In San Diego, one new complication to keep in mind is that as of Jan 1, Class A fire rating for the PV system must be met for permit approval. No panel by itself will meet this rating, but installed systems can. This has put a burden of testing on the racking manufacturer, and many of the common brands will offer conditional certificates of compliance that can be attached to a permit application. Most panels are rated either Type 1 or Type 2, with Type 1 providing more options for mounting configurations. LG panels are type 2, which means that if you want to install them in a method other than flush to a steep (>2:12) roof, the racking options are more limited.
I don't know how reverse tilt is addressed with respect to fire safety, but some research into the racking and panel combinations that are allowed is probably worthwhile if the design is being seriously considered.
Information on rack and panel ratings has been collected by CALSEIA here, and may be a good starting point if you want to understand this in more detail.
Also, see in this thread from last year more discussion of the development of the fire safety requirement.