Read that you divide the solar watts by battery to determine the charge controller size. Does that mean 6 270 watt panels and epever mptt 60amp charge controller cant work with a 12v battery bank?
Most Popular Topics
Collapse
Determine charge controller?
Collapse
X
-
-
1620 watts / 12v = 135amps. You will need 2, 60A charge controllers, or run the risk of overloading a single controller. Most MPPT controllers will self limit to their rated amps, but with more than double the rated power, you are looking at a risk of damaging a single controller.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister -
And someone else says that volts is more important. The epever says pv.input c as not exceed 150v. So panels are 30v 9 amp so run 3 in series and parelle would give me 90v 18 amps.making this possible.Comment
-
If you converted to a 24V system, you could pull it off with one controller and all your panels.
Or stay at 12V, and aim your panels in 3 different directions, like Bruce does, and get a "flat" moderate harvest all day long, instead of a noontime peak
The way a MPPT controller works, is to convert the voltage above battery voltage, to more amps, sort of like a step down transformer. Yes, the 90V side only has 18A, but MPPT controllers transform high voltage 90V 18A power to 12V 135A power. MPPT controllers are rated at their Max input Voltage, and their Max Output Amps, it's a very different spec than most people come across.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Well epever says as long as both the max PV of 1200 and voc are. Ot exceeded it should be fine. As they limit the output amps to 60.Comment
-
When you wire the panels in parallel the voltage will stay at 30v and the amps will add up to 18.
For a typical MPPT CC the max input wattage usually can be calculated by using the battery voltage times the amp rating of the CC. So a 12V battery with a 60amp CC can accept around 720watts ( 12 x 60 = 720). Some CC will allow a little more wattage to be inputed but that is because you really never get the full output of a panel or the CC can tolerate a higher wattage input.Comment
-
No. 3 of those panels wired in series will generate 90v at 9 amps. The voltage is added when you wire the panels in series but the amps will stay at what 1 panel provides.
When you wire the panels in parallel the voltage will stay at 30v and the amps will add up to 18.
For a typical MPPT CC the max input wattage usually can be calculated by using the battery voltage times the amp rating of the CC. So a 12V battery with a 60amp CC can accept around 720watts ( 12 x 60 = 720). Some CC will allow a little more wattage to be inputed but that is because you really never get the full output of a panel or the CC can tolerate a higher wattage input.Comment
-
Yes. You are correct. Now you just have to determine what the maximum amount of panel wattage your CC can handle understanding if that if you wire all 6, for a total of 1620w, then you may exceed the input rating which could either burn it up or clip the over wattage to generate power.Comment