  • PVAndy
    Solar Fanatic
    • Aug 2014
    • 230

    #16
    Originally posted by reader2580

    My plan would be to use Polaris connectors. I'm not sure the Milbank meter base has enough room inside for all the connectors and wires.

    My concern with a meter main is the 120% bus bar capacity rule probably applies to it. I would go with a meter main if allowed.
    Remember you also have NEC Box Fill & Bend Radius requirements to deal with

    Andy

    Comment

    • reader2580
      Solar Fanatic
      • Jan 2017
      • 281

      #17
      Originally posted by PVAndy
      Remember you also have NEC Box Fill & Bend Radius requirements to deal with
      Box fill is why I don't think there would be enough room in that Milbank meter base with main breaker. I would probably need a junction box of some sort.

      I currently have a junction box for my solar tap installed by an electrician. I don't think it would have passed inspection due to box fill had the inspector opened the box. The electrician told me that if I ever had to up size the solar feed conductors that I would need to do something different.
      Last edited by reader2580; 07-14-2020, 01:21 PM.

      Comment

      • PVAndy
        Solar Fanatic
        • Aug 2014
        • 230

        #18
        Originally posted by reader2580

        Box fill is why I don't think there would be enough room in that Milbank meter base with main breaker. I would probably need a junction box of some sort.

        I currently have a junction box for my solar tap installed by an electrician. I don't think it would have passed inspection due to box fill had the inspector opened the box. The electrician told me that if I ever had to up size the solar feed conductors that I would need to do something different.
        One last thought Most utilities in states we work in required disconnects with a "visible break" .
        A breaker does not have a visible break. It cost us over $30K on a megawatt site to rebuild the switchgear to meet this requirement when the vendor shipped the wrong Bolt Switch

        Andy

        Comment