    480 Watts = ?

    Hi Guys,

    Ok not too good on the math part of this, so this goes to the pros.

    I am in SW kentucky, and I have (4) 120 watt solar panels hooked together at 12 volts, going through a 20 amp controller and then to (4) 105 amp batteries.

    My question is what does this equal to in daily wattage?

    Thanks

    Milezone
  • russ
    Solar Fanatic
    • Jul 2009
    • 10360

    #2
    From PV Watts -

    Jan 42 kWh
    Feb 45 kWh
    Mar 58 kWh
    April 56 kWh
    May 58 kWh
    June 58 kWh
    July 60 kWh
    Aug 57 kWh
    Sept 52 kWh
    Oct 53 kWh
    Nov 39 kWh
    Dec 36 kWh
    "Year" 493 kWh

    PV Watts is calculated from long term data meaning the 'average' year - some will be better and some not as good.

    PV Watts starts with 1 kW so I enter 4.8 kW and take 10% for a result.

    Russ
    [SIGPIC][/SIGPIC]

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #3
      Originally posted by milezone
      My question is what does this equal to in daily wattage?
      You mean watt hours but to answer your question 0 watt hours because you burned up your 20 amp charge controller trying to push 40 amps through it.
      MSEE, PE

      Comment

      • milezone
        Member
        • Nov 2009
        • 54

        #4
        Hmmmm well the controller is ok, but you are correct my 20amp breaker blew. Luckily I have that. Ok well sounds like my panels are more than 20 amps? I could have swore they were only like 5 amps per panel.

        While I am on the subject of blowing things Am I ok with the 4 batteries? I checked the panels and was getting 18.5 volts as of 6:00pm today, if that helps any?

        Milezone

        Comment

        • milezone
          Member
          • Nov 2009
          • 54

          #5
          Hi Guys,

          Also I was always thinking of switching to a MPPT controller, and I know in the next few months I am going to add another 240 watts of solar (making it 720 watts total), can anyone recommend a good controller for this setup?

          Milezone

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            Originally posted by milezone
            Hmmmm well the controller is ok, but you are correct my 20amp breaker blew. Luckily I have that. Ok well sounds like my panels are more than 20 amps? I could have swore they were only like 5 amps per panel.
            Milezone currents and voltages all depend on panel specifications, how the panels are configured, and charge controller type.

            All you stated is you have 4 120 watt panels and a 20 amp charge controller.

            I assume you have standard 12 volt panels, wired in parallel. So if that assumption is correct your panel specs are likely 18 Vmp and 6.67 amps Imp. So if you have 4 of them in parallel will yield a Imp current of 4 x 6.67 amps = about 27 amps input to the controller @ 18 volts.

            As for controller type can be either PWM or MPPT.

            With PWM the Input Current = Output current. You are trying to pump in 27 amps into a 20 amp device. That will eventually let the magic smoke out. Sounds like you already know you have trouble because your breaker is too small. The breaker needs to be a minimum of 30 amps. So if you have a 20 amp PWM controller and the panels wired in parallel you are heading for trouble.

            I doubt you have MPPT so no need to go into that, but if you do, then you have turned your 480 watt panels into 260 watts because that is all a 20 amp MPPT charge controller will pass to the batteries (20 amp x 13 volt).

            Either way you are screwed.
            MSEE, PE

            Comment

            • milezone
              Member
              • Nov 2009
              • 54

              #7
              I thought MPPT Controllers were better? If I get a 60 amp Outback, would that not be a good one to get the most out of my setup?

              Or should I just go get a 60 amp PWM, as you make it seem like that will get my 480 watts to work together?

              And yes I have them parallel to keep a 12 volts setup. So yes I do need a new controller, would love to hear what you recommend for me. I have a few bucks to burn.

