We could spend all day wandering the web looking at neat stuff, but this is more of a forum, where folks interact with each other, a blind reference to a site where there are nnnyyyzzz is not really on topic. If there was a specific question, and you know of a specific answer (like we often refer folks to the Smartguage site where they lay out the math about how bad parallel batteries can be) that's much more in line with what we like to see. -
Check this guy and system out
go to youtube and search LDS Prepper. Look at his system he just put up. He is originally from Houston, moved to Idaho. He knows his stuff and has plenty of videos of his system.Leave a comment:
-
.....
Apparently the Hybrid Inverter, essentially performs this function by generating a programmable DC voltage source (from high voltage solar DC) to charge a battery bank(the load) which are subsequently used to generate AC which presumable is regulated and terminal voltage adjusts to the load. This is like the DC to AC conversion in a dual conversion UPS......Leave a comment:
-
You are getting good input from Inetdog. When a power supply is built, it typically is a voltage or a current
source (within practical limits). The PoCo is a voltage source, supplying whatever current the load conducts
while maintaining a stable voltage. For a GTI to supply the PoCo, it must be a current source, supplying
whatever power it has available as current into a stable voltage. A supply cannot be a voltage and a current
source at the same time; that operating point will be determined by the impedance of a load.
If a GTI were to change to output voltage reg at a defined point, it would cut off every time the line voltage
rose slightly. It the point was set way high, it would operate higher than the voltage desired when not PoCo
line connected. The only way to solve this is a method to change the inverter mode from one to the other,
which is not a feature generally available. Bruce RoeLeave a comment:
-
The problem is that when the standalone source is no longer actually supplying any power, and the GTI is able to produce more power than the load can absorb.
At that point the results will depend on just how the output voltage is regulated on the inverter or generator. In some cases the regulator will allow the voltage to rise to the point where the GTI cuts out. In other cases the circuitry of the standalone source will be damaged as it tries to reduce its output power below zero.
I understand now that a GTI has no output voltage regulation. If it did it would have to maintain that voltage on top of any Grid line variation probably as measured through output current sensing. So it would basically be an AC current source with additional AC Voltage limits all synced to the prevailing AC voltage (i.e. grid ). From a practical standpoint if the voltage were to be limited it would be by series regulation v.s. shunt as the GTI would have to massive to shunt for example: 10Kwatts of solar if there was no load.
Apparently the Hybrid Inverter, essentially performs this function by generating a programmable DC voltage source (from high voltage solar DC) to charge a battery bank(the load) which are subsequently used to generate AC which presumable is regulated and terminal voltage adjusts to the load. This is like the DC to AC conversion in a dual conversion UPS.
It is not impossible, just not what GTIs do; a GTI can not regulate it's output based on load except the SB TL with SPS which does it on a limited basis (1500 watts per plug).
EDIT: I have been reading alot and I thought I read a comment that the SPS was a simple mod, to the existing GTI. That sort of flies in the face of the current discussion so I might not be remembering that correctly.
EDIT EDIT: As per the other discussion on potential Contingency GT implementations, you run into the NEC safety interlock requirements with the grid. That is the biggest impediment to having full solar output at the GTI terminals without the grid. Not impossible just messy without doing a complete house transfer switch. The dual SB SPS is looking better.Leave a comment:
-
In my simplistic way of thinking as long as the terminal voltage at the output of the solar inverter was within range then there would be no danger of over driving anything. This would require some sort of DC-AC sine wave generation (like in the UPS) but apparently this just some type of coupled current source without any regulation. Without a schematic it is hard to discuss. You don't happen to have anything representative do you?
source (within practical limits). The PoCo is a voltage source, supplying whatever current the load conducts
while maintaining a stable voltage. For a GTI to supply the PoCo, it must be a current source, supplying
whatever power it has available as current into a stable voltage. A supply cannot be a voltage and a current
source at the same time; that operating point will be determined by the impedance of a load.
If a GTI were to change to output voltage reg at a defined point, it would cut off every time the line voltage
rose slightly. If the point was set way high, it would operate higher than the voltage desired when not PoCo
line connected. The only way to solve this is a method to change the inverter mode from one to the other,
which is not a feature generally available. Bruce RoeLeave a comment:
-
In my simplistic way of thinking as long as the terminal voltage at the output of the solar inverter was within range then there would be no danger of over driving anything. This would require some sort of DC-AC sine wave generation (like in the UPS) but apparently this just some type of coupled current source without any regulation. Without a schematic it is hard to discuss. You don't happen to have anything representative do you?Leave a comment:
-
In my simplistic way of thinking as long as the terminal voltage at the output of the solar inverter was within range then there would be no danger of over driving anything. This would require some sort of DC-AC sine wave generation (like in the UPS) but apparently this just some type of coupled current source without any regulation. Without a schematic it is hard to discuss. You don't happen to have anything representative do you?
At that point the results will depend on just how the output voltage is regulated on the inverter or generator. In some cases the regulator will allow the voltage to rise to the point where the GTI cuts out. In other cases the circuitry of the standalone source will be damaged as it tries to reduce its output power below zero.Leave a comment:
-
It is easy for it to monitor its own current output. But to prevent back driving an inverter or generator it has to be able to monitor the current at that source only. That requires a separate shunt placed in the circuit. And to distinguish between the two directions of energy flow it has to sense the phase angle of the current as well as the magnitude.Leave a comment:
-
It is easy for it to monitor its own current output. But to prevent back driving an inverter or generator it has to be able to monitor the current at that source only. That requires a separate shunt placed in the circuit. And to distinguish between the two directions of energy flow it has to sense the phase angle of the current as well as the magnitude.Leave a comment:
-
The GPS does not regulate its voltage output at all. It regulated the current that it outputs, proportional to the voltage waveform that it sees and proportional to the available panel power at the moment.
