need help isolating/fusing generator
  • somawheels
    • Jan 2015
    • 70
    I need an isolator and 32a trip/fuse between a generator and inverter.
    The generator makes 240v AC current; Im not sure which of the wires (live, neutral, earth) must be isolated, and which must be attached to a breaker.
    Thankyou for reading.
    Isolator? No such thing exist. You need a Transfer Switch, and if you have to ask, you have no biz messing with it. Get professional help.
    • somawheels
      • Jan 2015
      • 70
      This is the last and only thing I need help with, everything else about my setup is clear to me. That's why i came here, rather than to a professional, However, I will get a professional to look at it and give it the OK.
      Isolator? It isolates the power source, so i call it an isolator, I did this purposely because because I may have been able to use the breaker as an isolator depending on its wiring.
      I assume all 3 wires need to be in the switch. I don't know if the live and neutral or just the live need to be in a breaker.
        A breaker is not an isolator, unless it is 2 breakers with an Interlock. You need a Transfer Switch rated for your loads.
        Google "breaker interlock kit"
        • somawheels
          • Jan 2015
          • 70
          Thankyou, I just ordered a 3 pole switch yesterday. can i just put a breaker on the live/line side of the circuit? Could be safer if I got an RCD but I already have one of those between the inverted and load.
            You need a "double throw" switch so that there is no switch position such that the generator and the utility power are both connected to the load at the same time.
            Doing this with two separate single throw switches, requiring you to remember to open one before closing the other, is not safe nor is it legal.
            • somawheels
              • Jan 2015
              • 70
              Thanks for the warning, no worries though as i don't have utility - im offgrid.
                In this case the inverter and the generator are still two sources that you do not want to ever interconnect. You would damage one or both if you do.
                (Unless you have a more expensive hybrid inverter with a generator support feature.)
                  It's alright, only his generator and his inverter that will be unhappy. Label the switch " MAX SMOKE "
                  • somawheels
                    • Jan 2015
                    • 70
                    ...It does have a generator support feature, and will automatically switch between generator and batteries/solar as the power source.
                    To clean up this thread: I require a simple on/off 3 pole switch with an RCB between generator and inverter. If your inverter does not seamlessly switch between your two power sources, you need a "double throw" (or 3 position) switch so only one of the power sources can supply the load at one time.
                    You might use a 2 position switch with no off position (if you don't need this switch to isolate both your powersources, but only switch between them)
                    Thanks for your help