30 amp NEMA 3R rated DC disconnect is $175 - 225. 30 amp NEMA 3R AC disconnect is $14. What's so darn special about a DC disconnect? Is it that there are suckers to pluck? (Us) Or is there some physical reason why an AC disconnect, which is just a switch, won't work on DC?
Most Popular Topics
Collapse
What's so darn special about a DC disconnect?
Collapse
X
-
-
You have 2 questions.
1. The disconnect is for the fire department (and the owner in some cases for testing) to disconnect your solar PV panels when your house catches on fire. Just like your electric meter the first thing the FD will do is pull your meter out and pull the PV mods off-line.
2. As for the Disconnect itself has to do with UL listing. In order to be used in DC it has to be tested. There is nothing special about it, it is just the manufactures have not had their devices tested and listed for DC. It cost the manufactures a great deal of money to have their devices tested and listed by ULMSEE, PE -
AC circuits "stop and start" 60 times a second. This helps quench the arc when you turn off a switch.
DC flows continuously, and creates a much stronger arc, that has to have more extensive measures to quench.
Also, DC grid tie arrays, run at higher voltages - 300VDC - 600VDC, and the higher voltages are harder to quench.
Third - there are only a small fraction of DC boxes made, and they don't see the mass production "economy of scale" that the AC stuff does.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
AC circuits "stop and start" 60 times a second. This helps quench the arc when you turn off a switch.
DC flows continuously, and creates a much stronger arc, that has to have more extensive measures to quench.
Also, DC grid tie arrays, run at higher voltages - 300VDC - 600VDC, and the higher voltages are harder to quench.
Third - there are only a small fraction of DC boxes made, and they don't see the mass production "economy of scale" that the AC stuff does.Lawrence Lile, PEComment
-
But I just wait till after sunset to switch minePowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
There is a little more to it on the technical end as Mike pointed out where DC can sustain an arc longer over short distances. So there is some technical distances. If you are looking for decent pricing that is listed for both AC and DC check Square D QO line.MSEE, PEComment
-
UL Listed Alternative to DC Di$connect$
Heads up, you 24 volt people!Instead of an expensive DC disconnect, get yourself a "NEMA 3R enclosed Circuit Breaker Disconnect" from your local electrical supplier, and specify Square D QO breakers. Double check the fine print here:
Here are some other Square D Breakers listed for DC:
"Powerpact" HD, HG, HJ, HL 15-150A listed for 250VDC
Magnetic only model FH-DC 15-100A 500 VDCLawrence Lile, PEComment
-