    Originally posted by ButchDeal

    SolarEdge can and does drop off production with frequency modulation But it does not drop off individual optimizers.

    The bimodal system will need a disconnect method from the grid though to insure no back feeding or shorting from the grid.
    The bimodal inverter will also need a way to disconnect the grid tie inverter as mentioned to shut it completely off when not needed.

    Outback radian has three AC connections and frequency modulation in this way dedicating one of the AC connections to the grid, one to the grid tie inverter and one to the load.
    This is from Radian Documentation (AC Coupling Grid Tie Inverters With
    OutBack Battery-Based Inverters from 2017)


    Grid Tie Inverter Compatibility
    OutBack Power has successfully tested our AC coupling solution on SMA, Enphase and SolarEdge inverters.
    SolarEdge does not support blackout relay solutions, but has something called a Power Reduction Interface Port
    that can be used instead of a blackout relay to take the inverter offline.
    Sounds like it shuts them down. Outback calls the feature "frequency shifting" to slow down the Grid Tied Inverter.

    Leave a comment:


  • NetComrade
    replied
    Originally posted by ButchDeal

    The generator on the other hand can NOT magically create fuel when electricity is shoved down its throat....
    Gives me a laugh every time I re-read this thread.. THanks.

    Leave a comment:


  • NetComrade
    replied
    Originally posted by ButchDeal

    Why do you have so many small inverters on a single site?


    A bimodal inverter has batteries and can work on the grid and off the grid.
    It will not "fool" the solarEdge inverters but will control them to keep the battery charged and provide power to an emergency panel.
    take a look at the OutBack Radian inverters:
    http://outbackpower.com/outback-prod...ategory_id=529
    I think I finally have an answer to this question. After reading Outback's marketing material, I think this was sized so that we could connect it to Outback Radian, which has a maximum recommended wattage of 6000 (on the 8K model).

    BTW, MTV Solar has since been recommending the Schneider XW+.. I had them come out last week to assess and see what they say.


    Thanks for your patience and input.

    Leave a comment:


  • Ampster
    replied
    Originally posted by SunEagle

    It may make sense for the POCO to be able to "adjust" your energy storage system to meet the needs of a stable grid but to some people it may seem like just more of "the man" taking control of my stuff. Hopefully there is a happy medium for consumers and the POCO.
    Rule 21 has nothing to do with storage. It is the smart inverter algorithm that prevents a shock to the grid if all the grid tied inverters were to shut down at the same moment in time. At least that is my understanding. I am sure it is a result of the high rate of solar PV adoption. Hawaii and Puerto Rico have similar regulations. One of the side benefits is it makes it easier for a hybrid inverter to leverage grid tie inverter generation when the grid goes down.

    Leave a comment:


  • SunEagle
    replied
    Originally posted by Ampster

    I am just getting into a video of an Outback Webinar that seems to suggest that at least with Rule 21 compliant Gridtie inverters in California they can modulate down using a Frequency/Watt algorithm. I am hoping that is the case for my installation if I choose to go AC coupled.
    It may make sense for the POCO to be able to "adjust" your energy storage system to meet the needs of a stable grid but to some people it may seem like just more of "the man" taking control of my stuff. Hopefully there is a happy medium for consumers and the POCO.

    Leave a comment:


  • Ampster
    replied
    Originally posted by ButchDeal
    ............
    This is why the battery and bimodal system needs to be larger than the grid tie system, to handle the full charge and load.
    ...........
    I am just getting into a video of an Outback Webinar that seems to suggest that at least with Rule 21 compliant Gridtie inverters in California they can modulate down using a Frequency/Watt algorithm. I am hoping that is the case for my installation if I choose to go AC coupled.

    Leave a comment:


  • Ampster
    replied
    Originally posted by ButchDeal

    What extra capacity? If you are AC coupling you have the solar capacity of the grid tie inverter and that is it.
    You don't DC couple AND AC couple.
    No problem for me when the grid is down. My Skybox solar is 3k west facing with shadows late afternoon. My girid tie solar is 4k south facing, no shadows. If I have to choose I will take the grid tie output.
    Last edited by Ampster; 03-29-2019, 06:34 AM.

