correct you have to size everything on your smallest conductor. Fuses and Circuit breakers are sized to the wire and to protect the wire.

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #11
                      Originally posted by Aussiemike
                      Thanks Mike.
                      So effectively the 6AWG is completely wasted.
                      No, it is a meaningful length of low resistance (low loss) cable.
                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • Aussiemike
                        Solar Fanatic
                        • Mar 2017
                        • 137

                        #12
                        Thanks Mike

                        Comment

                        • Aussiemike
                          Solar Fanatic
                          • Mar 2017
                          • 137

                          #13
                          Morning guys.
                          Is it ok to attach the battery cables from the Charge Controller to the terminals of the Inverter?
                          Cheers Mike

                          Comment

                          • Aussiemike
                            Solar Fanatic
                            • Mar 2017
                            • 137

                            #14
                            Can I use this as a switch and not a circuit breaker? Or does it have to be DC?
                            Capture.JPG
                            Attached Files

                            Comment

                            • SunEagle
                              Super Moderator
                              • Oct 2012
                              • 15147

                              #15
                              Originally posted by Aussiemike
                              Morning guys.
                              Is it ok to attach the battery cables from the Charge Controller to the terminals of the Inverter?
                              Cheers Mike
                              Most charge controllers do not have an output rating big enough for an inverter so they can fail. It would be better to wire the inverter to the battery terminals.

                              Some type of DC voltage rated disconnect device needs to be used between the battery and inverter. If that circuit breaker is not DC voltage rated then you really shouldn't use it.