I have a small array of four Mission Solar 340W panels with IQ7+ micros that I installed five months ago and that has been working flawlessly ever since.
This morning I noticed on my egauge monitor that this array was only producing approx. 290W of power instead of the approx. 1100W it usually puts out. Also, this one microinverter had started up kind of late in the morning with the other three ones not producing at all. Yesterday, everything was normal! We had a storm and wind come through, but the panels worked fine the day after that storm. I have another array that is independent and that is producing power as always.
Here is what I did:
1. I checked the AC connection into my breaker box which is fine and has 251V.
2. I checked the Q cable under the panels with a non-contact voltage tester and also got line voltage to each panel.
3. I checked the Q cable wire connectors which seemed all tight and ok.
4. Put a clamp ampere meter around one of the phases in my breaker box to see if perhaps my energy monitor's CT was faulty. I registered no flow of current on either of the two channels.
Cycling the breaker does nothing. Tried it multiple times. I am puzzled that one of the four micros did produce some power this morning for a few hours. After I cycled the power, that microinverter would not come online anymore.
I have my micros registered with Enphase and might have to call them. I DO NOT have the Envoy system (due to the small system size not worth it for me). I have a distribution box in my attic and will double check if the transition from Q cable to Romex is tight, but I don't see why there should be a problem.
What could be going on with my IQ7+ inverters?
This morning I noticed on my egauge monitor that this array was only producing approx. 290W of power instead of the approx. 1100W it usually puts out. Also, this one microinverter had started up kind of late in the morning with the other three ones not producing at all. Yesterday, everything was normal! We had a storm and wind come through, but the panels worked fine the day after that storm. I have another array that is independent and that is producing power as always.
Here is what I did:
1. I checked the AC connection into my breaker box which is fine and has 251V.
2. I checked the Q cable under the panels with a non-contact voltage tester and also got line voltage to each panel.
3. I checked the Q cable wire connectors which seemed all tight and ok.
4. Put a clamp ampere meter around one of the phases in my breaker box to see if perhaps my energy monitor's CT was faulty. I registered no flow of current on either of the two channels.
Cycling the breaker does nothing. Tried it multiple times. I am puzzled that one of the four micros did produce some power this morning for a few hours. After I cycled the power, that microinverter would not come online anymore.
I have my micros registered with Enphase and might have to call them. I DO NOT have the Envoy system (due to the small system size not worth it for me). I have a distribution box in my attic and will double check if the transition from Q cable to Romex is tight, but I don't see why there should be a problem.
What could be going on with my IQ7+ inverters?