  • doctorman
    Member
    • Feb 2017
    • 40

    #16
    Total run is 90feet per line from the junction box to MSP + the trunk cable of the M215


    so, to sum up, the whole plan

    We have 2 roofs , upper and lower

    top roof has 4 strings on it
    15
    15
    13
    13

    lower roof has 2 strings on it
    12
    12

    the plan is to bring 2 wires from each string L1 , L2 plus a Neutral and Ground per roof into the attic using #10 THWN-2 Wires
    so
    8 wires + N and G for top roof
    4 wires + N & G for lower roof
    in conduit around 35 feet run

    from the attic go straight to the main service panel around 55' run
    12 wires for 6 strings + N & G 14 wires of #10 Either THWN-2 or ROMEX
    if I need conduit indoor for THWN-2 I might reconsider and do ROMEX
    a 10/3 wire has 4 wires in it so for 14 wires total I can run 4 Romex 10/3 or 5 of 10/2



    OR I can put a combiner box in the attic and just 1 Romex #4/3 to the main panel


    would appreciate your help with the best option

    Originally posted by SunEagle

    You would also need to de-rate the amp capacity of those 12 cables (6 cable runs) if they are all in the same conduit.

    Comment

    • NewBostonConst
      Solar Fanatic
      • Nov 2018
      • 113

      #17
      You can't transition wire sizes without the protection of fuses or breakers...

      What micro inverters are you using, many don't need a neutral or a ground...you could possibly get away with a single ground if required to the frames and rails.

      Comment

      • doctorman
        Member
        • Feb 2017
        • 40

        #18
        Originally posted by NewBostonConst
        You can't transition wire sizes without the protection of fuses or breakers...

        What micro inverters are you using, many don't need a neutral or a ground...you could possibly get away with a single ground if required to the frames and rails.
        I am not transitioning wire size , going from HTWN-2 #10 to ROMEX #10

        also the enphase trunk cable is 12AWG and no breaker needed in the junction box where I switch to the HTWN #10AWG

        Enphase M215

        so either I have to do ROMEX inside and out or HTWN-2?
        Can I run ROMEX in conduit?
        Can I run HTWN-2 without conduit indoor?

        Comment

        • NewBostonConst
          Solar Fanatic
          • Nov 2018
          • 113

          #19
          Originally posted by doctorman
          Total run is 90feet per line from the junction box to MSP + the trunk cable of the M215

          OR I can put a combiner box in the attic and just 1 Romex #4/3 to the main panel
          I am pretty sure you just ask about using a combiner box and #4/3, I am pretty sure that means you are asking if you can transition sizes. Also pretty sure I have seen combiner boxes without fuses or breakers....just trying to help, guess you can figure it out on your own.

          Comment

          • doctorman
            Member
            • Feb 2017
            • 40

            #20
            Originally posted by NewBostonConst

            I am pretty sure you just ask about using a combiner box and #4/3, I am pretty sure that means you are asking if you can transition sizes. Also pretty sure I have seen combiner boxes without fuses or breakers....just trying to help, guess you can figure it out on your own.
            oh... if I have a combiner box I will have breakers inside.

            Comment

            • ButchDeal
              Solar Fanatic
              • Apr 2014
              • 3802

              #21
              Originally posted by NewBostonConst
              Also pretty sure I have seen combiner boxes without fuses or breakers....just trying to help,
              OP has a microinverter system so we are talking about an AC combiner. It would require breakers.

              A DC combiner of TWO strings (3 with SolarEdge optimizers) would be possible without breakers or fuses.
              OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #22
                Originally posted by doctorman
                Can I run ROMEX in conduit?
                Maybe, but you may have to de-rate it per enclosed conductors



                Originally posted by doctorman
                Can I run HTWN-2 without conduit indoor?
                Very doubtful. That's what Romex was designed to accomplish, if it is permitted in your area. Not all areas permit romex.


