System specs: 24 JAM60S02-310/PR panels with IQ7-Plus microinverters (max output 290 va/1.29 a) split into 3 arrays. Array 1 has 16 panels split into two 8 panel strings. Arrays 2 and 3 each have 4 panels. Each array is on a different roof section.
Whenever I see an Enphase microinverter system, it always runs each string to a combiner (roof mounted or at ground level) with each string going to a 20 amp breaker, or fuse.
On DIY systems, I've noticed that if the DIY'r doesn't use a combiner box, they still run each string to a 20 amp breaker before combining the strings and connecting to a back fed breaker in their service panel. The Enphase design guide promotes this as well.
My question is this: Since the only limiting factor for the number of microinverters in a string is the 12 AWG Q cable ampacity rating (20 a), why can't the strings just be wire nutted together in a J-Box on the roof with a 10 AWG home run taking all the power to the back fed breaker I the service panel.
I don't understand the purpose of a combiner box with a 20 amp breaker for each string. The breaker will never flip, especially with only 8 microinverters (total current = 10.32 a).
Could this be an unneeded leftover from early microinverter systems?
Whenever I see an Enphase microinverter system, it always runs each string to a combiner (roof mounted or at ground level) with each string going to a 20 amp breaker, or fuse.
On DIY systems, I've noticed that if the DIY'r doesn't use a combiner box, they still run each string to a 20 amp breaker before combining the strings and connecting to a back fed breaker in their service panel. The Enphase design guide promotes this as well.
My question is this: Since the only limiting factor for the number of microinverters in a string is the 12 AWG Q cable ampacity rating (20 a), why can't the strings just be wire nutted together in a J-Box on the roof with a 10 AWG home run taking all the power to the back fed breaker I the service panel.
I don't understand the purpose of a combiner box with a 20 amp breaker for each string. The breaker will never flip, especially with only 8 microinverters (total current = 10.32 a).
Could this be an unneeded leftover from early microinverter systems?
Comment