Total run is 90feet per line from the junction box to MSP + the trunk cable of the M215
so, to sum up, the whole plan
We have 2 roofs , upper and lower
top roof has 4 strings on it
15
15
13
13
lower roof has 2 strings on it
12
12
the plan is to bring 2 wires from each string L1 , L2 plus a Neutral and Ground per roof into the attic using #10 THWN-2 Wires
so
8 wires + N and G for top roof
4 wires + N & G for lower roof
in conduit around 35 feet run
from the attic go straight to the main service panel around 55' run
12 wires for 6 strings + N & G 14 wires of #10 Either THWN-2 or ROMEX
if I need conduit indoor for THWN-2 I might reconsider and do ROMEX
a 10/3 wire has 4 wires in it so for 14 wires total I can run 4 Romex 10/3 or 5 of 10/2
OR I can put a combiner box in the attic and just 1 Romex #4/3 to the main panel
would appreciate your help with the best option
so, to sum up, the whole plan
We have 2 roofs , upper and lower
top roof has 4 strings on it
15
15
13
13
lower roof has 2 strings on it
12
12
the plan is to bring 2 wires from each string L1 , L2 plus a Neutral and Ground per roof into the attic using #10 THWN-2 Wires
so
8 wires + N and G for top roof
4 wires + N & G for lower roof
in conduit around 35 feet run
from the attic go straight to the main service panel around 55' run
12 wires for 6 strings + N & G 14 wires of #10 Either THWN-2 or ROMEX
if I need conduit indoor for THWN-2 I might reconsider and do ROMEX
a 10/3 wire has 4 wires in it so for 14 wires total I can run 4 Romex 10/3 or 5 of 10/2
OR I can put a combiner box in the attic and just 1 Romex #4/3 to the main panel
would appreciate your help with the best option