I have been running 9 REC 320w n-cell panels in 1 array for about 2 years. I installed a larger inverter that has 3 MPPT inputs (sunnyboy 5.0 us -41). I finally found more modules. I ended up buying 10 more and was going to put several on my west roof as well as adding to the south… making 3 arrays. Looking at the max specs 10amp and 600v total which you can attach 7100 watts to.
The Voc on these 320w modules are 40.80v and the amps are near the max… how in the world is it possible to attach 7100 watts to this without hitting the max 600v?
I know people say don’t use the STC but people also say oversized the PV arrays by 10-20%… 22 panels are 7,040 watts, then you at 898 volts.
The 7.7-us-41 also has the max volts of 600 with 10amps and says you can attach 10,905w
The Voc on these 320w modules are 40.80v and the amps are near the max… how in the world is it possible to attach 7100 watts to this without hitting the max 600v?
I know people say don’t use the STC but people also say oversized the PV arrays by 10-20%… 22 panels are 7,040 watts, then you at 898 volts.
The 7.7-us-41 also has the max volts of 600 with 10amps and says you can attach 10,905w