I am glad that you are contacting Generac to follow up on system voltages being higher than specification voltages. Generac set the max voltages for a reason.
One additional request please. Please post the wiring diagram if possible. Obscure any private information (like name, address, etc.) before posting.
I assume you have one battery cabinet. The inverter has 4 DC inputs for batteries and solar panels. One input is taken up by the battery cabinet.
Somehow your installer configured your six strings into the three DC inputs remaining at the inverter. Your installer may or may not have paralleled strings together before the PVLink.
It's important to understand how the strings are configured so we can see if paralleling and amp limitations are being followed for all devices.
Also show which string/PVLink is causing you grief on the drawing.
Thanks in advance.