I don't know if it is part of the UL 1741 spec, but I've noticed string inverters will fail to startup if they sense a grid voltage 5% over nominal spec of 240V. If the grid voltage is <252, they will sync to the grid and start producing power, and continue to operate as long as the grid voltage is no more than 10% over nominal spec (i.e. 264V).
In eastern Canada (and many other regions where electric heating is common), power companies run the grid hot to account for voltage drop in the winter when power draw is high. No-load voltage of 245V-250V is common. While it isn't common to see a no-load voltage over 252V, on sunny days with 2 6kW inverters running, I almost always see over 252V. Even with just one of the inverters running, 252V is common, so if I shut down one inverter for any kind of maintenance or testing, it may not start back up. One of my inverters allows me to increase the overvoltage limit beyond 264V, but so far I haven't found a way to change it on Solis 1P-4G-US inverters.
I see this issue only getting worse as more people add solar PV. As more houses on the same power phase in a neighborhood (around here power is distributed in 3 phases), that will elevate the local distribution voltage, making it more common to encounter >252V.
In eastern Canada (and many other regions where electric heating is common), power companies run the grid hot to account for voltage drop in the winter when power draw is high. No-load voltage of 245V-250V is common. While it isn't common to see a no-load voltage over 252V, on sunny days with 2 6kW inverters running, I almost always see over 252V. Even with just one of the inverters running, 252V is common, so if I shut down one inverter for any kind of maintenance or testing, it may not start back up. One of my inverters allows me to increase the overvoltage limit beyond 264V, but so far I haven't found a way to change it on Solis 1P-4G-US inverters.
I see this issue only getting worse as more people add solar PV. As more houses on the same power phase in a neighborhood (around here power is distributed in 3 phases), that will elevate the local distribution voltage, making it more common to encounter >252V.