Starting a new system in the deep Jungle of South America

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • sdold
    Moderator
    • Jun 2014
    • 1452

    #16
    Originally posted by josuemolina2000


    If my calculations are wrong, please let me know. 4x100w panels will do 400w / 12v = 33.33amps. How can I use 1 x20amp controller?

    I bought 30 amps controllers now, but I am not sure if I can use 4 panels with it. Whats the suggestion?
    A 100W panel will only produce about 5A if connected to a 12V battery. So 5A x 4 panels is about 20A.

    If you check the nameplate of the panel, it'll tell you that the voltage and current at maximum power (100W) is roughly 18V and 5A. It'll also tell you that the short circuit current (Isc) will be around 5.5A, which gives you a rough idea of the maximum current the panel can possibly produce.

    If the panel is connected to a battery directly or through a PWM controller, the panel voltage will be "pulled down" to about 12V and the current will be about 5A, or roughly 60W. What this means is that, with a PWM controller that really just operates as an on/off switch to the battery, the panel is really a 60W panel, not 100W. To get 100W out of it you'd need to use an MPPT controller and wire them in series. An MPPT controller allows the panels to "sit" at whatever voltage creates the most power, in this case about 18V/panel.
    Last edited by sdold; 10-09-2017, 01:58 PM.

    Comment

    • josuemolina2000
      Junior Member
      • May 2017
      • 17

      #17
      Originally posted by sdold

      A 100W panel will only produce about 5A if connected to a 12V battery. So 5A x 4 panels is about 20A.

      If you check the nameplate of the panel, it'll tell you that the voltage and current at maximum power (100W) is roughly 18V and 5A. It'll also tell you that the short circuit current (Isc) will be around 5.5A, which gives you a rough idea of the maximum current the panel can possibly produce.

      If the panel is connected to a battery directly or through a PWM controller, the panel voltage will be "pulled down" to about 12V and the current will be about 5A, or roughly 60W. What this means is that, with a PWM controller that really just operates as an on/off switch to the battery, the panel is really a 60W panel, not 100W. To get 100W out of it you'd need to use an MPPT controller and wire them in series. An MPPT controller allows the panels to "sit" at whatever voltage creates the most power, in this case about 18V/panel.
      My panels tags says:

      Isofoton I-100/12

      Max power: 100 +- 10% Wp
      Short Circuit Current: 6.54a
      Open Circuit Voltage: 21.6v
      Max Power Current: 5.74a
      Max power Voltage: 17.4v

      Max System Voltage 760v Safety Class II

      So, how many can I connect with a 30a PWM charge controller? Thanks in advance

      Comment

      • sdold
        Moderator
        • Jun 2014
        • 1452

        #18
        Originally posted by josuemolina2000

        My panels tags says:

        Isofoton I-100/12

        Max power: 100 +- 10% Wp
        Short Circuit Current: 6.54a
        Open Circuit Voltage: 21.6v
        Max Power Current: 5.74a
        Max power Voltage: 17.4v

        Max System Voltage 760v Safety Class II

        So, how many can I connect with a 30a PWM charge controller? Thanks in advance
        Four panels might be a good maximum for a 30A PWM controller. I'm curious what others think, but here's my logic: Guessing at the current from each panel being around 6A at 12V, 4 panels in parallel would be about 24A and 5 panels would be around 30. I don't feel good about running a PWM controller near its current limit because I recently received a couple of Xantrex/Schneider C12 controllers that had been running for years with a single 12V panel at around 6A or a little over, but then failed shortly after the addition of a second panel was added, doubling the charge current. The folks at Schneider said the likely cause of failure was running at maximum (or slightly above) in the intense heat of the summer we just had. We replaced them with 30A units.

        Not sure why someone would suggest a 20A controller for four panels, maybe it is OK and there is something I'm missing.

        Steve

        Comment

        • NEOH
          Solar Fanatic
          • Nov 2010
          • 478

          #19
          Originally posted by josuemolina2000
          Hello,
          I just wanted to double check if what I am doing will work.

          10 panels of 100w and 2 30a charge controllers. Working as 2 Sets of separate solar panels arrays 5 panels per charge controller:
          connected to the batteries, reaching around 55amps max of charge

          2 6volts 215ah batteries

          1 pure sine wave sunforce 1000w peak 2000w

          8avg cable for batteries and inverter

          Will this work?

          My needs:
          I just need to turn on my fridge (180w) sometimes during daylight, a max of 6 hours a day.
          4 LED lights for 3 or 4 hours. MAX.

          Extra, but not necessary:
          I also have a deep freezer that draws(240w MAX).
          Will my inverter run it too? How long?

          Thank you guys in advance.
          Why have you abandoned the "unlimited (free?) supply" of 20 Amp Charge Controllers?
          2 x 100 Watt PV Panels per Array / Charge controller = 16 amps each
          Install all five (5) PV Arrays ( all 10 panels ) pointed in multiple directions, in an "overlapping" arc ...
          Array #1 pointed with 2 hour Eastern bias = +30 Degrees
          Array #2 pointed with 1 hour Eastern bias = +15 Degrees
          Array #3 pointed straight up (+/-)
          Array #4 pointed with 1 hour Western bias = - 15 Degrees
          Array #5 pointed with 2 hour Western bias = - 30 Degrees
          producing a broad steady constant power stream for your Fridge during the day and more hours to recharge the battery.
          Connect all five charge controllers to the to the 12 Volt battery bank.

          Now you suggest (WHY?)
          500 Watts = 5 x 100 Watts Panels
          41 Amps = 500 Watts / 12 Volts
          But you have a 30 Amp Charge Controller?

          If you must use a 30 Amp Controller then consider ...
          300 Watts = 3 x 100 Watts Panels ( in parallel ? )
          25 Amps = 300 Watts / 12 Volts
          You have a 30 Amp Charge Controller.

          What are the RATINGS of your 100 Watt Panels?
          Voc =
          Vmp =
          Imp =
          Isc =

          What is the Make & Model of your 20 Amp Charge Controller?
          Is it PWM or MPPT ?

          What is the Make & Model of your 30 Amp Charge Controller?
          Is it PWM or MPPT ?
          Last edited by NEOH; 10-10-2017, 11:35 AM.

          Comment

          • josuemolina2000
            Junior Member
            • May 2017
            • 17

            #20
            Originally posted by NEOH

            Why have you abandoned the "unlimited (free?) supply" of 20 Amp Charge Controllers?
            2 x 100 Watt PV Panels per Array / Charge controller = 16 amps each
            Install all five (5) PV Arrays ( all 10 panels ) pointed in multiple directions, in an "overlapping" arc ...
            Array #1 pointed with 2 hour Eastern bias = +30 Degrees
            Array #2 pointed with 1 hour Eastern bias = +15 Degrees
            Array #3 pointed straight up (+/-)
            Array #4 pointed with 1 hour Western bias = - 15 Degrees
            Array #5 pointed with 2 hour Western bias = - 30 Degrees
            producing a broad steady constant power stream for your Fridge during the day and more hours to recharge the battery.
            Connect all five charge controllers to the to the 12 Volt battery bank.
            I really like this idea. The panels are like 8 years old, same with controllers. People dont want them anymore, because they dont want to have to buy batteries. so giving them away for nothing.

            Originally posted by NEOH
            Now you suggest (WHY?)
            500 Watts = 5 x 100 Watts Panels
            41 Amps = 500 Watts / 12 Volts
            But you have a 30 Amp Charge Controller?
            Because someone commented that 4 panels can be connected with the 20a CC. But I asked because my calculations were the same that you just typed.


            Originally posted by NEOH
            If you must use a 30 Amp Controller then consider ...
            300 Watts = 3 x 100 Watts Panels ( in parallel ? )
            25 Amps = 300 Watts / 12 Volts
            You have a 30 Amp Charge Controller.

            What are the RATINGS of your 100 Watt Panels?
            Voc =
            Vmp =
            Imp =
            Isc =
            My panels tags says:

            Isofoton I-100/12

            Max power: 100 +- 10% Wp
            Short Circuit Current: 6.54a
            Open Circuit Voltage: 21.6v
            Max Power Current: 5.74a
            Max power Voltage: 17.4v

            Max System Voltage 760v Safety Class II


            Originally posted by NEOH
            What is the Make & Model of your 20 Amp Charge Controller?
            Is it PWM or MPPT ?
            8 years old phocos 20a PWM CC

            Originally posted by NEOH
            What is the Make & Model of your 30 Amp Charge Controller?
            Is it PWM or MPPT ?
            New 30A PWM controllers that are inexpensive like this ones but bought on Ebay.
            https://www.amazon.com/ALLPOWERS-Cha...FP691G9GM5V4WJ

            Comment

            • NEOH
              Solar Fanatic
              • Nov 2010
              • 478

              #21
              ================================================== ==========================
              2 x 100 Watt PV Panels per Array / Charge controller
              Install all five (5) PV Arrays ( all 10 panels ) pointed in multiple directions, in an "overlapping" arc

              Array #1 pointed with 2 hour Eastern bias = +30 Degrees
              Array #2 pointed with 1 hour Eastern bias = +15 Degrees
              Array #3 pointed straight up (+/-)
              Array #4 pointed with 1 hour Western bias = - 15 Degrees
              Array #5 pointed with 2 hour Western bias = - 30 Degrees
              Producing a broad steady constant power stream for your Fridge during the day and more hours to recharge the battery.
              Connect all five charge controllers to the to the 12 Volt battery bank.
              ================================================== ====

              The above design means you buy very little equipment = VERY LOW BUDGET
              You really do need a battery !!!
              You replied that the Charge Controller is PWM, not MPPT
              PWM is not as efficient as MPPT.
              This costs you nothing to connect and try

              How many Continuous Hours of 100% sunlight will actually shine on your panels?
              What time does the sun rise above the trees in the east?
              What time does the sun set below the trees in the east?


              Max Power Point = 17.4 Volts
              So, connect two ( or three ) PV Panels in parallel to each charge controller, not in series.

              PWM mode
              =========
              12.0 Volts x 5.74 Amps x 2 = 140 Watts per charge controller
              14.8 Volts x 5.74 Amps x 2 = 169 Watts per charge controller
              NOTES:
              Watts harvested is lower and varies with battery voltage
              Do you really care since the PV Panels and CC's are free?
              You could even add a third PV Panel in parallel for more energy = more amps.

              MPPT Mode
              ==========
              17.4 Volts x 5.74 Amps x 2 = 199 Watts
              Notes:
              Watts harvested is higher and is independent of battery voltage, = increased cost.

              Estimate at Solar Noon, 5 arrays of 2 PV Panels in parallel per Charge Controller, battery at 13 volts
              Array #1 - 9.9 Amps = 5.74 Amps x 2 x 86%
              Array #2 - 11.0 Amps = 5.74 Amps x 2 x 96%
              Array #3 - 11.5 Amps = 5.74 Amps x 2 x 100%
              Array #4 - 11.0 Amps = 5.74 Amps x 2 x 96%
              Array #5 - 9.9 Amps = 5.74 Amps x 2 x 86%
              ===============================
              Total = 53 Amps x 80% = ~42 Amps in the real world x 13 Volts = 560 Watts harvested

              Big bus bar at the battery connection.

              If you need more energy in the morning, then add another PV Array + CC and point those PV Panels directly towards the morning sun = +45 Degrees East?
              If you need more energy in the evening, then add another Array + CC and point those PV Panels directly towards the evening sun.= - 45 Degrees West?
              The sun is weaker in the morning and the the evening

              An alternate design ...
              Array #1 = East +45 degrees ( and maybe 3 panels in parallel ? )
              Array #2 = East +30 degrees
              Array #3 = East +15 degrees
              Array #4 = Up
              Array #5 = West -15 degrees
              Array #6 = West -30 degrees
              Array #7 = West -45 degrees ( and maybe 3 panels in parallel ? )

              See how they have ROWS OF PANELS = ARRAYS pointing East, Up and West in this photo ...


              Will your freezer be shut and off all night?

              Comment

              • AzRoute66
                Solar Fanatic
                • Jul 2017
                • 446

                #22
                Originally posted by NEOH
                See how they have ROWS OF PANELS = ARRAYS pointing East, Up and West in this photo ...
                Great photo. Love the concept for off-grid.

                Comment

                • josuemolina2000
                  Junior Member
                  • May 2017
                  • 17

                  #23
                  Originally posted by NEOH
                  ================================================== ==========================
                  PWM mode
                  =========
                  12.0 Volts x 5.74 Amps x 2 = 140 Watts per charge controller
                  14.8 Volts x 5.74 Amps x 2 = 169 Watts per charge controller


                  An alternate design ...
                  Array #1 = East +45 degrees ( and maybe 3 panels in parallel ? )
                  Array #2 = East +30 degrees
                  Array #3 = East +15 degrees
                  Array #4 = Up
                  Array #5 = West -15 degrees
                  Array #6 = West -30 degrees
                  Array #7 = West -45 degrees ( and maybe 3 panels in parallel ? )

                  See how they have ROWS OF PANELS = ARRAYS pointing East, Up and West in this photo ...
                  https://www.solarworld-usa.com/~/med...ntronics-1.jpg

                  Will your freezer be shut and off all night?

                  Thanks for your answer.
                  Everything will be shut down after 10pm. And will not be running everyday, because power comes back. Maybe a week in a row max.

                  I got 2 6v Batt for cell towers of 215Ah.

                  I think because of my budget, time and space(Live in a hill, not a lot of space nearby) I will be doing the following:

                  Array #1 = with a: 30a PWM
                  East +30 degrees 2 panels
                  East +15 degrees 2 panels


                  Array #2 = with a 30A PWM
                  Up 4 panels

                  Array #3 = with a: 30A PWM
                  West -15 degrees 2 panels
                  West -30 degrees 2 panels


                  TOTAL of: 12 panels and 3 30A PWM CC and 12V 214ah battery bank. 1200 peak 2400 pure sine wave.


                  ALL in parallel of course.

                  4 panels per array should give from:
                  276W to 340W MAX.

                  If I add 1 more, 5 panels per array should give from:
                  345W to 425W MAX. Do you really think they could reach that high, even when they are so old?

                  Thanks
                  Last edited by josuemolina2000; 10-10-2017, 06:11 PM.

                  Comment

                  • NEOH
                    Solar Fanatic
                    • Nov 2010
                    • 478

                    #24
                    Originally posted by josuemolina2000


                    Thanks for your answer.
                    Everything will be shut down after 10pm. And will not be running everyday, because power comes back. Maybe a week in a row max.

                    I got 2 6v Batt for cell towers of 215Ah.

                    I think because of my budget, time and space(Live in a hill, not a lot of space nearby) I will be doing the following:

                    Array #1 = with a: 30a PWM
                    East +30 degrees 2 panels
                    East +15 degrees 2 panels


                    Array #2 = with a 30A PWM
                    Up 4 panels

                    Array #3 = with a: 30A PWM
                    West -15 degrees 2 panels
                    West -30 degrees 2 panels

                    TOTAL of: 12 panels and 3 30A PWM CC and 12V 214ah battery bank. 1200 peak 2400 pure sine wave.

                    ALL in parallel of course.

                    4 panels per array should give from:
                    276W to 340W MAX.

                    If I add 1 more, 5 panels per array should give from:
                    345W to 425W MAX. Do you really think they could reach that high, even when they are so old?

                    Thanks
                    OK, sounds like a plan.

                    I do not like Cell Tower batteries.
                    They are typically float type batteries and not rated for many Deep Discharges.
                    But that 215 AH battery will stabilize your Charge Controllers and the DC-to-AC Inverter which is all you really need, for now.

                    I have read, about 1/2% to 3% degradation per year on average for PV Panels, some more, some less.

                    Why not test all of the PV Panels before proceeding?
                    Under full sun ...
                    Measure the Voc = Voltage Open Circuit = 21.6 Volts
                    Measure the Isc = Amps Short Circuit= 6.54 Amps ( Special 10 Amp setting on multimeter )
                    Let us know what you measure.

                    Note that I had degraded the Net Amps = 80% x Theoretical Amps, to account for all losses.
                    You will have to deal with HEAT - which lowers the PV Voltage.
                    But the PWM Charge Controllers are already doing that, so ... Hmmm???

                    Do you have plans for a copper bus bar at the +/- battery terminals for all of these AMPS?
                    Last edited by NEOH; 10-10-2017, 07:42 PM.

                    Comment

                    • josuemolina2000
                      Junior Member
                      • May 2017
                      • 17

                      #25
                      Originally posted by NEOH
                      OK, sounds like a plan.

                      I do not like Cell Tower batteries.
                      They are typically float type batteries and not rated for many Deep Discharges.
                      But that 215 AH battery will stabilize your Charge Controllers and the DC-to-AC Inverter which is all you really need, for now.


                      Do you have plans for a copper bus bar at the +/- battery terminals for all of these AMPS?
                      Actually, I am not sure if they are for cell phone tower, they say they are for different applications, included solar.
                      Sorry is in Spanish
                      http://www.bateriasdacar.com/EnglishDacar/img/espetecnica/IMP-SOLAR-002.pdf

                      I will do the test some time next week.

                      And, no, I have no plans for a copper bus bar. I got cable #6 for my 2 6v batteries in series.

                      Oh, and BTW, I am in Ecuador, South America. So that pretty much tells you the sun inclination here.
                      Last edited by josuemolina2000; 10-10-2017, 08:49 PM.

                      Comment

                      • bcroe
                        Solar Fanatic
                        • Jan 2012
                        • 5209

                        #26
                        Originally posted by NEOH
                        ================================================== ==========================
                        2 x 100 Watt PV Panels per Array / Charge controller
                        Install all five (5) PV Arrays ( all 10 panels ) pointed in multiple directions, in an "overlapping" arc

                        Array #1 pointed with 2 hour Eastern bias = +30 Degrees
                        Array #2 pointed with 1 hour Eastern bias = +15 Degrees
                        Array #3 pointed straight up (+/-)
                        Array #4 pointed with 1 hour Western bias = - 15 Degrees
                        Array #5 pointed with 2 hour Western bias = - 30 Degrees
                        Producing a broad steady constant power stream for your Fridge during the day and more hours to recharge the battery.
                        Connect all five charge controllers to the to the 12 Volt battery bank.
                        ================================================== ====

                        The above design means you buy very little equipment = VERY LOW BUDGET
                        You really do need a battery !!!
                        You replied that the Charge Controller is PWM, not MPPT
                        PWM is not as efficient as MPPT.
                        This costs you nothing to connect and try

                        How many Continuous Hours of 100% sunlight will actually shine on your panels?
                        What time does the sun rise above the trees in the east?
                        What time does the sun set below the trees in the east?


                        Max Power Point = 17.4 Volts
                        So, connect two ( or three ) PV Panels in parallel to each charge controller, not in series.

                        PWM mode
                        =========
                        12.0 Volts x 5.74 Amps x 2 = 140 Watts per charge controller
                        14.8 Volts x 5.74 Amps x 2 = 169 Watts per charge controller
                        NOTES:
                        Watts harvested is lower and varies with battery voltage
                        Do you really care since the PV Panels and CC's are free?
                        You could even add a third PV Panel in parallel for more energy = more amps.

                        MPPT Mode
                        ==========
                        17.4 Volts x 5.74 Amps x 2 = 199 Watts
                        Notes:
                        Watts harvested is higher and is independent of battery voltage, = increased cost.

                        Estimate at Solar Noon, 5 arrays of 2 PV Panels in parallel per Charge Controller, battery at 13 volts
                        Array #1 - 9.9 Amps = 5.74 Amps x 2 x 86%
                        Array #2 - 11.0 Amps = 5.74 Amps x 2 x 96%
                        Array #3 - 11.5 Amps = 5.74 Amps x 2 x 100%
                        Array #4 - 11.0 Amps = 5.74 Amps x 2 x 96%
                        Array #5 - 9.9 Amps = 5.74 Amps x 2 x 86%
                        ===============================
                        Total = 53 Amps x 80% = ~42 Amps in the real world x 13 Volts = 560 Watts harvested

                        Big bus bar at the battery connection.