                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • doctorman
                  Member
                  • Feb 2017
                  • 40

                  #23
                  Spoke with tech at Enphase,
                  the data sheet for enphas eM215 Voltage drop calculation https://enphase.com/sites/default/fi...Vdrop_M215.pdf

                  so I am safe using #10 wire for 90' , to their understanding no need for conduit inside the house with THWN-2 unless the inpector asks for it

                  or I can do THWN and conduit to the inside of the attic combiner and a #4 Romex to the main panel



                  Originally posted by doctorman
                  Total run is 90feet per line from the junction box to MSP + the trunk cable of the M215


                  so, to sum up, the whole plan

                  We have 2 roofs , upper and lower

                  top roof has 4 strings on it
                  15
                  15
                  13
                  13

                  lower roof has 2 strings on it
                  12
                  12

                  the plan is to bring 2 wires from each string L1 , L2 plus a Neutral and Ground per roof into the attic using #10 THWN-2 Wires
                  so
                  8 wires + N and G for top roof
                  4 wires + N & G for lower roof
                  in conduit around 35 feet run

                  from the attic go straight to the main service panel around 55' run
                  12 wires for 6 strings + N & G 14 wires of #10 Either THWN-2 or ROMEX
                  if I need conduit indoor for THWN-2 I might reconsider and do ROMEX
                  a 10/3 wire has 4 wires in it so for 14 wires total I can run 4 Romex 10/3 or 5 of 10/2



                  OR I can put a combiner box in the attic and just 1 Romex #4/3 to the main panel


                  would appreciate your help with the best option


                  Comment

                  • NewBostonConst
                    Solar Fanatic
                    • Nov 2018
                    • 113

                    #24
                    THWN needs to be in concuit.

                    I have a new workshop and I'm running 6/3 out to it. My run will need to go from my existing panel through the attic, down an external column (with normal housing siding) and then into an underground

                    Comment

                    • doctorman
                      Member
                      • Feb 2017
                      • 40

                      #25
                      Originally posted by NewBostonConst
                      thank you , Im not worried about rodents , but woud worry about NEC. so that settles it


                      NEC 300.3(A) prohibits THHN (or any other type of single wire save for a few exceptions such as single conductor MI and SE/USE, overhead wires, or an EGC) from being run outside some sort of raceway (conduit, surface raceway, cable tray, etc):
                      (A) Single Conductors. Single conductors specified in Table 310.104(A) shall only be installed where part of a recognized wiring method of Chapter 3.

                      Comment

                      • littleharbor
                        Solar Fanatic
                        • Jan 2016
                        • 1998

                        #26
                        Pulling Romex through conduit doesn't sound like any fun for anything more than a short or straight pull.
                        2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                        Comment

                        • doctorman
                          Member
                          • Feb 2017
                          • 40

                          #27
                          Originally posted by littleharbor
                          Pulling Romex through conduit doesn't sound like any fun for anything more than a short or straight pull.
                          why would I do romex in conduit
                          in conduit will be thwn
                          in house will switch to romex
                          just have to calculate the cost see which is cheaper

                          Just found out the trunk cable I was sold was landscape , eventhough w eare installing portrait , meaning I lose a lot of V in the trunk cable
                          I reduced the damage by installing the junction box in the middle of the string and beefing it up to #8 HTWN wire and #4/3 Romex

                          Comment

                          • littleharbor
                            Solar Fanatic
                            • Jan 2016
                            • 1998

                            #28
                            [QUOTE=doctorman;n391817]

                            why would I do romex in conduit
                            in conduit will be thwn




                            Reread your post #18, your words, not mine.


                            2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                            Comment

                            • Ampster
                              Solar Fanatic
                              • Jun 2017
                              • 3658

                              #29
                              Originally posted by doctorman
                              ......
                              Just found out the trunk cable I was sold was landscape , eventhough w eare installing portrait , meaning I lose a lot of V in the trunk cable
                              I reduced the damage by installing the junction box in the middle of the string and beefing it up to #8 HTWN wire and #4/3 Romex
                              Great workaround. I had similar situation once and alternated panel hookups in two short cable runs to jbox. It was a waste of cable but I had more cable than time to get correct cable.
                              9 kW solar, 42kWh LFP storage. EV owner since 2012

                              Comment

                              • NewBostonConst
                                Solar Fanatic
                                • Nov 2018
                                • 113

                                #30
                                Originally posted by doctorman

                                why would I do romex in conduit
                                in conduit will be thwn
                                in house will switch to romex
                                just have to calculate the cost see which is cheaper

                                Just found out the trunk cable I was sold was landscape , eventhough w eare installing portrait , meaning I lose a lot of V in the trunk cable
                                I reduced the damage by installing the junction box in the middle of the string and beefing it up to #8 HTWN wire and #4/3 Romex
                                It gets very hard for the next guy when you keep switching cable sizes. Someone might see the bigger wire and think they can increase the breaker size, but in reality when done and the other end of the wire it is small it is dangerous. In this situation it could cause a house fire. Upsize the THWN to match the Romex if possible. I am sure the cost is not worth a life. Correct me if I am wrong.

                                Comment