    Leave a comment:


  • ButchDeal
    replied
    Originally posted by jflorey2
    Because it provides a way to reduce solar generation, rather than cut it off completely. Agreed that you still need all that other stuff.
    that doesn't make AC coupling any simpler or easier to implement since you need all the same equipment. It makes it a little less harsh on the equipment since it isn't going to flip the grid tie on and off but will instead ramp the grid tie down.
    implementation is actually a bit more complex in that you have to do everything you would without frequency shifting as well as a few tasks to configure frequency shifting on bimodal and grid tie.

    Leave a comment:


  • jflorey2
    replied
    Originally posted by ButchDeal
    not sure why it would make AC coupling any easier to implement? you still need all the other equipment to disconnect and sizing.
    Because it provides a way to reduce solar generation, rather than cut it off completely. Agreed that you still need all that other stuff.

    Leave a comment:


  • ButchDeal
    replied
    Originally posted by Ampster

    I am waiting for the firmware update on the Outback Skybox so I can try to AC couple it to my SolarEdge grid tie inverter. The Skybox solar is enough to keep my batteries charged and run my critical loads. In a major emergency the additional 4kW capacity of the grid tie inverter would be useful to charge my EVs.
    What extra capacity? If you are AC coupling you have the solar capacity of the grid tie inverter and that is it.
    You don't DC couple AND AC couple.

    Leave a comment:


  • Ampster
    replied
    Originally posted by ButchDeal

    ..........
    Outback radian has three AC connections and frequency modulation in this way dedicating one of the AC connections to the grid, one to the grid tie inverter and one to the load.
    I am waiting for the firmware update on the Outback Skybox so I can try to AC couple it to my SolarEdge grid tie inverter. The Skybox solar is enough to keep my batteries charged and run my critical loads. In a major emergency the additional 4kW capacity of the grid tie inverter would be useful to charge my EVs.

    Leave a comment:


  • ButchDeal
    replied
    Originally posted by jflorey2
    Thanks! Good to know. It will certainly make AC coupled systems easier to implement.
    not sure why it would make AC coupling any easier to implement? you still need all the other equipment to disconnect and sizing.

    Leave a comment:


  • ButchDeal
    replied
    Originally posted by J.P.M.

    On the video: Looks like this may be another example of more non vetted and possibly dangerous nonsense from the idiot's bible.

    At least such idiocy might have a side bennie of improving the gene pool a bit.
    one would hope but the problem is that people see it and think he is an expert and tested something out. They don't know that he is just an idiot that has been lucky so far.

    Leave a comment:


  • jflorey2
    replied
    Originally posted by ButchDeal
    SolarEdge can and does drop off production with frequency modulation
    Thanks! Good to know. It will certainly make AC coupled systems easier to implement.

    Leave a comment:


  • J.P.M.
    replied
    Originally posted by ButchDeal

    You seem to be confusing two different function of the Powerwall. The CT clamps and modulation are used to prevent back feeding when the grid is operational. When the grid is down the CTs monitoring grid are NOT used, just the battery state. As long as the battery state is not full the grid tie inverter is allowed to generate as much as it can, when the battery starts to get full it throttles back the grid tie, or shuts it down (cold with a disconnect).

    This is why the battery and bimodal system needs to be larger than the grid tie system, to handle the full charge and load.

    All backup systems have to have a transfer switch to disconnect the grid and an auto-transformer to balance the legs. Not all battery systems have backup capabilities (no transfer switch and no auto-transformer); these would be used just for load shifting.

    In the video the owner did not get an automatic transfer switch to save money. It is not clear that he has a way to shut off the grid tie inverter completely either. Thus he has hacked together an AC coupled system but it likely wouldn't pass code and would definitely not be automatic, and I am not sure that it can manage the batteries since it is disconnected most of the time.
    On the video: Looks like this may be another example of more non vetted and possibly dangerous nonsense from the idiot's bible.

    At least such idiocy might have a side bennie of improving the gene pool a bit.