    I believe another challenge for the direct burial heavy feed has been solved.
    The digger on my 18 inch deep trencher has been lengthened enough to
    reach 24 inches. Will not push it too hard.

    I still need to locate the original buried power cable, to avoid hitting it. Bruce Roe

    trencher243.JPGtrencher245.JPG

    Leave a comment:


  • bcroe
    replied
    Originally posted by bcroe
    The aluminum direct burial wire arrived, 288 lb for 300 foot Triplex. Looks like
    most of the connections can go straight into my box terminals, 2 of the 6 will
    need to be reduced to 2 gauge copper to go into a 100A breaker.
    Think I solved the transition of 4/0 AL to 1/0 CU house end of my triplex AL
    buried cable. These terminals are designed for AL or CU 200A circuit, mounted
    on half inch bakelite. They came from my 200A meter boxes, in the center to
    splice the neutral wires together. I removed them (as many probably do)
    because that wire runs straight thru, no connection. No bucks spent. The
    house end distribution box already has a suitable N terminal for that wire.

    Here the 1/0 is already wired to the (4 position) 100A breaker, 4/0 AL will come in
    on the right. Until the project completes next spring, the 80A breaker just above
    will continue to feed through adequate but less efficient 4 gauge.

    Oh I discovered a RANDOM blower operation mode for my electronic
    thermostat. I still would not use it, my unit is not random, can set and modified
    times as I decide

    Bruce Roe

    4010trans.JPG4010cover.JPG
    Last edited by bcroe; 10-05-2019, 12:44 PM.

    Leave a comment:


  • Ampster
    replied
    That was a simple solution for the inverter side. It also reduced the number of connections.

    Leave a comment:


  • bcroe
    replied
    Originally posted by Ampster

    I would use a split bolt because I wouldn't trust a wedge to stay under various temperature changes. . If the copper and aluminum are fresh just cover them with antioxident. I use a product called NoAlox. Often available at Home Centers under Ideal or Gardner Bender brands. Electrical supply houses carry it too.
    The NoAlox is here. I solved the 4/0 4/0 2/0 termination problem at the inverter end by
    upgrading the inverter sub panel from a 100A to a 200A. This panel takes those wires
    directly, and will become the main feed at the inverter shed when the big wire is in place.

    Cannot do this at the other end, the 4/0 pair must be reduced enough into a 100A breaker.
    Bruce Roe

    S225boxDone.JPG
    Last edited by bcroe; 09-18-2019, 12:16 PM.

    Leave a comment:


  • bcroe
    replied
    Originally posted by foo1bar
    Wow.....
    I would inspect every inch of the length of that wire.
    Make sure there are no cuts in the insulation, no spots where it's been smashed, no kinks, etc.
    Make sure there's nothing else to make you think that the wire has been mistreated.
    Will do that inspection. Perhaps initially, and after a year, will do a leakage test to ground at
    operating voltage. Expectation is something like 10 micro amps, at 250V that amounts to
    0.022 KWH per year loss. Something entirely different would be bad.

    Will also check for warm connections, as before. And voltage drop. Bruce Roe

    Leave a comment:


  • foo1bar
    replied
    Originally posted by bcroe
    It came with some so called lugs on the end, but they are useless.
    Wow.....

    I would inspect every inch of the length of that wire.
    Make sure there are no cuts in the insulation, no spots where it's been smashed, no kinks, etc.
    Make sure there's nothing else to make you think that the wire has been mistreated.



    Leave a comment:


  • Mike90250
    replied
    Those lugs are unbelievable. Someone should go to jail for that. Pure and simple arson.

    Leave a comment:


  • bcroe
    replied
    Originally posted by foo1bar
    There are - I'm just not seeing that they're any cheaper than the screw-down splices like
    IT-250. (which are IMO easier to use - don't need to put layers of tape on them afterward).

    https://www.ecmweb.com/content/elect...kills-lost-art recommends
    2 layers of cambric tape (sticky side out on first layer so can easily remove tape without
    residue later if needed), 4 layers of rubber tape, and 2 layers of vinyl tape on split bolts.
    The aluminum direct burial wire arrived, 288 lb for 300 foot Triplex. Looks like
    most of the connections can go straight into my box terminals, 2 of the 6 will
    need to be reduced to 2 gauge copper to go into a 100A breaker. It came with
    some so called lugs on the end, but they are useless. I put some 4 Ga they are
    replacing in the pic for comparison.

