    Need Advice on a 2.8 Xantrex PV Array System

    The system I'm building:
    Xantrex GT2.8 NA 240/208UL grid tie inverter.
    208/240 Vac
    Input voltage, Maximum Power Point range Certified operating range: 195–550 VDC.
    (Unit is operable as low as 193 VDC.)
    Absolute maximum array open circuit voltage 600 VDC
    Maximum input current 15.4 ADC (240 V), 14.9 ADC (208 V)
    Maximum array short circuit current 24 ADC

    The panels:
    Rated Power (Pmax) 240W
    Maximum Power Voltage (Vpm) 29.7V
    Maximum Power Current (Ipm) 8.08A
    Open Circuit Voltage (Voc) 36.9V
    Short Circuit Current (Isc) 8.62A
    Module Efficiency 14.8%
    Series Fuse Rating 15A
    Power Tolerance 0 ± 3%
    Maximum System (DC) Voltage 1000V/DC (IEC)

    The plan is to run 14 panels (2 strings of 7 in series) running the 2 arrays in parallel.

    Is my math correct? That'll be 258.3 Vdc running at 16.16A for a total of 3360Wdc Max. I've been told that I should add enough cells to be 10-15% above the rating of the inverter. Is this correct? Does my math add up, and is this the best configuration for efficiency? Or, should I be running a single series array with 13 panels (479Vdc 8.08A)?

    I'm new to this so please bear with me.
  • Naptown
    Solar Fanatic
    • Feb 2011
    • 6880

    #2
    Switch inverters to a Power1 which will allow the low voltage input and in a 3KW size as you are a bit over powered with the Xantrex you are considering.
    NABCEP certified Technical Sales Professional

    [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

    [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

    [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

    Comment

    • stevenh
      Junior Member
      • Jun 2013
      • 7

      #3
      Originally posted by Naptown
      Switch inverters to a Power1 which will allow the low voltage input and in a 3KW size as you are a bit over powered with the Xantrex you are considering.
      I've already purchased the Xantrex. It was a deal I couldn't pass on. Now I need to match the panels to the inverter.

      Should I just go with 12 240s in a single series array?

      Comment

      • Naptown
        Solar Fanatic
        • Feb 2011
        • 6880

        #4
        Non temperature corrected Voc on those panels is 518V If you use the coldest temp and the NEC table and multiply by 1.25 it comes in over the 600V
        Here's where location matters.
        If you are tropical and the temp never drops below 70 you could put all 14 in series
        If you live in alaska or the great white north you need to compensate for temperature coefficient. (this will be on the spec sheet of the module and expressed as a % per degree C. Remember to start at 25C and count from there as that is the starting point for this.
        NABCEP certified Technical Sales Professional

        [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

        [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

        [URL="http://www.gaisma.com"]www.gaisma.com[/URL]