  • SunShine123
    • Jun 2022
    • 3
    Inverter Keeps Rebooting
    I recently installed a SolarEdge inverter, load side. Over the past week, we've noticed the inverter rebooting as if it's detected a power loss or major voltage drop. We've also noticed one of our computer UPS' clicks over to battery mode at the same time. PowerChute reports the UPS as having a 'blackout'; though power isn't lost in the house. It appears random, and isn't tied to any major load (A/C, Freezers, Sump pump, etc) firing at the same time. It appears random, thus far.
    I'm suspecting voltage issues or other something else is going on, causing our inverter and UPS to trip off. Other devices seem unaffected, lights don't dim/flicker, etc. A/C fires up fine and draws power without issue or tripping these devices.
    Before I poke the power company over it, any thoughts or ideas on how to collect additional evidence?
    Yea - poke SolarEdge and see what they have to say. Maybe the two can get into a finger pointing contest. Just be careful they both don't pull a tag team and point both (middle) fingers at you.
      I once had a feeder line from the pole to the meter, going bad that caused same sort of thing. PoCo did nothing till the line fell down.
        Originally posted by SunShine123
        I recently installed a SolarEdge inverter, load side. Over the past week, we've noticed the inverter rebooting as if it's detected a power loss or major voltage drop. ...........
        If the SolarEdge software can produce a graph of frequency and voltage that might be a start. Do you have installer version of the software or did you use an installer?. In that case they may be able to help.
        • SunShine123
          • Jun 2022
          • 3
          Our installer is looking from their side now; and we have a case open with SolarEdge. I adjusted the voltage sensitivity on our UPS and seems to have stopped the blackouts, so I suspect it's tied to that.
          • Mike 134
            • Jan 2022
            • 432
            At least you have peace of mind knowing it's not an inverter problem with the UPS also picking up the momentary glitch.
            Unfortunately, with my professional history with power companies unless you're sitting in the dark or can hit them with MULTIPLE documents proving there is a problem you're out of luck. Best you can do is some troubleshooting such as any neighbors have an issue or is it site specific to your place? Narrow it down to get it fixed. I noticed you changed the threshold on the UPS . My power company in the midwest allows +/- 10% of 120V, inside that range you get "looks fine from our side" answer
            • SunShine123
              • Jun 2022
              • 3
              I'm pulling the logs from my UPS into my SIEM now. I do log analysis as part of a troubleshooting job; if there's one thing I can do, it's collect evidence. The logs are showing actual blackouts, not over/under voltage. It was set at 2-4ms and tripping. I tuned it down to 6-8 ms and that seems to have resolved it. If I can get the SE inverter to that and if that counts as 'rapid shutdown', we probably can work around the line side problems.