Solar install turning out really bad - looking for some help/advice please.
Collapse
X
-
59.38V?
240 A?
I think they messed that one up too...Leave a comment:
-
The installer...err I should say...his kids? Literally a couple high schoolers, came out to put on the two missing labels that we needed.
Apparently they didn't know how to rivet the sign on the disconnect because they just double side taped it on there. They were actually on the phone with the installer who said to just tape it and he'll come back out after the inspection to secure it. WTF.
Oh, and the red tag, is supposed to say the DC conductors are ungrounded, not UNDERGROUND. SMH.
The other label they got right, and even riveted it. I think I should black out his info though, he's getting no free advertising from me...or any credit for how the job came out looking in the end.
Leave a comment:
-
Whew!! 1 inspection down, 2 to go.
Leave a comment:
-
Also, your permit called out the SolarEdge inverter with the integral AC/DC safety switch, and yours has only the DC switch. You've got AC disconnects that make it compliant, but it is just another thing the inspector could pick on if he gets the vibe this job was not done right. I'd really roll out the red carpet for the guy.Leave a comment:
-
That is strange, I don't know why the wires go from black to red and red to black in the middle terminal block. It came pre-wired from SolarEdge like that.
As for using a white wire for the DC-...well, that's my installer for you...I guess he didn't have black 6AWG wire to use? Guess we'll see what the inspection says, if they even open the disconnect. It would REALLY suck if they say it needs to be changed.
As for the combiner box, I'm not saying to make changes to the box itself...I'm saying to basically just put a fuse between the DC- coming in from the string and the DC- terminal block...I mean isn't that all it is? Isn't that the only difference between the DC+ and DC- setup right now?
Regarding the fuse size, it does look like 20 A would be justifiable. Your permit probably got approved on the basis of 10 panel strings with an Isc of 9.08 AMP, which isn't really correct in a SolarEdge system, but whatever. With 16 * 310 W panels in a string, the rated current for that circuit would be 4960 W / 350 V = 14.2 A, which would require 20 A fuses min. Your 13 panel string would be 4030 W / 350 V = 11.5 A * 1.25 = 14.4 A, so 15 A fuses looks OK for those. The 11 panel string could be sized with 15 A fuses as well.
Also, your permit called out the SolarEdge inverter with the integral AC/DC safety switch, and yours has only the DC switch. You've got AC disconnects that make it compliant, but it is just another thing the inspector could pick on if he gets the vibe this job was not done right. I'd really roll out the red carpet for the guy.Leave a comment:
-
That is strange, I don't know why the wires go from black to red and red to black in the middle terminal block. It came pre-wired from SolarEdge like that.
As for using a white wire for the DC-...well, that's my installer for you...I guess he didn't have black 6AWG wire to use? Guess we'll see what the inspection says, if they even open the disconnect. It would REALLY suck if they say it needs to be changed.
As for the combiner box, I'm not saying to make changes to the box itself...I'm saying to basically just put a fuse between the DC- coming in from the string and the DC- terminal block...I mean isn't that all it is? Isn't that the only difference between the DC+ and DC- setup right now?Leave a comment:
-
For reference, here is the picture from the manual:
Modifying the combiner box as you suggested is probably not OK. One of the things about code is that all components used must be UL listed for that purpose. Making changes to the combiner box, even if you do everything right and use a listed fuse block, might still not be compliant. Like many things electrical... it will work, but it isn't right. It would be better to do that than leave it as-is, though.
The problem with your AC disconnect ground isn't so much the ground screw, but the way you put more than one conductor in the conduit bushing. If that lug was only listed for one conductor, putting two in it isn't compliant. A clean solution would be to get rid of that extra solid conductor pigtail, and instead cut and strip the green ground wire in the loop so that you have two ends. Those ends could both be grounded to the enclosure using something like this.Attached FilesLeave a comment:
-
Leave a comment:
-
The communication is DC powerline... in other words, embedding a low power AC signal in the 350 DC voltage. I checked their patent and have been otherwise unsuccessful at finding information about what frequency the signal is at. I might try to put a scope on mine when it is running to see if I can find it. I doubt it would interfere with radio transmissions, and it is relatively reliable method of communication.
somewhere, but never actually measured anything. I don't expect it to interfere,
was more worried about it being interfered with. BruceLeave a comment:
-
He connected it to the grounding terminal inside the inverter's disconnect box, is this method ok?
I asked the guy at Home Depot for a grounding lug, he gave me a baggie of green grounding screws and said that's what I need.
Would a copper one be good, like this one on Amazon?
http://www.amazon.com/Panduit-CS70-1.../dp/B00B5WAH2SLeave a comment:
-
He connected it to the grounding terminal inside the inverter's disconnect box, is this method ok?
I asked the guy at Home Depot for a grounding lug, he gave me a baggie of green grounding screws and said that's what I need.
Would a copper one be good, like this one on Amazon?
http://www.amazon.com/Panduit-CS70-1.../dp/B00B5WAH2SLeave a comment:
-
To what did he connect that bare 6 AWG ground wire inside the inverter? A wire from the inverter straight to the electrode would be required in a transformer based inverter, to ground reference the DC side. If he ground referenced the DC side on this, that should fault the inverter, so hopefully it is just connected to the same ground terminal as the 8 AWG. I don't know how that terminal would accept two wires though.
Also, the way you screwed in the ground in the AC disconnect is not really right. It should be a listed lug, like that shown in this picture. You don't even need any extra wire to do it right, it looks like the looped green wire is long enough to get out to a lug and back with changing anything else.
Would a copper one be good, like this one on Amazon?
Leave a comment:
-
Your combiner box appears to have two problems:
1) White wire was used for the DC- conductors. In a SolarEdge system, these conductors are floating, not ground referenced. Only ground referenced conductors may be white.
2) The fuses are only on the DC+ wires. Since it is not ground referenced, fuses are required on the DC- wires as well. Those fuses were shown on your permit drawing, so there is a good chance this will fail inspection if the inspector sees it.
Using this combiner is a safety problem and it should be replaced with the permit approved model or an equivalent even if the inspector misses it. The text from the SolarEdge document specifically calls this out:
I would like it done right though, and I should have bought the specified Sunny Boxy SBCBTL6-10 combiner instead of the one I did, I only got the one I did because it was 1/2 the size and was pre-wired (I liked the MC4 connectors on there, thought it would be a cleaner install)..pricewise they are about the same. It shouldn't be too much of a problem to swap them out I don't think.
Also to confirm, it says I need 20A fuses, is that correct? My combiner uses 15A fuses right now and the permit spec'd 15A as well.
EDIT: Or another thought...can fuses be added for the DC- inside the combiner box I already have in place? I would only need 2 more fuse holders (only using 3 out of 4 now) and then run the DC- wires to the fuse holder input and a wire from each out to the DC- terminal block that's there now.
This is what I'm imagining, would this be possible? Any negative side to doing this?
I believe I followed all the rules stated in that paragraph so there shouldn't be a problem there.Leave a comment:
-
Thanks for that info. It sounds like my idea was on the right track. IN ADDITION, their inverter
communicates with the power boxes to set the output voltage of each one. That is how they
maintain a 350V string voltage. I didn't hear an explanation of how that communication is done.
This system does solve problems with shading and odd numbers of panels. The claim of 15%
more energy might apply in a difficult situation like that. I don't think they would have any
advantage over a straight forward ground mount string system that had no complex mounting
restrictions.
Leave a comment:
Leave a comment: