Had the city inspection today, kinda odd
The city inspector came today. Had a couple of quibbles about labels and one strange one, at least to me. The main panel is on the outside garage wall, the inverter is in the garage just to the side of it. The AC disconnect box is outside next to the main. He wouldn't approve it... said the inverter's in the garage, the AC disconnect has to be inside the garage.
Sure seems to me the firemen would like to have the disconnect on the outside. The installer said he has never heard of having it inside. I believe him.
He told me arguing with the inspector is futile. I believe him there too.
Soooo... I wait some more.6k LG 300, 16S, 2E, 2W, Solaredge P400s and SE5000Comment
-
I guess that he wants to see the disconnect "in sight" from the inverter, and for someone who is going to be working on the inverter, that has some merit.
Usually the NEC will accept remote disconnects if they are lockable in the OFF position.
Possibly that would satisfy the inspector if it was not obviously lockable when he saw it.
Unfortunately POCO and/or the FD may later insist on a disconnect on the outside too.
If there is a breaker in the outside panel that can also disconnect the AC feed to the GTI (i.e. not a line side tap), then you will have the best of both worlds.
Now, what about an outside DC disconnect for the panels?Last edited by inetdog; 09-29-2014, 08:24 PM.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
The AC disconnect is the standard type Square D that you can flip the lever down & padlock it. You can also padlock the cover closed. There is a 30a breaker in the main panel also.
The DC disconnect is on the inverter itself, none on the outside wall. There are none in the electrical drawing or single line drawing that was approved for the permit.6k LG 300, 16S, 2E, 2W, Solaredge P400s and SE5000Comment
-
Sorry to hear about your delay. But to be honest, I've never seem a picture of the SolarEdge inverter not together with the AC disconnect. eg. their own site http://www.solaredge.us/groups/us/in...solar-inverter. Maybe your installer is not familiar with the SolarEdge products? Anyway good luck with re-inspection.16xLG300N1C+SE6000[url]http://tiny.cc/ojmxyx[/url]Comment
-
FWIW, the most relevant section of the 2011 NEC is 690.14(C)(1):
(1) Location. The photovoltaic disconnecting means shall be installed at a readily accessible location either on the outside of a building or structure or inside nearest the point of entrance of the system conductors.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
I guess that he wants to see the disconnect "in sight" from the inverter, and for someone who is going to be working on the inverter, that has some merit.
Usually the NEC will accept remote disconnects if they are lockable in the OFF position.
Possibly that would satisfy the inspector if it was not obviously lockable when he saw it.
Unfortunately POCO and/or the FD may later insist on a disconnect on the outside too.
If there is a breaker in the outside panel that can also disconnect the AC feed to the GTI (i.e. not a line side tap), then you will have the best of both worlds.
Now, what about an outside DC disconnect for the panels?
"Location. The photovoltaic disconnecting means shall be installed at a readily accessible location either on the outside of a building or structure or inside nearest the point of entrance of the system conductors."
To clarify for others - this section of code is about the DC disconnect.
If the DC wires are inside metal conduit while inside the house then I think his DC disconnect meets the code requirement. (at least my understanding is the disconnect is built into the inverter for Solaredge inverters and that counts for a DC disconnect for this. And that there is an exception that allows the DC wires to have the disconnect be away from where it enters the structure if they're inside conduit (comply with 690.31(G)).)Comment
-
The city inspector came today. Had a couple of quibbles about labels and one strange one, at least to me. The main panel is on the outside garage wall, the inverter is in the garage just to the side of it. The AC disconnect box is outside next to the main. He wouldn't approve it... said the inverter's in the garage, the AC disconnect has to be inside the garage.
Sure seems to me the firemen would like to have the disconnect on the outside. The installer said he has never heard of having it inside. I believe him.
He told me arguing with the inspector is futile. I believe him there too.
Soooo... I wait some more.
I know the PCV pipe were big since I have 100A breaker to sub panel using 4 gauge wires..... Here are photos of inside out.Comment
-
To clarify for others - this section of code is about the DC disconnect.
If the DC wires are inside metal conduit while inside the house then I think his DC disconnect meets the code requirement. (at least my understanding is the disconnect is built into the inverter for Solaredge inverters and that counts for a DC disconnect for this. And that there is an exception that allows the DC wires to have the disconnect be away from where it enters the structure if they're inside conduit (comply with 690.31(G)).)
(1) Located where readily accessible(2) An alternating-current disconnecting means shall be mounted within sight of or in the inverter.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
True. The inverter output circuit would be covered primarily by section 705. The only relevant general location provision is in 705.22, namely
There is a requirement for an AC disconnect to be located within sight of the inverter in 705.70 But if you look at the entire section, you see that .70 applies only when the inverter itself is "...Mounted in Not-Readily-Accessible Locations. Utility-interactive inverters shall be permitted to be mounted on roofs or other exterior areas that are not readily accessible." Not exactly applicable to the inside of a garage.
It comes back to the 1st and 2nd rule of inspectors.
1. They are always right. 2. Even if they are wrong refer to rule 1.Comment