+ More Options
Posts
  • NEOH
    • Nov 2010
    • 478
    East Array + South Array + West Array ?
    I am helping with the design of a Ground Mount PV system.
    My friend bought a whole pallet of 275 Watt PV Panels = Qty 30.
    From the PV Label ...
    Voc = 38.7 volts
    Isc = 9.17 amps
    Vmp = 31.7 volts
    Imp = 8.69 amps
    And he bought an SMA 5000 watt US 240 Volt AC Grid Tie Inverter with 3 independent MPPT channels
    Each channel has a 480 Volt max for MPPT, and 600 volt absolute max.
    So, the first calculation we did was this ...
    480 volts / 38.7 volts Voc = 12 Panels max in the Southern facing array!
    Next, we calculated this ...
    East Array = 9 panels x 275 Watts = 2,475 watts x 80% = 1,980 watts (net)
    South Array = 12 panels x 275 Watts = 3,330 watts x 80% = 2,640 watts (net)
    West Array = 9 panels x 275 Watts = 2,475 watts x 80% = 1,980 watts (net)
    Total Watts of all 30 Panels = 1,980 + 2,640 + 1,980 = 6,600 Watts which is greater than 5,000 watts
    So, the question is ...
    "How do we calculate the ANGLE for the East & West array 'wings' with respect to the larger South Array"
    We realize that for every 15 degrees, the East Array will peak 1 hour earlier and
    the West array will peak 1 hour later.
    Rotate the East and West arrays back 15 degrees ( 1 hour ), then at Solar Noon ...
    East Array = sin(75) x 1,980 = 1,912
    South Array = 2,640 watts
    West Array = sin(75) x 1,980 watts = 1,912
    Total watts is too high 6,464 = 1,912 + 2,640 + 1,912
    Rotate the East and West arrays back 30 degrees ( 2 hours ), then at Solar Noon ...
    East Array = sin(60) x 1,980 = 1,714
    West Array = sin(60) x 1,980 watts = 1,714
    Total watts is too high 6,068 = 1,714 + 2,640 + 1,714
    Rotate the East and West arrays back 45 Degrees ( 3 hours ), then at Solar Noon ...
    East Array = sin(45) x 1,980 = 1,400
    West Array = sin(45) x 1,980 watts = 1,400
    Total watts (input) is "OK" at 5,440 = 1,400 + 2,640 + 1,400
    I am not sure we should rotate the East & West Arrays back much more, since the morning and evening sun is lower at 9am & 3pm
    At 9:00AM total watts is ...
    East Array = sin(90) x 1,980 = 1,980
    South Array = sin(45) x 2,640 = 1,866
    West Array = sin(0) x 1,980 watts = 0
    Total watts from 9:00AM is 3,846 = 1,980 + 1,866 + 0
    At 3:00PM total watts is ...
    East Array = sin(0) x 1,980 watts = 0
    West Array = sin(90) x 1,980 = 1,980
    Total watts from 9:00AM is 3,846 = 0 + 1,866 + 1,980
    So, from 9:00am until 3:00pm ...
    6 Hours x 4,500 Watts (avg) = 27 kWhr every sunny summer day?
    Is there a better way to use all 30 PV Panels with this SMA 5kW Inverter?
    • 15007
    Please help me out and describe what you are trying to accomplish. What's your desired end result ?
    It appears you are trying to do a PV application but are ignorant of how to go about it or what's available to help with your task.
    My guess is you will need a lot more education before you can pull off whatever it is you have in mind.
    Start with : " Solar Power Your Home for Dummies" and then get familiar with PVWatts.
    You can get some help here but it'll go a lot faster and better for you, and you'll waste a lot less of others' time if you put some time and effort into understanding the basics. From what you write it's pretty obvious to me you have a lot to learn.
    Welcome back to the neighborhood and the forum of few(er) illusions.
      • 5208
      There is a lot to be considered here, every situation will be different. The main
      issues here at 42 deg lat were getting the most energy through a limited size
      inverter plant, maximizing collection under clouds, and minimizing the labor to
      keep the array cleared of snow. Here you see 3 single test panels set up to
      answer your sort of question. These were tested at varied angles and curves
      plotted. The big array is facing east, on its back side are panels facing west,
      a south facing array is outside the picture.
      I will come back with some curves, what is your latitude and snow situation?
      Bruce Roe
      • NEOH
        • Nov 2010
        • 478
        It would be better for you, if you learned some manners.
        I clearly know more than the basics and that is why my friend asked me for help.
        This is NOT your standard configuration.
        Do you not understand the simple question ...
        "... Is there a better way to use all 30 PV Panels with this SMA 5kW Inverter? ..."
        Reply, if and only if, you have you have some applicable knowledge.
        • NEOH
          • Nov 2010
          • 478
          Bruce Roe
          BCROE,
          Thank you, for the reply
          40 degrees North Latitude
          This is a Ground Mount, so snow can be ( will be ? ) removed, as needed.
          The other option that we are considering...
          12 panels SOUTH on the "A" MPPT Channel input
          12 panels SOUTH on the "B" MPPT Channel input
          0 panels on the "C" MPPT Channel input
          This wastes 8 of the purchased PV Panels.
          11 panels x 275 Watts x 80% = approx 2,500 watts on each MPPT channel input.
          I need to run the math on this configuration
          After looking at you photo, I realized that we could do ...
          12 panels facing EAST on the "A" MPPT Channel input
          12 panels facing WEST on the "B" MPPT Channel input
          Wasting 6 panels.
          There appears to be many options ...
          None of which are your "Standard Configuration"
          I want to maximize the Watt-Hours produce for my friends system, using what he bought / owns.
            • 15007
            I believe I have more applicable knowledge with respect to your situation than you are probably aware of or are capable of understanding or absorbing, but I won't be replying further to this thread.
            Good luck in your future endeavors.
              • 5208
              In the ideal situation your panels will collect the most energy facing south, 180 deg. But
              here the unclouded part of the day can be earlier hours, leaving poor output mid day. Often
              clouds will drop output, but I have partly compensated by using a very high DC/AC setup.
              Clouds do not care so much what direction the panels face, but all facing south would waste
              output (and overload the string inverters). So the experiment is to keep the inverters busy
              for a lot more hours per day but not overloaded. The 2013 attempt managed to produce this
              curve, inverters running full power for 8 hours, as opposed to just mid day.
              That result was not really optimized, esp relative to snow, so the test panels
              were set up in 2016. A look at the position of the rising and setting sun showed
              it to be average about straight E-W, more to the north in summer, more to the
              south in winter. The tests were with straight E-W panels as close enough to
              quickly reach full power in summer, without huge loss of winter production.
              This will be impacted by latitude, and by the degree of larger DC/AC.
              The next curve shows the 3 test panel relative output over a sunny day. The tilt
              here was 61 deg from flat. Other angles were tried, to get a near flat a curve over
              the day. Note the instantaneous sum of the E and W panels (1 and 3) is so close
              to flat, hardly any south facing input is needed to bring up the middle, at least for
              this month.
              The conclusion was that for a high DC/AC ratio (previously chosen to
              compensate for clouds) at this latitude, I could collect the most energy with
              most panels facing E-W, and a lesser number of S facing panels. The same
              simple string inverters were shared by all panels. The curves may not be as
              good in winter, but those months are so cloudy it is less important.
              As for snow there is a sticky on exactly how I handle that. The last array design
              is optimized for production in warmer months and for snow rejection in that
              season. This with tilt changed twice a year, very easy to do. What little snow
              sticks will soon be melted by the first good sun, or is very easily removed. Bruce Roe
              • NEOH
                • Nov 2010
                • 478
                this month.
                BCROE,
                Thank You for the graphs.
                We are trying to maximize the Yearly kWhrs produced using 30 x 275W PV Panels and one 5 KW Inverter.
                "... Multiple Arrays, pointed in multiple directions ..." <= Yes that is exactly what I was describing in message #1.
                In your Sine Wave Graph ...
                Your sine wave #1 is my proposed South-West Rack with 9 panels
                Your sine wave #2 is my proposed South Rack with 12 panels
                Your sine wave #3 is my proposed South-East Rack with 9 panels
                You used two (2) sine waves ( East & West only ), while I propose using three (3) sine waves
                Adding up all three (3) of my sine waves should produce nearly constant Watts Output from 9AM until 3PM, without any clipping
                Owner's original idea
                South Array #1 = 10 panels on MPPT Channel A
                South Array #2 = 10 panels on MPPT Channel B
                South Array #3 = 10 panels on MPPT Channel C
                It is an "OK" configuration but the Inverter will be clipping the 6,600 Watts down to only 5,000 Watts from 10am until 2pm = LOW Yield !
                Assuming ...
                4 hours at 100% = 4 x 5,000 = 20.0 kw ( He lost a whopping 6,600 whrs = 1,600 x 4 due to clipping ! )
                2 hours at 70% = 2 x 4,620 = 9.24 kw
                2 hours at 50% = 2 x 3,300 = 6.60 kw
                Estimate Daily Total = 36 kwhr
                My idea ( per message #1 )
                South-East Array ... 9 panels on MPPT Channel A = 1,980 watts x 6.4 hours = 12.6 kwhr
                South Array ...........12 panels on MPPT Channel B = 2,640 watts x 6.4 hours = 16.9 kwhr
                South-West Array ... 9 panels on MPPT Channel C = 1,980 watts x 6.4 hours = 12.6 kwhr
                Where 6.4 Solar hours = 4 x 100% + 2 x 70% + 2 x 50% ( same as above )
                Estimated DailyTotal = 42 kwhr = 12.6 + 16.9 + 12.6 <<< This prevents the loss of the 6,600 watts due to clipping !
                This design barely exceeds the MAX Watts of the Inverter, which maximizes the yield from the 30 Solar Panels
                Also, this design is better than above, for days that are just sunny in the morning, or just sunny in the evening
                I call it "Opportunity" PV Solar.
                Nearly constant PV Watts generated from 9AM until 3PM
                BCROE "East - West" idea
                He is installing a very simple Fixed Ground Mount.
                I don't see how an East-West only design can have a higher Yearly kWhr production vs "SE + South + SW"
                I don't think we gain anything by greatly exceeding the Inverters Max Watts and then CLIP the Inverter for 8 hours = he loses watts
                You have enough Solar Panels to "max out" your inverter for 8 Hours, he does not, that is a huge design difference.
                To "max out" a 5KW Inverter for 8 hours, he would need 23 Panels facing East and 23 Panels facing West = 46 Panels
                He only has 30 Panels.
                Please explain how "East + West only" can generates more Yearly kWhrs vs "South-East + South + South-West" ?
                I have winter ( Dec - Jan - Feb ) data for my system
                I will check to see how many Daily PV Hours an "East + West" setup might lose.
                EDIT:
                My kWhr PV Production for Dec & Jan is ~45% of June.
                I remove all snow from my Solar Panels, as needed.
                So, winter production is much lower but not insignificant.
                  • 15154
                  Why not install the full amount of panels the inverter can accept on 2 channels (I presume that is 11 panels per channel or 22 total) and the rest (8 panels) install either on the East or West side whichever gets more days of good sunlight.
                  Putting the majority of your panels facing South will not over load the inverter yet should yield the highest output compared to a portion at 3 different compass headings.
                  Unfortunately with the weather patterns not being consistent every day, a fixed array will get you a mixer of good days of production and not so good days.
                    • 5208
                    BCROE,
                    I am not presenting a cookbook method to the ideal solution, just showing some ideas
                    that worked for my latitude, snow, cloud, and inverter limits situation. Note in particular
                    that designing to minimize snow impact will require a more complex mount with easy
                    variable tilt. My first winter I was out at sunrise nearly 2 dozen times to get the snow
                    off, each time taking more than an hour. The redesign reduced those efforts by 80%,
                    make your decision and be prepared to live with it.
                    Your variables are all different from mine, your best solution will also be different. I
                    am not claiming which is best for you, however I bought panels to do the job. I am
                    pushing out ideas that might be overlooked, and later long regretted.
                    Guess I will throw out one more idea. Panels may be mounted landscape, portrait,
                    or any angle between, the sun does not care. My solar area is on a 10% grade,
                    some 6.3 degrees. I have seen people move all kinds of dirt, build embankments,
                    and so on to get an array perfectly level. The arrays I built are laser straight, but
                    they follow the land. The yellow level here shows just how much slope I have.
                    good luck,
                    Bruce Roe
                    • NEOH
                      • Nov 2010
                      • 478
                      Yes, you are correct ...
                      South Array #1 on Chan A = 11 Panels x 275W x 80% = 2,420 Watts
                      South Array #2 on Chan B = 11 Panels x 275W x 80% = 2,420 Watts
                      SE or SW Array on Chan C = 8 Panels x 275W x 80% = 1,760 Watts
                      I was so focused on keeping the system symmetrical, that I never considered this option
                      He has a huge flat farm, clear East & West horizons
                      Would the South-East PV Array be cooler in the morning vs the hotter South-West PV Array in the evening?
                      Therefore, potentially more watts in the morning vs evening?
                        • 15154
                        I was so focused on keeping the system symmetrical, that I never considers this option
                        He has a huge farm, clear East & West horizons
                        Only you and your friend can determine which is the better focus. Sometimes there could be fog in the morning or clouds in the afternoon. It all depends on where the array is located and they type of weather you get.
                        Still since the 8 panel array is the smallest the output affected by clouds or fog is much smaller then the 22 panels facing South.
                        • NEOH
                          • Nov 2010
                          • 478
                          good luck,
                          Bruce Roe
                          Wow, that is a nice Ground Mount
                          My friend does not have the skill set to build a Ground Mount like yours.
                          I have read about East-West facing PV Panels installations = no shading.
                          https://www.pv-tech.org/editors-blog...t-solar-design
                          Maybe I was missing a key element of the East-West design and so I posted my concerns.
                          An East-West design can certainly fully utilize an Inverter at 100% Power, for many, many hours.
                            • 5208
                            He might be able to build this cheap, simple 2 sided array. This version has disadvantages
                            of fixed tilt, requiring unshaded area on both sides, being too close to the ground to clear
                            all snow accumulation, and perhaps a 10 year life. Bruce Roe
                            • NEOH
                              • Nov 2010
                              • 478
                              No concerns that wood can shrink or warp?
                              After I clean the snow off of my panels, I drive past with my JD Tractor with a front mounted 2 stage snow blower.
                              Shoots snow about 8' away and makes a perfect path in front panels for the next day