Yes, lots of people on another forum have developed reliable sources for those 272's, and some 280 cells from EVE.
Did this thread discussion about surge loads inform you about the complexity of picking the right hybrid inverter? It really has nothing to do with the kWhr capacity of the batteries except the batteries need to be able to provide the kW discharge to serve the loads.
I was able to open that video after several tries. I have used that same vendor ( Emily at Shenzen Basen) before with good results. Search for Shenzen Basen to see more reviews.
30kw DIY battery for $310/kwh, which hybrid inverter is recommended?
Collapse
X
-
-
well youtubers are showing off their 272ah lifepo4 batteries now. much better price of about $120/kwh of storage.
Leave a comment:
-
The Sunny Island split phase option can manage a generator. This is their off grid solution, but as far as I can tell, doesn't work with the SMA automatic transfer switch but will manage a third party transfer switch between the grid and generator. I didn't elaborate earlier because this is an expensive solution. But user Salts bought some sunny islands cheap and did the work himself to it turned out to be a nice system.Leave a comment:
-
Good to know that there is a 240 volt split phase option. Too bad there is not a generator input. That is a feature of the internal transfer switches of most hybrids that adds to their cost effectiveness.
i do know that the generator input on the SolArk is bidirectional so it can be used for AC coupling a GT inverter. That may give SolArk flexibility in meeting the calculations for busbar adequacy by not having to go through the critcal loads panel and with another breaker. That calculation did complicate my Skybox installation with regard to the busbar rating of my critcal loads panel.Last edited by Ampster; 04-05-2021, 03:14 PM.Leave a comment:
-
When I say phase, I had to find an SMA blog posting when talking about SMA battery inverters. The SMA high voltage battery inverter is a 240VAC output device. So one SMA high voltage battery inverter per 240 VAC; not 1 per leg of 240VAC. The other thing is that the SMA automatic transfer switch doesn't manage a generator.
Their offgrid solution is SMA sunny island is a 120VAC output device. So one Sunny Island per 120vac, but you can pair two together for 240VAC.
Leave a comment:
-
Leave a comment:
-
Hopefully this helps the OP evaluate which hybrid is recomended? The answer involves a lot more analysis and understanding than the OP may have thought when he framed the question. For example my Skybox could not handle the surge loads of A/C and the typical deep well pump but it sounds like the SMA can do that easily. Yet each of them could run just fine on a 30 kW(h) DIY battery.Leave a comment:
-
Perhaps the transfer switch on the SMA works differently which may make the calculation simpler?
1) Connection to utility grid and household distribution: Maximum input and output current: 200 amp
2) Solar inverter AC connection: Maximum overcurrent protection of circuit breaker of PV inverter:50amps. Inverter AC restriction: 9600 Watt inverter power max (40amps at 240 VAC)
3) Battery inverter AC connection: Maximum overcurrent protection of circuit breaker of battery inverter: 50 amp; (remember one battery inverter per phase so the max here would be 1 SMA 6.0 battery inverter)
It looks like if you went to the trouble of installing the SMA automatic transfer switch, you could still have a 200 amp grid connection and 200 and household distribution when using an SMA battery inverter and SMA solar inverter.
Leave a comment:
-
The SMA high voltage battery inverter is 6.0 kW
Last edited by Ampster; 04-04-2021, 01:13 AM.Leave a comment:
-
Just went through this exercise for a customer that wanted a Sol-Ark hybrid inverter. One thing that stood out about this relatively new design is that it has a grid output AC max current over 32amps which means it can't be used for backfeeding without modifying a typical 200A breaker panel. I like the all-in-one design for being easy to set up and it looks like a nice user interface, but even the 8kW version is too powerful for a simple grid tie. Am I wrong about this??
I'm still recommending with the SMA storage bundle using a 10kWh BYD battery. Solidly engineered, proven quality, can be added to an existing grid-tied system, not cheap...
Or is it that the SMA solution just has less capacity?
Leave a comment:
-
Q: If all places like this went away how would folks know pump curves exist and how to use them ?
A: The same way they always have - pick up a book and get informed. Alternately these days google "pump curves" or "pump lift + GPM", get swamped with hits and spend 10 minutes learning.
Leave a comment:
-
Or is it that the SMA solution just has less capacity? If that is the case there is a smaller SolArk or the Outback Skybox if one wants to consider an All In One inverter. I have heard good things about SMA offerings but as you mentioned have not seen anything that is competitive with All In One hybrids. I am more interested in understanding the options and relative costs of the solutions. In one sense this may get us back to the title of the thread which was about "which hybrid inverter is recommended?'Leave a comment:
-
Just went through this exercise for a customer that wanted a Sol-Ark hybrid inverter. One thing that stood out about this relatively new design is that it has a grid output AC max current over 32amps which means it can't be used for backfeeding without modifying a typical 200A breaker panel. I like the all-in-one design for being easy to set up and it looks like a nice user interface, but even the 8kW version is too powerful for a simple grid tie. Am I wrong about this??
I'm still recommending with the SMA storage bundle using a 10kWh BYD battery. Solidly engineered, proven quality, can be added to an existing grid-tied system, not cheap...Leave a comment:
-
Yup, and inverter manufacturers publish specs showing surge capacity of their inverters. If people could read and understand that information and integrate that into an optimum system; there would not be much demand for forums like this.Leave a comment:
-
Yes, I looked up a table for pumps and it suggested as @oregon_phil mentioned that it also depends on how much flow one wants. For example a lift of 225 feet could be done with less than a 1 hp pump but the flow would be less than 5 gallons per minute. At that rate you would need a larger tank on the surface depending how how long you want to take showers.Leave a comment: