Trying to trace why the inverter and meter are not getting power and it seems the problem is the AC Disconnect, though I can't for the life figure how this would go bad.
The top wires are coming from the main panel and I get a reading of 241v on the top two terminals. With the disconnect in the ON position, the bottom either reads 0V or fluctuates all over the places from 0...10...43...7. Seems all the disconnect should do is snap the bars into place when it's turned to the ON position, and the bars do snap in and visually look like they are making good contact.
Anyone ever run into this before?
The top wires are coming from the main panel and I get a reading of 241v on the top two terminals. With the disconnect in the ON position, the bottom either reads 0V or fluctuates all over the places from 0...10...43...7. Seems all the disconnect should do is snap the bars into place when it's turned to the ON position, and the bars do snap in and visually look like they are making good contact.