New Features & Enhancements
Added display of DC power and current measurements via SetApp’s Status screen for commercial inverters. Inverters with synergy technology will display the measurements per unit.
Support S0 consumption meter
Support wireless gateway for wireless communication between SolarEdge inverters and the monitoring platform. Read more about the wireless gateway at: https://www.solaredge.com/us/product...less-gateway#/
For North America installations – enhanced circuit breaker trip protection in installations with smart EV charger and a battery both connected to the energy hub inverter. In cases where EV and battery are charging from the grid simultaneously, the charging levels of each device are reduced to prevent the inverter's circuit breaker tripping.
For Australia installations
Enhanced phase balancer for system installations comprised of multiple single phase inverters with power output of 5kW and above on 2-phase or 3-phase grids
New Country grid codes:
Australia VIC
Australia Essential Energy
Australia Ausgrid
Australia Endeavour Energy
Australia SAPN
Australia Horizon Power
Australia Evoenergy
Fixes
ESS Operation Mode menu item may appear in the Energy Manager screen in locations where this is not required (non-U.S. locations)
When reactive power mode is set to ‘Q’, the ‘Cos Phi’ status in the Status screen might show NA
For North America installations - inverters with built-in consumption metering, changing the meter function setting might not be applied on the first attempt
When manually turning-on Smart Energy device that is configured to a lower excess PV priority, can result in another Smart Energy device with higher excess PV priority increase its power
False communication error 3x2 when there’s an LTE cellular connection
Known Issues
For StorEdge installation, in case of TOU profile change from SetApp, the new settings may not be reflected in the monitoring platform.
Workaround: Re-apply the TOU profile from the monitoring platform
In installations with S0 meter, the monitoring platform charts may present power telemetries that fluctuate by ~50W.
Workaround: The fluctuations do not affect the meter accuracy; users can disregard the spikes in the chart.
For North America installations - inverters with built-in consumption metering:
Changing the meter function setting might not be applied on the first attempt
The CT rating might receive a value different from its default upon connection
Workaround: Set the meter function again
In sites with three phase StorEdge inverter, the low voltage battery connected via CAN bus, might appear in SetApp under the Modbus devices
While performing a battery test in StorEdge installations, a test-in-progress icon can appear after the test results were already received
When the inverter is in alternative power source (APS) mode, pairing cannot be performed
In case of a communication issue between the leader inverter and its follower(s), the follower inverter’s RRCR value will reset
CosPhi shows wrong value during pairing on SetApp
Workaround: There is no meaning for CosPhi during pairing
If smart energy device status is manually changed while the AC is disconnected from the inverter, when the inverter’s AC is restored, it will restore the smart energy device state as before the AC disconnection.
Workaround: Manually change the smart energy device state if needed
When resetting the inverter energy counters, ‘This Year’ value doesn’t reset.
Inverter without HD-Wave technology temperature shows 0 when in standby mode
Workaround: In standby mode, there is no production, thus temperature sensing is not relevant
Added display of DC power and current measurements via SetApp’s Status screen for commercial inverters. Inverters with synergy technology will display the measurements per unit.
Support S0 consumption meter
Support wireless gateway for wireless communication between SolarEdge inverters and the monitoring platform. Read more about the wireless gateway at: https://www.solaredge.com/us/product...less-gateway#/
For North America installations – enhanced circuit breaker trip protection in installations with smart EV charger and a battery both connected to the energy hub inverter. In cases where EV and battery are charging from the grid simultaneously, the charging levels of each device are reduced to prevent the inverter's circuit breaker tripping.
For Australia installations
Enhanced phase balancer for system installations comprised of multiple single phase inverters with power output of 5kW and above on 2-phase or 3-phase grids
New Country grid codes:
Australia VIC
Australia Essential Energy
Australia Ausgrid
Australia Endeavour Energy
Australia SAPN
Australia Horizon Power
Australia Evoenergy
Fixes
ESS Operation Mode menu item may appear in the Energy Manager screen in locations where this is not required (non-U.S. locations)
When reactive power mode is set to ‘Q’, the ‘Cos Phi’ status in the Status screen might show NA
For North America installations - inverters with built-in consumption metering, changing the meter function setting might not be applied on the first attempt
When manually turning-on Smart Energy device that is configured to a lower excess PV priority, can result in another Smart Energy device with higher excess PV priority increase its power
False communication error 3x2 when there’s an LTE cellular connection
Known Issues
For StorEdge installation, in case of TOU profile change from SetApp, the new settings may not be reflected in the monitoring platform.
Workaround: Re-apply the TOU profile from the monitoring platform
In installations with S0 meter, the monitoring platform charts may present power telemetries that fluctuate by ~50W.
Workaround: The fluctuations do not affect the meter accuracy; users can disregard the spikes in the chart.
For North America installations - inverters with built-in consumption metering:
Changing the meter function setting might not be applied on the first attempt
The CT rating might receive a value different from its default upon connection
Workaround: Set the meter function again
In sites with three phase StorEdge inverter, the low voltage battery connected via CAN bus, might appear in SetApp under the Modbus devices
While performing a battery test in StorEdge installations, a test-in-progress icon can appear after the test results were already received
When the inverter is in alternative power source (APS) mode, pairing cannot be performed
In case of a communication issue between the leader inverter and its follower(s), the follower inverter’s RRCR value will reset
CosPhi shows wrong value during pairing on SetApp
Workaround: There is no meaning for CosPhi during pairing
If smart energy device status is manually changed while the AC is disconnected from the inverter, when the inverter’s AC is restored, it will restore the smart energy device state as before the AC disconnection.
Workaround: Manually change the smart energy device state if needed
When resetting the inverter energy counters, ‘This Year’ value doesn’t reset.
Inverter without HD-Wave technology temperature shows 0 when in standby mode
Workaround: In standby mode, there is no production, thus temperature sensing is not relevant
Comment