X
 
  • Time
  • Show
Clear All
new posts
  • littleboss
    Junior Member
    • Sep 2019
    • 13

    #1

    Ground mount panels - inverter location

    Any reason I shouldn't mount a Fronius Primo (or other brand string inverter) at the panels location and then just run 240VAC over to the house (100' away) as opposed to running DC through the conduit. I save on wiring and don't have higher voltage DC running underground.
  • heimdm
    Solar Fanatic
    • Oct 2019
    • 180

    #2
    What is your DC voltage? The higher the volts the lower your amps, and the thinner wire that is required. Because of the distance, you have to add that into the equation.

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #3
      Under 600V, there is no real difference if you run 450VDC vs 240VAC except the 450V can use smaller ( cheaper) wire
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • robbyg
        Member
        • Apr 2021
        • 93

        #4
        Originally posted by littleboss
        Any reason I shouldn't mount a Fronius Primo (or other brand string inverter) at the panels location and then just run 240VAC over to the house (100' away) as opposed to running DC through the conduit. I save on wiring and don't have higher voltage DC running underground.
        All the reasons above plus the 100 foot walk back and forth every time you need to change something in the settings or the inverter trips.
        Good exercise but it can be annoying after awhile.

        Comment

        • littleboss
          Junior Member
          • Sep 2019
          • 13

          #5
          Originally posted by heimdm
          What is your DC voltage? The higher the volts the lower your amps, and the thinner wire that is required. Because of the distance, you have to add that into the equation.
          10 panels per string @ 40V = 400VDC total and 10.4A

          Comment

          • littleboss
            Junior Member
            • Sep 2019
            • 13

            #6
            Originally posted by robbyg

            All the reasons above plus the 100 foot walk back and forth every time you need to change something in the settings or the inverter trips.
            Good exercise but it can be annoying after awhile.
            You can't manage these fancy inverters with your computer or a phone app?

            Comment

            • SunEagle
              Super Moderator
              • Oct 2012
              • 15161

              #7
              Originally posted by littleboss
              Any reason I shouldn't mount a Fronius Primo (or other brand string inverter) at the panels location and then just run 240VAC over to the house (100' away) as opposed to running DC through the conduit. I save on wiring and don't have higher voltage DC running underground.
              Most ground mounts have the inverter close to the panels but you should still run the Voltage drop calculation to make sure.

              Comment

              • robbyg
                Member
                • Apr 2021
                • 93

                #8
                Originally posted by littleboss
                You can't manage these fancy inverters with your computer or a phone app?
                I don't know about Fronius but most inverters have to be reset from the unit itself. The software is typically centered around monitoring and has limited ability to change settings. Check the manual and see what you can do remotely. None the less I would rather be seeing, hearing and smelling what is happening with the inverter before I do something like reset it.

                Comment

                • reader2580
                  Solar Fanatic
                  • Jan 2017
                  • 281

                  #9
                  I mounted my Solaredge inverters at my ground mount array. I was told that DC is more sensitive to voltage drop than AC. My run is something like 175 feet. I upsized my wire one size more than necessary for the amperage to combat voltage drop.

                  I don't know why the concern about having inverters far away. It isn't like you are visiting them every day, or even every week. My Solaredge inverters just work and have never needed a reset.

                  Comment

                  • peakbagger
                    Solar Fanatic
                    • Jun 2010
                    • 1566

                    #10
                    Somewhere I saw a post that an AHJ decided that if the inverter was installed in the house versus an ground mount array that the array had to have Rapid Shutdown Devices. I did not make sense to me but in that case the inverter was mounted at the array to avoid the hassle.

                    Comment

                    Working...