it is 42.2V for a single PV module. put 3 in series and you would have 126.6V which is by most peoples math, OUTSIDE of the 125V max spec of the optimizer.
Make the PV module a little code and it only gets worse...
The documents for the optimizers specifies that they only work with the 3 phase commercial inverters and lists the models.
the electrical is WAY WAY out of range. you are using different numbers.
a P17-335 pv module has :
1X 3X series
VMPP of 42.2V 126.6V
IMPP of 7.94A 7.94A
VOC of 51.1V 153.3V
ISC of 8.54A 8.54A
wattage 335 1,005 watts
The P730 has an absolute MAX Voltage input (Voc) of 125V < 126.6V
MPPT operating range of 12.5V to 105V < 126.6V
Max Short circuit amp (Isc) of 11A
MAX DC input current of 13.75a
rated input wattage of 730w < 1005 watts of 3 in series
Minimum string length is 8 optimizers on 3 phase 208V inverter which is less than the 6 you would have
This is Before temperature coefficient which will make this worse!
Make the PV module a little code and it only gets worse...
The documents for the optimizers specifies that they only work with the 3 phase commercial inverters and lists the models.
the electrical is WAY WAY out of range. you are using different numbers.
a P17-335 pv module has :
1X 3X series
VMPP of 42.2V 126.6V
IMPP of 7.94A 7.94A
VOC of 51.1V 153.3V
ISC of 8.54A 8.54A
wattage 335 1,005 watts
The P730 has an absolute MAX Voltage input (Voc) of 125V < 126.6V
MPPT operating range of 12.5V to 105V < 126.6V
Max Short circuit amp (Isc) of 11A
MAX DC input current of 13.75a
rated input wattage of 730w < 1005 watts of 3 in series
Minimum string length is 8 optimizers on 3 phase 208V inverter which is less than the 6 you would have
This is Before temperature coefficient which will make this worse!