Building Reserve and Using KWH

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • bcroe
    replied
    Net Metering year 11 concluded, generated about 28,800 kWh.
    Still running the original panels and inverters. With the relatively
    warm and somewhat less cloudy winter, the surplus was around
    5,600 kWh given as a gift to the PoCo. The only original wiring
    is the 220 ft buried DC conductors between the combiner box
    and the inverters. Bruce Roe

    Leave a comment:


  • Rade
    replied
    Originally posted by Ampster

    POCO is Power Company.
    Merci!

    Leave a comment:


  • Ampster
    replied
    Originally posted by Rade
    Question: What is a "POCO"? It's not an acronym I am familiar with.
    POCO is Power Company.

    Leave a comment:


  • Rade
    replied
    Question: What is a "POCO"? It's not an acronym I am familiar with.

    Leave a comment:


  • bcroe
    replied
    This has been a year of very little rain, but local farmers managed to
    get an average corn crop anyway. There were a lot of clouds that
    did not produce any rain, just hurt solar. As of 1 Nov NetMetering
    winter reserve matched my past best, 14,000 kWh. Usually it then
    starts to reduce, but record warm weather and a few more sunny
    days have it still holding 13 Nov. With any luck there will be plenty
    of kWh thru this winter. Equipment has been doing well since the
    switch repair.

    Bruce Roe

    Leave a comment:


  • PNPmacnab
    replied
    Originally posted by bcroe

    Once again Nyle announced the e8 water heating heat pump adapter,
    might soon be available. It is still in the process of being Energy Star
    certified, UEF tested, UL tested, and other things. If I ever get one,
    the energy reserve might be exhausted, better than giving it away.

    IMGP2436.jpg
    A friend of mine just got a e8 end of May and finally got around to installing it. He is quite impressed. He got build #4, just after the ones sent off for regulatory testing. So, I guess that is still experimental as it has no certification. Surprised it is a 120V unit with the market being primarily commercial. He uses it in singe pass full temperature output.

    Leave a comment:


  • bcroe
    replied
    Originally posted by DanS26
    Bruce, I use silver conductive grease on every connection and a torque screwdriver or wrench. Not to be confused with dielectric grease. It’s expensive but we’ll worth it IMO. Use very sparingly as excess will short a circuit. If + and - are near each other.
    Never had a connection failure in my system.
    I am again bringing the main PV wiring into a more regular review,
    even using a temp gauge to check for a box heating up after a
    few hours at max power. I will be using some kind of terminal
    protection on everything now. And spare shutdown assemblies
    are prepared and sealed, just in case. The post mortum hints to
    me, the issue has been the aluminum terminal block that came
    bolted to the DC shutdown switch assembly. I am replacing all
    of these with copper terminal blocks + anti corrosion stuff.

    This year the big solar item is the smoke. Usually not so common
    here in nothern IL. Even smoke not looking so thick, has a big
    impact on solar energy. I am used to seeing the 15KW system
    peaked out for nearly 8 hours a day many times. But recently it
    has trouble getting up to the full 15KW capacity. Even when the
    sky is not cloudy, production might be down 20% or more. Still
    the array is fighting it, energy reserve is about 7.8MWh vs 8MWh
    best at this date.

    Then there is air quality, worst numbers I have ever seen. But
    smoke containts physical particulate, which my electronic air filter
    can remove no matter how small. The furnace blower operates it
    around 20 minutes every hour. This really works, even before the
    smoke, I could see that the dust particles in a beam of sun were
    way down. The overall PV system produces enough energy to
    allow this luxury (?) at no extra cost beyond cleaning the filter.
    The blower motor (a standardized direct drive) was recently
    replaced as the original was about to fail. All motor wires were
    the same, though I did need to touch up the impeller balance.

    Bruce Roe

    Leave a comment:


  • DanS26
    replied
    Bruce, I use silver conductive grease on every connection and a torque screwdriver or wrench. Not to be confused with dielectric grease. It’s expensive but we’ll worth it IMO. Use very sparingly as excess will short a circuit. If + and - are near each other.

    Never had a connection failure in my system.

    Leave a comment:


  • Mike 134
    replied
    Originally posted by bcroe
    After a decade the 15KW system here has again developed
    wiring problems. The twin 7.5KW inverters normally are a
    match to around 1%, but lately EAST was lagging some. A
    quick check with the clamp on DC ammeter indicated all
    strings were close to a match. More checking, after half a
    day running full power (that is up to 8 hours with this
    configuration) the EAST DC disconnect box was getting pretty
    warm.

    As usual I set up a night work light and waited for the darkness.
    Inside the Square D 361 box a 6 gauge wire looked like it
    was cooking its insulation. The 361 is rated 30A against
    the 22 I run, and 600VDC against my 400, 3 contact positions.
    Something about the plus array wire was making poor contact
    and getting ready to burn out. It was not my wire clamp screw.

    I had this same failure on another contact years ago, I had
    just moved the wires to the spare position. Something was
    not making good contact, not sure if it was the bolts holding
    metal together, or the switch contact. Is there a contact lube
    that should be used on these?

    Fortunately I have a lot of spare parts, and these boxes are
    designed so a few screws from the open door side allow
    replacing whole units. I found a nice switch section, made
    sure all its screws were pretty tight, and soon had it installed.
    Hand test today indicated proper cool operation.

    There are plenty of the 361 outdoor boxes on Evil Bay, some
    with 600V fuses (that I do not need), and some with just a
    switch. Bruce Roe PVburnedDC.jpg
    Is that brownish color light rust on the rivets? Perhaps some condensation over the past 10 years leading to the poor connection.

    Leave a comment:


  • bcroe
    replied
    After a decade the 15KW system here has again developed
    wiring problems. The twin 7.5KW inverters normally are a
    match to around 1%, but lately EAST was lagging some. A
    quick check with the clamp on DC ammeter indicated all
    strings were close to a match. More checking, after half a
    day running full power (that is up to 8 hours with this
    configuration) the EAST DC disconnect box was getting pretty
    warm.

    As usual I set up a night work light and waited for the darkness.
    Inside the Square D 361 box a 6 gauge wire looked like it
    was cooking its insulation. The 361 is rated 30A against
    the 22 I run, and 600VDC against my 400, 3 contact positions.
    Something about the plus array wire was making poor contact
    and getting ready to burn out. It was not my wire clamp screw.

    I had this same failure on another contact years ago, I had
    just moved the wires to the spare position. Something was
    not making good contact, not sure if it was the bolts holding
    metal together, or the switch contact. Is there a contact lube
    that should be used on these?

    Fortunately I have a lot of spare parts, and these boxes are
    designed so a few screws from the open door side allow
    replacing whole units. I found a nice switch section, made
    sure all its screws were pretty tight, and soon had it installed.
    Hand test today indicated proper cool operation.

    There are plenty of the 361 outdoor boxes on Evil Bay, some
    with 600V fuses (that I do not need), and some with just a
    switch. Bruce Roe PVburnedDC.jpg

    Leave a comment:


  • bcroe
    replied
    Here I am again, smoke from wild fires in the NW is sending haze over
    the IL area again. While not terribly severe, it is enough to cause the
    inverters to drop out of clipping (about 7600W each), to more like 7300
    or 7400W. Bruce Roe

    Leave a comment:


  • DanS26
    replied
    I recently added an antenna to my mid-1800's barn with a very slick metal roof.........

    IMG-0756.jpg

    Leave a comment:


  • bcroe
    replied
    The pair of Fronius IG 7.5 are just doing their thing after 10 years.
    The new-out-of-the-box spare is mounted next to them, just need
    to move 2 wires and throw a breaker if backup is needed. Guess
    it might be a good idea to actually try that some day, might take
    commissioning to get it going. No more worries about high line
    voltage programming since the heavy feed was installed in 2020.

    Looking good so far this year, the 15KW inverter plant delivered
    150KWh today. The previous year was rather poor sun, generation
    was a bit under 28,000 KWh. I got to keep more of that, the 2020
    heavy feed is delivering close to an extra 1000KWh of generation
    to the meter for credit. I made it past 1 April reset with a 1700 KWh
    in the black surplus (given to the PoCo). Most stuff here just ran,
    one of the 6 heat pumps needs attention.

    Some energy ideas, new mounts could boost output and reduce snow
    accumulation. And more house insulation, windows and in attic.
    Observation of loads is ongoing, but Energy Star and some mods
    have brought efficiency to a high level. Design a clipping level monitor.

    However most attention today is catch up on stuff ignored for the
    first PV decade. Need to get a new antenna up before the old one
    falls down, still considering J.P.M.s advice how to (not) do that on
    the steel roof. Some really big chunks of snow slid down this winter,
    I am building some clamp on slide restrictors using the same 6061
    aluminum and 18-8 SS bolts that have worked so well holding panels.
    Bruce Roe

    Leave a comment:


  • DanS26
    replied
    hey Bruce...just wondering how those 7.5 Fronius inverters are holding up?

    I wake up every morning and think I'm glad to see another day. My eleven year old Fronius transformer inverters must think the same thing........well maybe if they were AI.

    Leave a comment:


  • bcroe
    replied
    Originally posted by bcroe
    So another year, Nyle periodically says the unit will
    be available, but once again failed to deliver it. Bruce Roe
    Once again Nyle announced the e8 water heating heat pump adapter,
    might soon be available. It is still in the process of being Energy Star
    certified, UEF tested, UL tested, and other things. If I ever get one,
    the energy reserve might be exhausted, better than giving it away.

    Although this property was purchased with an eye to eliminating the
    building maintenance (painting, etc), there was one standard roof on
    the house. The shingles, facia, and rain gutters got replaced in 2021,
    but now it was so slippery I could hardly go up there. As discussed
    earlier, clamps to attach are quite expensive, $5 and up each. After
    a bit of experimentation, I came up with this DIY version, using the
    same 6061 aluminum and 18-8 hardware as the ground mounts. I
    put some special conductive tape over the roof ridge first, to avoid
    scratching the paint too much.

    This is not normally under much stress, it just gives me a handhold
    and a place to connect a safety strap. Note the foot friction strips
    which stick to the roof. Bruce Roe

    IMGP2436.jpg
    Last edited by bcroe; 05-04-2023, 12:14 AM.