"3 tons of cooling = 36,000 BTU/hr.
10.5 kW electrical input to A/C unit ? You sure about that ?"
Yes, 36,000 BTU/Hr = 10.5kW (at least according to Google). But I realize his HVAC won't actually draw that much while running. My decrepit 4 Ton only draws 29 Amps @ 240V (last time I measured) or very roughly 5.5-6.0kW according to my Solar Edge consumption data while the HVAC is running.
But it's breakered at 50 or 60amps (I forget which).
Realistically, I would expect his 3 ton unit to draw ~20-25 amps continuously.
What is not clear to me, is what happens when the compressor tries to start while running on battery? Does it buzz and cause the lights to dim as one would expect if it was current starved? Is there a large voltage sag? Or does it not try at all -- suggesting the power monitoring circuity / control boards "don't like" the power quality coming from the inverters? E.g. bad ground, lack of neutral, issue with bonding, etc?
The controller for natural gas hot water heater is similarly "fussy."
10.5 kW electrical input to A/C unit ? You sure about that ?"
Yes, 36,000 BTU/Hr = 10.5kW (at least according to Google). But I realize his HVAC won't actually draw that much while running. My decrepit 4 Ton only draws 29 Amps @ 240V (last time I measured) or very roughly 5.5-6.0kW according to my Solar Edge consumption data while the HVAC is running.
But it's breakered at 50 or 60amps (I forget which).
Realistically, I would expect his 3 ton unit to draw ~20-25 amps continuously.
What is not clear to me, is what happens when the compressor tries to start while running on battery? Does it buzz and cause the lights to dim as one would expect if it was current starved? Is there a large voltage sag? Or does it not try at all -- suggesting the power monitoring circuity / control boards "don't like" the power quality coming from the inverters? E.g. bad ground, lack of neutral, issue with bonding, etc?
The controller for natural gas hot water heater is similarly "fussy."