This is my first post. First, I would like to express my gratitude to all members of this forums. Your advice has been invaluable in times of need after being severely impacted by a category 4 hurricane. Using the information and advice from this forum I was able to successfully design and install a small off grid solar system. The system performed flawlessly. Mainly because, as advised, we had enough PV power and enough battery capacity (charged at 10% of C20 and never exceeded the 20% DOD level). Again, I want to thank all member for their time. Thank you!
In my jurisdiction an electrical installation does not have to be inspected but must be certified by a licensed electrician. We follow NEC 2017 but do not have a rapid shutdown requirement. My home has a 100-amp service (#2 AWG). The meter enclosure is the main panel. One 100-amp breaker. Ground and neutral are bonded in this panel. Four conductors run from this panel (3 #2 AWG and 1 #8 AWG ground wire) to the distribution panel (100-amp sub panel).
I would like to install a 7.6 kw inverter. (To keep things simple in this post I will ask a question about the inverter size in another post.) To control costs, I would like to avoid a meter tap. I have experience installing electrical panels and sub panels. I researched the possible solutions and found a viable one.
The solution would be to replace the subpanel with a 200-amp sub panel. Use a 100-amp 2 pole breaker to backfeed (with hold down screw). And use a 40-amp breaker for the Inverter. The thing that make me doubt about this solution is that the 200-amp subpanel will still be feed by 100-amp cable (#2 AWG). Is this solution NEC compliant? Thank you very much.
In my jurisdiction an electrical installation does not have to be inspected but must be certified by a licensed electrician. We follow NEC 2017 but do not have a rapid shutdown requirement. My home has a 100-amp service (#2 AWG). The meter enclosure is the main panel. One 100-amp breaker. Ground and neutral are bonded in this panel. Four conductors run from this panel (3 #2 AWG and 1 #8 AWG ground wire) to the distribution panel (100-amp sub panel).
I would like to install a 7.6 kw inverter. (To keep things simple in this post I will ask a question about the inverter size in another post.) To control costs, I would like to avoid a meter tap. I have experience installing electrical panels and sub panels. I researched the possible solutions and found a viable one.
The solution would be to replace the subpanel with a 200-amp sub panel. Use a 100-amp 2 pole breaker to backfeed (with hold down screw). And use a 40-amp breaker for the Inverter. The thing that make me doubt about this solution is that the 200-amp subpanel will still be feed by 100-amp cable (#2 AWG). Is this solution NEC compliant? Thank you very much.