Is there an inverter that will run on solar during power outages?
Is there an inverter that will run on solar during power outages?
Collapse
X
-
-
-
Comment
-
On the SMA with secure power supply, I take it that you just run a wire from the connection to a dedicated outlet?Comment
-
As foggysail mentioned the IQ8 is still new to the US and may work if the grid is down but I do not know what other equipment is needed to make it work. You will have to do more research.Comment
-
There is fundamental issue that US electrical code requires that all panels on an occupied dwelling are shut down immediately when grid power is lost so that the wiring from the back of the panels to the main panel is not energized. It is called Rapid Shutdown. What is Rapid Shutdown and why was it implemented in the United States? - AC Solar Warehouse Therefore trying to get power out of an array that is required to be shut down by code is a problem. Note, if you have ground mount panels or they are not on an occupied dwelling than you may find a solution as rapid shutdown is not required.
I really do not know how a new hybrid system with roof mounted panels are going to get away with this barring a code change.Comment
-
Peakbagger, that article is about protecting fire fighters from a shock hazard.
The section prohibiting BOTH roof and ground mount grid connected systems from operating when there is a loss of grid power is in Section 705.40 of the 2020 NEC.
NFPA 70®: National Electrical Code® It's free to view.Comment
-
Comment
-
Your call, I have a Sunny Island Inverter which is swiss army knife of inverters (but it needs a charge controller. There were a lot of the SMAs for sale for relative cheap aftet the DC Solar auctions but that source is drying up. The SPS units have lot of limitations.Comment
-
I was thinking about getting a couple of the Sunny Boy SB5.0-1SP-US-41. Is this a decent inverter?
Comment
-
Peakbagger, that article is about protecting fire fighters from a shock hazard.
The section prohibiting BOTH roof and ground mount grid connected systems from operating when there is a loss of grid power is in Section 705.40 of the 2020 NEC.
NFPA 70®: National Electrical Code® It's free to view.Comment
-
If you buy two of them you in theory will have two 2000 watt 120 volt manually switched outlets (one for each inverter). Given there is zero surge capacity or ride through for diminished panel output (a cloud passing by) I think having a small UPS plugged into the outlet might be the best option.Comment
-
Mike, I think we are talking about two different things. Off grid systems are legal and do not need to have UL 1741SA protections if not connected to a grid. On the other hand the RSD requirements appear to be applicable to all PV systems on occupied dwellings. I do not claim to be a code pro but would be willing to be educated. It would be helpful if you stated the actual chapter and section of the code rather than just a link to the code.Comment