Actually #6 should fly at least between the combiner and the inverter, so really the only change on the permit there should be changing the #2 to #6.
The #6 on the AC side between the inverter and the service panel though does need to be #4, but that's easy to fix and I believe I can still run 3/4" conduit. I got a calculation of 33% conduit fill using 2x4AWG and 1x10AWG ground (NEC says up to 40% is ok).
As for the temperature adjustment calculation, all the conduit is in the attic, there is literally none on the roof...unless you count the 4" or so coming out of the roof and into the combiner box. I was told by the designer that anything under 24" does not need to be calculated for.
The #6 on the AC side between the inverter and the service panel though does need to be #4, but that's easy to fix and I believe I can still run 3/4" conduit. I got a calculation of 33% conduit fill using 2x4AWG and 1x10AWG ground (NEC says up to 40% is ok).
As for the temperature adjustment calculation, all the conduit is in the attic, there is literally none on the roof...unless you count the 4" or so coming out of the roof and into the combiner box. I was told by the designer that anything under 24" does not need to be calculated for.