                        If you need more energy in the morning, then add another PV Array + CC and point those PV Panels directly towards the morning sun = +45 Degrees East?
                        If you need more energy in the evening, then add another Array + CC and point those PV Panels directly towards the evening sun.= - 45 Degrees West?
                        The sun is weaker in the morning and the the evening

                        An alternate design ...
                        Array #1 = East +45 degrees ( and maybe 3 panels in parallel ? )
                        Array #2 = East +30 degrees
                        Array #3 = East +15 degrees
                        Array #4 = Up
                        Array #5 = West -15 degrees
                        Array #6 = West -30 degrees
                        Array #7 = West -45 degrees ( and maybe 3 panels in parallel ? )

                        See how they have ROWS OF PANELS = ARRAYS pointing East, Up and West in this photo ...
                        Thats cool, wonder what the latitude is, and what the hourly power curve looks like? What is their cloud situation? Bruce Roe

                        Comment

                        • NEOH
                          Solar Fanatic
                          • Nov 2010
                          • 478

                          #27
                          Originally posted by AzRoute66
                          Great photo. Love the concept for off-grid.
                          Pointing all of the PV Panels due south minimizes the amount time to recharge the battery bank.
                          Lead Acid Batteries need time, lots of time, too much time ... Bulk => Absorb => Float

                          This graph ...



                          made me think about adding East - West pointing:
                          1) Generate more PV Power earlier in the day - to switch from the Battery Bank to PV power, as soon a possible in the morning.
                          2) Generate more PV Power later in the day, to delay switching to the battery bank in the evening.

                          Thus, giving the battery bank more time to recharge.
                          The challenge is get the "Orange Curve" in the graph, as wide as possible, and as high as possible.
                          The "Blue Curve" is less desirable for off-grid.

                          Comment

                          • NEOH
                            Solar Fanatic
                            • Nov 2010
                            • 478

                            #28
                            Originally posted by josuemolina2000

                            Actually, I am not sure if they are for cell phone tower, they say they are for different applications, included solar.
                            Sorry is in Spanish
                            http://www.bateriasdacar.com/EnglishDacar/img/espetecnica/IMP-SOLAR-002.pdf

                            I will do the test some time next week.

                            And, no, I have no plans for a copper bus bar. I got cable #6 for my 2 6v batteries in series.

                            Oh, and BTW, I am in Ecuador, South America. So that pretty much tells you the sun inclination here.
                            Your inclination is straight up.

                            The PDF,

                            "... Stationary Monoblock Electromagnet Free (EMEL) batteries with Lead - Silver alloy provide a minimum water consumption compared to lead - Antimony. Are the most suitable for the uses of Power Backup (Telecom, UPS) and Photovoltaic due to its long life and to its exceptional operating capacity in slow loading and unloading regimes. The main advantages of our Monoblock accumulator is the ease of handling and / or replacement of the same in in case of failure, as well as a greater reserve capacity of electrolyte, which translates into the need for low maintenance. Monoblocks, for their part, occupy very little space, install quickly and at the same time are very robust and compact. As for the difference between stationary batteries type OPzS and our monoblock is that our can be easily configured in modular benches and can reach the required capacities without have OPzS type cells that are very heavy and difficult to install. ..."

                            Whenever I see "Telecom" or "UPS", I think Float forever and fewer deep cycles.
                            Let us know how it works for you, because that is what matters.
                            Last edited by NEOH; 10-11-2017, 09:55 AM.

                            Comment

                            • josuemolina2000
                              Junior Member
                              • May 2017
                              • 17

                              #29
                              Originally posted by NEOH

                              Your inclination is straight up.
                              Sorry about this question, it might be dumb.. Are you saying I dont need to tilt them at all?

                              Comment

                              • NEOH
                                Solar Fanatic
                                • Nov 2010
                                • 478

                                #30
                                I am at 42 Degrees North Latitude, so I have a huge fixed tilt pointing south.

                                Enter you County & City ...
                                http://solarelectricityhandbook.com/...alculator.html
                                and it will display your optimum Monthly Tilt

                                For you ...
                                The sun is mostly directly overhead ( straight up )
                                Dec worst case South = 22 Degrees tilt
                                Jun worst case North = 24 Degrees tilt

                                So, if you had a Fixed Ground Mount the tilt would be fixed at +/-0 Degrees?

                                Seasonal Tilt ...
                                Last edited by NEOH; 10-11-2017, 09:54 AM.

                                Comment

                                Working...