So I've asked a similar question before, but now after finally reviewing the 2022 NFPA and IFC codes, I think I have this right. I have a mixed roof, one part flat, one part pitched. On the flat part, if I read the codes right, there are NO setback requirements for flat roofs, right??? I would put in a 36" pathway to get to the pitched roof, but that is it for requirements, and even that seems more than the code requires. For the pitched roof, if I am covering less than 33% of the roof, and its not the side facing the street, then an 18" setback from the horizontal ridge is the only requirement. There does need to be 3 feet on either side as well (for fire ladders) I was told by a building inspector, but that doesn't seem to be exactly right (seems only 1 36" area is needed). If this is correct, then those houses with flat roofs can accommodate a lot more solar panels then what most solar installers are suggesting. Any comments or thoughts would be welcomed, especially anyone who has installed on flat roofs.
Here is the IFC code (Flat roofs are actually excepted from these requirements though):
1205.2.1Solar photovoltaic (PV) systems for Group R-3 buildings.
Solar photovoltaic (PV) systems for Group R-3 buildings shall comply with Sections 1205.2.1.1 through 1205.2.3.
Exceptions:
Not fewer than two 36-inch-wide (914 mm) pathways on separate roof planes, from lowest roof edge to ridge, shall be provided on all buildings. Not fewer than one pathway shall be provided on the street or driveway side of the roof. For each roof plane with a photovoltaic array, not fewer than one 36-inch-wide (914 mm) pathway from lowest roof edge to ridge shall be provided on the same roof plane as the photovoltaic array, on an adjacent roof plane or straddling the same and adjacent roof planes.
Here is the IFC code (Flat roofs are actually excepted from these requirements though):
1205.2.1Solar photovoltaic (PV) systems for Group R-3 buildings.
Solar photovoltaic (PV) systems for Group R-3 buildings shall comply with Sections 1205.2.1.1 through 1205.2.3.
Exceptions:
- These requirements shall not apply to structures designed and constructed in accordance with the International Residential Code.
- These requirements shall not apply to roofs with slopes of 2 units vertical in 12 units horizontal (16.7-percent slope) or less.
Not fewer than two 36-inch-wide (914 mm) pathways on separate roof planes, from lowest roof edge to ridge, shall be provided on all buildings. Not fewer than one pathway shall be provided on the street or driveway side of the roof. For each roof plane with a photovoltaic array, not fewer than one 36-inch-wide (914 mm) pathway from lowest roof edge to ridge shall be provided on the same roof plane as the photovoltaic array, on an adjacent roof plane or straddling the same and adjacent roof planes.
Comment