Greetings everyone - newbie here - I have acquired the following equipment for very little $$$
17 Canadian Solar panels : CS6x-320P and a Fronius IG4000 NEG String inverter.
Specs of the panels:
Operating volts: (vmp) 36.8 Open circuit volts: (voc) 45.3
Operating current: (imp) 8.69 amps Short circuit current: (isc) 9.26 amps
Fronius IG4000 NEG:
AC max cont. output: 4000w
AC max cont. current 16.7 A
DC operating voltage range 150 - 450v
DC max system voltage 500v
DC max continuous current: 26.1 A
Doing the math I should be able to string 12 of these together to get close to the 4000 watt output, however is it safe to use the optimum voltage of 36.8 which would be close (441.6) to the 450 v max DC of the Fronius? If I calculate using the voc of 45.3 each I'm over the max of 500 at 543.6
-or-
My other option is to configure an array using pairs in series/parallel. This way the amperage doubles but the voltage drops to max voc: 271 and vmp: 220.8 with the amps going to 17,3 which is still under the max amps of the Fronius.
I have read that the higher the voltage in the string inverters the more efficient they work, however I'm leaning towards the series/parallel array since the voltage is lower.
About Me: I'm a pretty good electrician but I have zero experience installing solar panels.
Racking: I was leaning towards unirac
Any comments are much appreciated.
17 Canadian Solar panels : CS6x-320P and a Fronius IG4000 NEG String inverter.
Specs of the panels:
Operating volts: (vmp) 36.8 Open circuit volts: (voc) 45.3
Operating current: (imp) 8.69 amps Short circuit current: (isc) 9.26 amps
Fronius IG4000 NEG:
AC max cont. output: 4000w
AC max cont. current 16.7 A
DC operating voltage range 150 - 450v
DC max system voltage 500v
DC max continuous current: 26.1 A
Doing the math I should be able to string 12 of these together to get close to the 4000 watt output, however is it safe to use the optimum voltage of 36.8 which would be close (441.6) to the 450 v max DC of the Fronius? If I calculate using the voc of 45.3 each I'm over the max of 500 at 543.6
-or-
My other option is to configure an array using pairs in series/parallel. This way the amperage doubles but the voltage drops to max voc: 271 and vmp: 220.8 with the amps going to 17,3 which is still under the max amps of the Fronius.
I have read that the higher the voltage in the string inverters the more efficient they work, however I'm leaning towards the series/parallel array since the voltage is lower.
About Me: I'm a pretty good electrician but I have zero experience installing solar panels.
Racking: I was leaning towards unirac
Any comments are much appreciated.