on grid, but want off grid capability?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • mudhole
    Member
    • Mar 2020
    • 89

    #1

    on grid, but want off grid capability?

    I installed a 5kw, grid tie using a sunnyboy inverter, it has been up and working for about 2 years now.

    My question is: worse case scenario, we lose the grid, what hardware do I need to run well pump intermittently(240) and freezer? could I reconfigure my array to use an outback charge controller, and then maybe a midnite inverter, pure sine wave? from farm equipment i could scavenger 4 large deep cell 12v. I could just bypass my current inverter.

    does this sound plausible?
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    1) you will need batteries, 48V, about 100ah per KW used ( this is to provide ripple filtering for the inverter, another calculation involves Load Size and duration )

    2) you will need a Hybrid inverter, or just create a totally separate system using your existing HV DC PV array and a HV DC charge controller
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • mudhole
      Member
      • Mar 2020
      • 89

      #3
      thanks mike90250, so 1. when you say 100ah per Kw, did you mean per Kw-h? or whatever my peak Kw is?, 2. my thought was to just have a completely different inverter, just for off grid.

      Comment

      • mudhole
        Member
        • Mar 2020
        • 89

        #4
        so i estimate my well pump at 1 kwh per day and my chest freezer 1kwh per day, how do i size out the batteries and the inverter?, i calcuated out a start up amperage of around 20 amps if both units started at the same time. If my array is 5kw and i get average 5.5 sun hours a day....

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15151

          #5
          Originally posted by mudhole
          so i estimate my well pump at 1 kwh per day and my chest freezer 1kwh per day, how do i size out the batteries and the inverter?, i calcuated out a start up amperage of around 20 amps if both units started at the same time. If my array is 5kw and i get average 5.5 sun hours a day....
          Wait. So both of your loads only use 1kWh per day. but how many watts do they draw when they are running? The size of the batteries and inverter are based on what the load draws when it is running. If it runs 24 hours a day then you can say it draws (1kWh / 24hours = 41.66 watts) but I think is will draw a lot more then that when it is running. To big of a load may cause the inverter to shut down due to low battery voltage.

          So as Mike states you will need about 100ah per each kW of load.

          Comment

          • mudhole
            Member
            • Mar 2020
            • 89

            #6
            they both use around 365 kwh a year per, so per day 1 kwh per, the start up amps are 10 amps per, the running amps are 5 amps each, one at 220v x 5 amps , one at 110v at 5 amps., so if both a are running, roughly 1.5 kw load.

            so i need 150 ah battey? and at very minimum 2kw inverter?

            I just had another idea, is there just a way to trick my grid tie sunnyboy to not shut down due to grid being down? and then hook up UPS between whatever I want to run?

            Comment

            • mudhole
              Member
              • Mar 2020
              • 89

              #7
              of course I would disconnect the main line coming into the house from the grid....i am just wanting to be prepared if something goes bump in the night for a Longggg time

              Comment

              • Ampster
                Solar Fanatic
                • Jun 2017
                • 3658

                #8
                Originally posted by mudhole
                ............

                I just had another idea, is there just a way to trick my grid tie sunnyboy to not shut down due to grid being down? and then hook up UPS between whatever I want to run?
                It is not a trick per se, it is called AC coupling and it is what most hybrid inverters are capable of doing. That ability was implicit in the earlier suggetions for hybrid inverters. Depending on how old your Sunny Boy the interaction can be seamless or clunky. The latest specification of UL1741SA allows the hybrid grid forming inverter to modulate the GT grid dependent inverter. Older GT inverters can only be on or off but that can still provide some functionality to charge batteries and serve loads.
                9 kW solar, 42kWh LFP storage. EV owner since 2012

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15151

                  #9
                  Originally posted by mudhole
                  they both use around 365 kwh a year per, so per day 1 kwh per, the start up amps are 10 amps per, the running amps are 5 amps each, one at 220v x 5 amps , one at 110v at 5 amps., so if both a are running, roughly 1.5 kw load.

                  so i need 150 ah battey? and at very minimum 2kw inverter?

                  I just had another idea, is there just a way to trick my grid tie sunnyboy to not shut down due to grid being down? and then hook up UPS between whatever I want to run?
                  Answer to your last question. NO. I do not know of any device that tricks the inverter to think there is a grid. But there are inverters that can charge a battery system or provide a limited wattage output.. For that matter the one I am thinking about is made by SMA and has the secure power option.

                  Comment

                  • mudhole
                    Member
                    • Mar 2020
                    • 89

                    #10
                    so if i was able to charge a UPS, hooked up to my SMA, I would be able to run the freezer etc, well pump at night(would have to figure out how to get 220v), but either way, I would need 100ah battery per KW, so in my case 150 ah battery.

                    Comment

                    • mudhole
                      Member
                      • Mar 2020
                      • 89

                      #11
                      this just seems so clumsy, DC to AC to DC to AC

                      Comment

                      • SunEagle
                        Super Moderator
                        • Oct 2012
                        • 15151

                        #12
                        Originally posted by mudhole
                        this just seems so clumsy, DC to AC to DC to AC
                        They do make water pumps that run directly from a solar panel and actually have a float switch to turn it off if the tank gets full.

                        Comment

                        • Mike90250
                          Moderator
                          • May 2009
                          • 16020

                          #13
                          Originally posted by mudhole
                          thanks mike90250, so 1. when you say 100ah per Kw, did you mean per Kw-h? or whatever my peak Kw is?, 2. my thought was to just have a completely different inverter, just for off grid.
                          For every KW of power the inverter produces, there needs to be about 100ah of battery ( @ 48V. or 200ah battery @ 24V) to "buffer" the 120Hz surges the inverter draws. too small of battery and the inverter starts distorting it's output and generating excess internal heat. If you have 2kw of loads, you need 200ah of battery to keep the inverter safe. ( all in the fine print of the manual)
                          This is totally different than the amount of battery required to sustain a load for a set amount of hours.

                          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                          solar: http://tinyurl.com/LMR-Solar
                          gen: http://tinyurl.com/LMR-Lister

                          Comment

                          • littleharbor2
                            Solar Fanatic
                            • Jan 2016
                            • 223

                            #14
                            You can go with a separate hybrid inverter or another option is using a Sunny Island inverter in conjunction with your Sunny Boy GTI. This combination may require only certain models of Sunny Boy inverters. so maybe or maybe not an option for you.
                            2 Kw PV Classic 200, Trace SW 4024 460ah,

                            Comment

                            • mudhole
                              Member
                              • Mar 2020
                              • 89

                              #15
                              so, the hybrid inverter will still run when the grid goes down? if so, how does that work without the danger of linesmen getting electrocuted?