Originally posted by inetdog
entire array would have to shift from + ground reference to - ground reference and back
each line cycle. This would appear as a square wave of hundreds of volts magnitude on the
array wiring, making a HORRENDOUS radio interference generator & antenna. Some of the
AC output current would be flowing in the array. I don't know what happened when panels
first became available, but I don't believe such a design has been produced for a long time.
These days high frequency ferrite cores are able to provide isolation without the use of
a huge 60 HZ iron core. The array voltage reference to ground is fixed; EMI filters may
be applied as needed to the input & output. I'm going to suggest, a "transformerless"
inverter is one where the input & output circuits are NOT isolated; current may flow between
them. Same as small radios of the 50s & 60s.
That brings us to today; PV inverters operate with one input lead at ground potential.
Was the rule, if one conductor is not bonded to ground in the inverter, the array disconnect
must break both leads? Fronius does not bond an input to ground; they place a 1A fuse
between an input lead and ground. A ground fault will blow that fuse and the voltage be
detected by the inverter. By this theory these inverters must disconnect both leads, which
probably is never done (except here). And probably not bonded on any other inverter with
GFI function.
I'm now suggesting the above is incorrect. The rule is, or should be stated, that any
inverter with non isolated input-output (current can flow between them) require both
array leads to disconnect. Isolated inverters with one input REFERENCED to ground
(but not necessarily BONDED) require only the other lead be disconnected. Failing
that, I suspect most private installations are not compliant. Bruce Roe