It does NOT actually raise its voltage a little bit above the line voltage, since it sees only its terminal voltage, not the unaugmented line voltage. If the current it pushes causes a voltage drop in the wiring back to the service entrance, then the GTI voltage will indeed be higher than the grid voltage, but that is a purely passive result of the resistance in the wire.
Since it does not know the "real" grid voltage, all that the GTI can do is shut down if the "grid" voltage it sees goes too high. That may be enough to protect an off-grid inverter or generator that the GTI is trying to sync to, but it is an all or nothing response.
[/QUThe SunnyBoy/SunnyIsland combination is unique in the industry in that the GTI (the SI) will proportionally decrease its power output in response to an increase in frequency of the SunnyIsland output.
A hybrid inverter and the Sunny Island have in common the presence of an internal shunt located where it can sense the direction of power flow on the external source side of the connected loads, not just the voltage present. This also requires that the "grid/generator" interface goes in series through the SI and its internal transfer switch.
Thanks for your considerate response; it is seemly rare.Leave a comment:
-
I'm saying that what you've illustrated in your drawings is nothing like what the installation manual shows. In your sketches, you are using the transfer switch to toggle between the generator and the PV system, with the loads receiving power from whichever is selected. Those same loads are also connected to the grid, with only the main circuit breaker in between. Not ok.
The installation manual shows the transfer switch toggling between grid power and generator power, with a few critical circuits moved off the main (slots 6/8 and 11) and into the switch's load center or a critical loads subpanel. The switch is interlocked so that the generator can never feed back into the grid, or any loads other than the critical ones that were relocated. Again, your sketch is using this interlock feature to prevent the generator and PV system from seeing each other... necessary for the function of your system, but insufficient to meet code. You need a hard interlock between the grid and your other sources of power, or you need a device that has that safety mechanism built in.
I'll read what inetdog has to say, he seems to have a better idea.Leave a comment:
-
...
OK I'll take you word on it but find it hard to believe that the GTI has no safety feature to prevent it's output from rising too far to an overvoltage condition without shutting down. Maybe that is really why it wouldn't work, the voltage would rise (it is not voltage regulated) with load and the GTI would shut down due to overvoltage. It is a "dumb SMA grid tie inverter" not even as smart as a dumb UPS.
How does the GTI even push the first watt of power unless it can regulate it's output voltage above the grid?
Seems like this industry has a ways to go yet if that is the case.
It does NOT actually raise its voltage a little bit above the line voltage, since it sees only its terminal voltage, not the unaugmented line voltage. If the current it pushes causes a voltage drop in the wiring back to the service entrance, then the GTI voltage will indeed be higher than the grid voltage, but that is a purely passive result of the resistance in the wire.
Since it does not know the "real" grid voltage, all that the GTI can do is shut down if the "grid" voltage it sees goes too high. That may be enough to protect an off-grid inverter or generator that the GTI is trying to sync to, but it is an all or nothing response.
The SunnyBoy/SunnyIsland combination is unique in the industry in that the GTI (the SI) will proportionally decrease its power output in response to an increase in frequency of the SunnyIsland output.
A hybrid inverter and the Sunny Island have in common the presence of an internal shunt located where it can sense the direction of power flow on the external source side of the connected loads, not just the voltage present. This also requires that the "grid/generator" interface goes in series through the SI and the internal transfer switch to get to the the loads.Last edited by inetdog; 07-12-2015, 03:22 AM.Leave a comment:
-
The installation manual shows the transfer switch toggling between grid power and generator power, with a few critical circuits moved off the main (slots 6/8 and 11) and into the switch's load center or a critical loads subpanel. The switch is interlocked so that the generator can never feed back into the grid, or any loads other than the critical ones that were relocated. Again, your sketch is using this interlock feature to prevent the generator and PV system from seeing each other... necessary for the function of your system, but insufficient to meet code. You need a hard interlock between the grid and your other sources of power, or you need a device that has that safety mechanism built in.
OK I'll take you word on it but find it hard to believe that the GTI has no safety feature to prevent it's output from rising too far to an overvoltage condition without shutting down. Maybe that is really why it wouldn't work, the voltage would rise (it is not voltage regulated) with load and the GTI would shut down due to overvoltage. It is a "dumb SMA grid tie inverter" not even as smart as a dumb UPS.
Seems like this industry has a ways to go yet if that is the case.
Google "grid tie inverter as a current source" for a better explanation than one I can provide.Leave a comment:
-
It is called a hybrid inverter. See Xantrex, Outback, Conext, etc. Expect to pay a few X more for it than for a dumb SMA grid tie inverter of equal power. You'll also need some kind of small battery for it to function properly, although it doesn't need much capacity if the rest of your contingency plan meets your needs.
OK, so the 10kW single inverter version is DOA...
How does the GTI even push the first watt of power unless it can regulate it's output voltage above the grid?
Seems like this industry has a ways to go yet if that is the case.Leave a comment: