I bought some 230w panels to build a higher capacity system for my hobby shop. The panel label says 60 cell, open circut voltage 37 volts and vmp 29.8 volts. I believe the panel is for a 24v system. My question is, the old panels I had were 36 cell for 12 volt system, so if these are for 24 volt system shouldn't they be 72 cell ( twice the cells for twice the voltage) or will the panel still work with 12v controller & battery.
Most Popular Topics
Collapse
Are my 60 cell panels 12 or 24 v
Collapse
X
-
-
Those would be considered 20 V panels, also called grid-tie panels. You'll probably need an MPPT controller to use them with batteries... voltage is too low for PWM in parallel at 24 V, and putting them in series will usually be out of the input voltage range of a PWM controller.
CS6P-260P/SE3000 - http://tiny.cc/ed5ozx -
I bought some 230w panels to build a higher capacity system for my hobby shop. The panel label says 60 cell, open circut voltage 37 volts and vmp 29.8 volts. I believe the panel is for a 24v system. My question is, the old panels I had were 36 cell for 12 volt system, so if these are for 24 volt system shouldn't they be 72 cell ( twice the cells for twice the voltage) or will the panel still work with 12v controller & battery.
MSEE, PEComment
-
The 29V is too low to safely rely on charging a 24V bank, which may need +30V for full recharging. Put 2 panels in series with a MPPT controller and you would be OKPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment