Solaredge ground fault isolation fault
  • qrper
    • Dec 2019
    • 38
    Be VERY careful with a megger. They often use high voltage to test for leakage, and most panels are only rated to 600V. You risk damage to panels if you test above the panel rating. Some +250V panels now come with a 1,000v rating, but know what your test gear is putting onto the panels.
    Will be! The test will use 500 V dc. According to SolarEdge, the two leads from the panel are shorted together and then they connect to the positive side of the megger. The negative side goes to the frame or array mounting structure. screenshot_226.png
    • emartin00
      • 511
      I had an isolation fault on my SolarEdge array last year. As you have realized, it is not necessarily the same as a ground fault.
      The issue I had was that one of the conduit connections had come loose and the entire vertical section of conduit filled with water and froze. The ice caused enough damage to the insulation of one of the wires to generate the isolation fault. Not enough to cause any ground fault, just enough to partially compromise it's integrity. As soon as the ice melted I pulled new wires and it worked fine again.
      I would check all of you wires and make sure they are properly rated for wet conditions, and you don't see any damage. Also check all connections to make sure they are water tight.
      • qrper
        • Dec 2019
        • 38
        That about sums the issue up. Like you said, it's not a ground fault, but an isolation fault.
        I've triple checked all the connections, every MC4 was popped open and inspected. Because this is a ground mounted array, none of the wires are in conduit. However that being said, the wires are PV rated 1000Vdc direct burial and so on.
        My Megger should be here today, if UPS shows up early, they don't usually make it here until later in the afternoon, and with snow and rain forecasted for this afternoon, may not get much done.
        I still suspect those used panels I have on half the array.
          • 5209
          much done.
          You could start taking things apart, but do not leave MC4s hanging in the weather. It will not take
          very long for the contacts to start corroding. I made up a bunch of dummy plugs for protection,
          with the wire hole sealed and the clips ground off. Bruce Roe
          • qrper
            • Dec 2019
            • 38
            Most likely UPS won't be here until 4-5 pm, and then It's suppose to rain. That's a good idea about using MC4 connectors as plugs. However, I'm going to leave all the wiring intact until the meter/weather corporates a bit.
            BTW.. disconnected the used panels sub-array and the isolation value as reported by the Solaredge inverter is now 11,000k Ω. With the used panels, this morning it was 593KΩ. According to Solaredge, anything under 600KΩ will fault the inverter. The other day, I checked and isolation value was 600.11kΩ and the inverter was still producing power.
              • 5209
              My own measurements on a pair of 2 year arrays each showed some 100 megohms to ground,
              at 450 VDC including 56 panels in sun, 460 feet of 6 gauge wire in plastic conduit, and all the
              PV wire connecting the panels to a combiner box. This in Feb. The leakage may not be linear
              with applied voltage, which is why I would not use a simple ohm meter. Bruce Roe
              • qrper
                • Dec 2019
                • 38
                I'm not much of a car guy. However the friends that I know that tinder with cars have always told me you need the right tool for the job.
                How true!
                The Klein megger showed up a bit earlier than UPS normal deliveries.
                It was getting late, but the results, while not eye openers, sure confirmed what I had thought to be the problem.
                The used modules are not worth a crap in this grid tie installation.
                According to Solaredge, a good module should be at least 80MΩ when both leads are shorted together and measured to the frame.
                To set a baseline, I tested one of the new Hyundai panels and it should 4000MΩ
                I tested one of the used Trina panels and it showed 1.8MΩ
                One panel would not test because the meter detected voltage to ground. That was the panel that I read 27 Vdc with the Fluke to ground. I never did break out the Simpson 260.
                I checked random panels out of the 12 and some were in the 100MΩ to 1200MΩ.
                Then there were the ones that showed 2MΩ, 30MΩ, and 40MΩ.
                Clearly these panels won't be able to be used in a grid tie installation. I wonder if that is why they were pulled to begin with?
                Bottom line, without that Megger meter, I'd still be chasing my tail.
                Now... what to do?
                I'm mike
                • foo1bar
                  • 1833
                  Now... what to do?
                  If it were me, I'd junk the one that has a short.
                  And see if removing that got things back working.
                  I'd probably test each of the other 11 and write down what the test results were so I could check them the next time I had cloudy/rainy weather and was having problems.
                  Since it was working most of the time, just giving a fault on cloudy/rainy days, I think there's a good chance it'll work fine once the panel with the short is removed.