Is anyone doing direct burial for DC lines versus conduit? Code would allow me to bury USE-2 wires without conduit.
The rapid shutdown box I am looking at is set up for a 1" conduit. A 1" conduit is technically big enough for the conductors I am running, but I think it will be a pain to pull four #8s and a ground through 150+ feet of 1" conduit. I also think I could end up being over 360 degrees of bend in the conduit and need a pull box. A conduit body can be used for a pull box, but it can't be buried. I would like to avoid a giant access box in the middle of my yard just to have a conduit body accessible.
Direct burial seems so much easier other than having to be 24" deep instead of 18" deep.
The rapid shutdown box I am looking at is set up for a 1" conduit. A 1" conduit is technically big enough for the conductors I am running, but I think it will be a pain to pull four #8s and a ground through 150+ feet of 1" conduit. I also think I could end up being over 360 degrees of bend in the conduit and need a pull box. A conduit body can be used for a pull box, but it can't be buried. I would like to avoid a giant access box in the middle of my yard just to have a conduit body accessible.