              Milezone

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #8
                Originally posted by milezone
                I thought MPPT Controllers were better? If I get a 60 amp Outback, would that not be a good one to get the most out of my setup?
                MPPT controllers are a lot better, much better. Problem is with your setup if it is MPPT and 20 amps it will limit the battery charge current to 20 amps. Watts = volts x amps. So with a 20 amp MPPT controller operating in 12 volts the max wattage you can input without wasting panel wattage is roughly 13 volts x 20 amps = 260 watts. Anything over 260 watts will not be used.

                Before I go into a detailed explanation read this thread please. After you do you will understand this:

                If you used say a 30 amp PWM controller vs a 40 Amp MPPT controller with your panels at 480 watts:

                The PWM controller will output 13 volts x 26.7 amps = 346 watts out of 480 input.

                With a 40 amp MPPT controller will output 13 volts x 35.3 amps = 459 watts out of 480 watts input.
                MSEE, PE

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #9
                  Rouge has a new mid (60v) voltage MPPT charge controller out,

                  30A 12 / 24 v battery
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • milezone
                    Member
                    • Nov 2009
                    • 54

                    #10
                    Hi Sunking,

                    First thank you for the help, I know we noob's can be a pain in the rump.
                    Ok so I am going with a 60 amp outback controller. This should give me plenty as you say for my 480 watts, and room to add 2 more. Is this the proper thinking?
                    Which means I need to bump up my fuse also to 60 amp, correct? Thanks

                    Milezone

                    Comment

                    • milezone
                      Member
                      • Nov 2009
                      • 54

                      #11
                      Went with Northern Arizona Wind & Solar. Great help they were as well. Got a new 60 amp Outback controller, MNEDC-Quad Enclosure for 1-4 Panel Mount Breakers, 3 60 amp breakers, some wires, and ground bus bar (to ground the entire system). Watch out, I am working for the total NEC Spec legal and approved system.

                      Milezone

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #12
                        Originally posted by milezone
                        Ok so I am going with a 60 amp outback controller. This should give me plenty as you say for my 480 watts, and room to add 2 more. Is this the proper thinking?
                        Which means I need to bump up my fuse also to 60 amp, correct? Thanks

                        Milezone
                        Ok now you are talking and have something to work with. First you do not have to be stuck with wiring your panels in parallel anymore. Which is great because it is parallel is very inefficient. You can now use a series/parallel combination. With 4 panels you can wire them all in series to get the voltage up and current way down.

                        Operation with 12 volt battery your panel wattage is limited to around 800 watts input. If you move up to 24 volts you can input 1600 watts, and at 48 volts 3200 watts.

                        As for the combiner fuse now depends on panel configuration. If you stick with 4 panels in parallel you will need a 30 amp fuse/breaker. Wire them in series and you only need a 10 amp breaker.
                        MSEE, PE

                        Comment

                        • milezone
                          Member
                          • Nov 2009
                          • 54

                          #13
                          The only problem I have is my inverter, it is 1,000 watt pure sine wave, but 12 volts. So if I do change to 24 volts, I would have to get a new inverter, whcih are quite expensive.

                          Comment

                          • Sunking
                            Solar Fanatic
                            • Feb 2010
                            • 23301

                            #14
                            Originally posted by milezone
                            The only problem I have is my inverter, it is 1,000 watt pure sine wave, but 12 volts. So if I do change to 24 volts, I would have to get a new inverter, whcih are quite expensive.
                            Yes you will, that is life. You feel into the trap of 12 volts which is very limited and inefficient.
                            MSEE, PE

                            Comment

                            • Securityxpert4u
                              Junior Member
                              • Jun 2011
                              • 8

                              #15
                              Originally posted by milezone
                              The only problem I have is my inverter, it is 1,000 watt pure sine wave, but 12 volts. So if I do change to 24 volts, I would have to get a new inverter, whcih are quite expensive.
                              Don't know how much you paid for your inverter, but you can always use a step up or step down DC converter to use it with the ideal 24V or 48V series string...just a thought

                              Comment