I was reviewing NEC code requiring the dc wiring once it enters the building since my inverters are going in a detached garage.
The code states:
690.31(G) Photovoltaic System Direct Current Circuits on or in a Building. Where PV system dc circuits run inside a building, they shall be contained in metal raceways, Type MC metal-clad cable that complies with 250.118(10), or metal enclosures from the point of penetration of the surface of the building to the first readily accessible disconnecting means. The disconnecting means shall comply with 690.13(B) and (C) and 690.15(A) and (B). The wiring methods shall comply with the additional installation requirements in 690.31(G)(1) through (4).
If I am reading correctly, does this mean once the pv wires go through the exterior walls, everything needs to be in metal race (rigid metal conduit [rmc], electrical metal tubing [rmt], or flexible metal-clad cable, until it reaches the inverter. In my setup the wires will enter, then hit fuses, then make their way to the inverter.
The code states:
690.31(G) Photovoltaic System Direct Current Circuits on or in a Building. Where PV system dc circuits run inside a building, they shall be contained in metal raceways, Type MC metal-clad cable that complies with 250.118(10), or metal enclosures from the point of penetration of the surface of the building to the first readily accessible disconnecting means. The disconnecting means shall comply with 690.13(B) and (C) and 690.15(A) and (B). The wiring methods shall comply with the additional installation requirements in 690.31(G)(1) through (4).
If I am reading correctly, does this mean once the pv wires go through the exterior walls, everything needs to be in metal race (rigid metal conduit [rmc], electrical metal tubing [rmt], or flexible metal-clad cable, until it reaches the inverter. In my setup the wires will enter, then hit fuses, then make their way to the inverter.
Comment