Yes, I know how ethernet over powerline works. My point is that the optimizer the inverters states is unreporting is still reporting data out.
Wire probably is too small. I'll ask installer how they determined 10 AWG was ok. But, 6000/245 = 24.5 amp and assuming the SE-6000 inverter never puts out more than it's max output of 6kw, this amperage should never be exceeded, so 10 AWG over 60' is borderline bad but not egregious. An SE7600 would clearly need bigger wire with 32 amp max output.
I'm not happy about the ungrounded optimizers and I'm not happy the AWG is at best pushing the envelope or at worst simply too small. Nonetheless, I am 98% certain my issue is a bad inverter. I just went through a full reboot cycle and all 22 optimizers came up as P_OK. It is a cloudy day, so production would be small. Yet, within 60 seconds the AC VOLTAGE TOO HIGH error came up and during that minute the VAC was 245 and the VDC was in the 440s, far higher than the normal 370 the system always ran at under all conditions.
So, if all optimizers are reporting, something is causing the inverter to drive the system at an exceptionally high 440 volts and then shut down for high AC volts (though the screen never went above 245).
Weird stuff (zero production periods in middle of day) was happening back on 4/11 and 4/12 and then seems to have been simply up and died.
My installer has finally responded. So, hopefully I'll get some movement on this.
Wire probably is too small. I'll ask installer how they determined 10 AWG was ok. But, 6000/245 = 24.5 amp and assuming the SE-6000 inverter never puts out more than it's max output of 6kw, this amperage should never be exceeded, so 10 AWG over 60' is borderline bad but not egregious. An SE7600 would clearly need bigger wire with 32 amp max output.
I'm not happy about the ungrounded optimizers and I'm not happy the AWG is at best pushing the envelope or at worst simply too small. Nonetheless, I am 98% certain my issue is a bad inverter. I just went through a full reboot cycle and all 22 optimizers came up as P_OK. It is a cloudy day, so production would be small. Yet, within 60 seconds the AC VOLTAGE TOO HIGH error came up and during that minute the VAC was 245 and the VDC was in the 440s, far higher than the normal 370 the system always ran at under all conditions.
So, if all optimizers are reporting, something is causing the inverter to drive the system at an exceptionally high 440 volts and then shut down for high AC volts (though the screen never went above 245).
Weird stuff (zero production periods in middle of day) was happening back on 4/11 and 4/12 and then seems to have been simply up and died.
My installer has finally responded. So, hopefully I'll get some movement on this.
Comment