SMA Error Code 6803

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Salts
    Solar Fanatic
    • Sep 2019
    • 216

    #1

    SMA Error Code 6803

    I have an SMA Sunny Boy SB6.0-1US-40 (Actually I have two of them now)

    This past weekend, I added a second inverter and a new string of panels. I also transferred over a string from the 1st inverter to the new (identical) inverter.

    Now the first inverter is throwing an error code 6803. Its making power just fine, but it isn't happy. When I looked up the code, it basically telling me that STRING A is missing. Well Duh, I transferred STRING A to the 2nd inverter.

    How do I clear the code? The SMA manual is of no help.

    I tried logging into the inverters setup menu and turning off the string monitoring option.. ON/OFF and it was on so I turned it off.. but the inverter is still throwing the code.

    Any ideas?

    Thanks!
  • sabersix
    Member
    • Mar 2015
    • 84

    #2
    I did a Google search on SMA 6803 and found this: "Check whether a string is connected to input A. If a string that once was connected is not used anymore, the string-failure detection must be reset."

    Here is what I found for string failure detection. This may get you in the right area.

    Activating String-Failure Detection:

    Activate the user interface ( > Establishing a connection to the user interface).
    Log into the user interface as an Installer.
    On the right-hand side of the menu bar, select the menu User Settings ( > Start Page Design of the User Interface).
    In the context menu, select [Starting the installation assistant].
    Select [Save and next] until you reach the String configuration step.
    Activate string-failure detection and configure it as required.
    Last edited by Mike90250; 06-10-2020, 12:01 PM. Reason: restored as a possssible addition to original troubleshooting. Moderator..
    5.775 kW System: 21 SolarWorld SW275 x 1 SMA 5000

    Comment

    • Salts
      Solar Fanatic
      • Sep 2019
      • 216

      #3
      Originally posted by sabersix
      I did a Google search on SMA 6803 and found this: "Check whether a string is connected to input A. If a string that once was connected is not used anymore, the string-failure detection must be reset."

      Here is what I found for string failure detection. This may get you in the right area.

      Activating String-Failure Detection:

      Activate the user interface ( > Establishing a connection to the user interface).
      Log into the user interface as an Installer.
      On the right-hand side of the menu bar, select the menu User Settings ( > Start Page Design of the User Interface).
      In the context menu, select [Starting the installation assistant].
      Select [Save and next] until you reach the String configuration step.
      Activate string-failure detection and configure it as required.
      I found all that via a google search as well.. Tried the installation assistant as well as under the "Device parameters" tab, under DC SIDE, there is a string detection menu (See picture)

      Tried resetting it there as well. Tried turning it off and on, tried resetting operational data, and tried different combinations (ordering), still throws the code.

      What the hell SMA?

      I'm wondering if this has something to do with string ordering. A must be used before B and B must be used before C. Since I disconnected A and only using B and C inputs, the inverter is having a hissy fit.

      Screenshot_2020-06-10 SMA device - Device parameters.png
      Attached Files

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Then I'd try moving C to A and reset.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • solarix
          Super Moderator
          • Apr 2015
          • 1415

          #5
          There is a parameter down in the operations menu called something like " .... inhibition reset" that will remove any error messages.
          Might have to call SMA tech support though....
          BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

          Comment

          • Salts
            Solar Fanatic
            • Sep 2019
            • 216

            #6
            Originally posted by solarix
            There is a parameter down in the operations menu called something like " .... inhibition reset" that will remove any error messages.
            Might have to call SMA tech support though....
            Winner!
            Under "Device Parameters" tab then >>Device >>Operation >>Reset Operating Data >>Dropdown menu to "Reset Events"

            Error message gone! My inverter is happy again.

            Thank you Solarix!

            Comment

            • solarix
              Super Moderator
              • Apr 2015
              • 1415

              #7
              Salts: You are welcome. (From the trenches of inverter reliability)
              BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

              Comment