    Probably a spring project, should get me 700 KWH a year that now burn up in
    adequate but inefficient, small wire. And avoid inverter HV trip. Bruce Roe

    Triplex1.JPGTriplex2.JPG

    Leave a comment:


  • bcroe
    replied
    Originally posted by azdave

    Maybe I'm misunderstanding your mod but isn't that just like using the "circulation" setting on the fan selection switch? My thermostat has that feature and it randomly turns only the blower on and off throughout the day to keep the air feeling fresh and the filters collecting dust. You aren't still running an old, round, gold-colored Honeywell with the mercury tilt switch are you?
    You are kidding, right? You are asking someone who daily drives a 1977 (police equipped)
    Oldsmobile, and measures KWH with a spinning disc meter. Technology proved reliable
    over decades.

    No I never have seen such a circulation thermostat. Can you set the run and pause times?
    Maybe the thermostat for my 2014 heat pump (deceased) actually could do that, but I would
    never trust that battery powered electronic marvel with keeping my pipes from freezing
    while I am away. That heat pump quit every 2 years, and I am NOT expecting much better
    from its wonder thermostat.

    When they put in the 2014 heat pump, I ran a new thermostat cable for it NEXT TO MY
    ROUND, GOLD COLORED, MERCURY SWITCH thermostat and told them not to touch
    it, just connect to the furnace blower terminals. SHE (who drives a Honda at 437,000 miles)
    is in complete agreement.

    AMANA.JPG

    Lately I have been considering removing the deceased 2014 and its thermostat, but
    SHE likes the inside/outside digital temp readout. Bruce Roe
    Last edited by bcroe; 08-28-2019, 10:43 PM.

    Leave a comment:


  • foo1bar
    replied
    Originally posted by bcroe
    Thanks, there are split bolts rated for 4/0 AL.
    There are - I'm just not seeing that they're any cheaper than the screw-down splices like IT-250. (which are IMO easier to use - don't need to put layers of tape on them afterward).

    https://www.ecmweb.com/content/elect...kills-lost-art recommends2 layers of cambric tape (sticky side out on first layer so can easily remove tape without residue later if needed), 4 layers of rubber tape, and 2 layers of vinyl tape on split bolts.

    Leave a comment:


  • azdave
    replied
    Originally posted by bcroe
    ...I have an electrostatic air filter I would like operated regularly. And a little air mixing
    between zones could be useful.
    Maybe I'm misunderstanding your mod but isn't that just like using the "circulation" setting on the fan selection switch? My thermostat has that feature and it randomly turns only the blower on and off throughout the day to keep the air feeling fresh and the filters collecting dust. You aren't still running an old, round, gold-colored Honeywell with the mercury tilt switch are you?

    Leave a comment:


  • bcroe
    replied
    Originally posted by foo1bar
    The POCO here uses something similar to what you see if you search for "Polaris IT-250". The version they used had 4 ports, and was more water-tight I think. But since you're going to be above ground (theirs was underground), and only doing a simple size change, not branching, the IT-250 or ISR-250 are probably more appropriate.

    If you go with a split bolt, I would make sure it's rated for aluminum. .
    Thanks, there are split bolts rated for 4/0 AL. With 2 different sizes above ground,
    I am leaning toward split bolt. Bruce Roe

    Leave a comment:


  • foo1bar
    replied
    Originally posted by bcroe
    These wires will not be used at anything like current capacity, the idea is oversize to control loss over a long run. Bruce Roe
    The POCO here uses something similar to what you see if you search for "Polaris IT-250". The version they used had 4 ports, and was more water-tight I think. But since you're going to be above ground (theirs was underground), and only doing a simple size change, not branching, the IT-250 or ISR-250 are probably more appropriate.

    I've also seen description in this forum of a crimped-on "pin terminal" to change sizes to fit into a breaker's input. So that might be an option - or a crimped on reducer to change sizes.

    If you go with a split bolt, I would make sure it's rated for aluminum.

    I don't know the other thing you have in the picture. But I think you're right to make sure you understand the proper way to use them before you use it.

    Leave a comment:


  • Ampster
    replied
    Originally posted by bcroe

    I see some things like this AMP B1-T which is rated to connect 4/0 aluminum to
    copper. Drive that wedge in I guess. There are also some big rated larger versions
    of this split bolt available. If these work, what is the prep process and anti oxident to
    use in the process?
    I would use a split bolt because I wouldn't trust a wedge to stay under various temperature changes. . If the copper and aluminum are fresh just cover them with antioxident. I use a product called NoAlox. Often available at Home Centers under Ideal or Gardner Bender brands. Electrical supply houses carry it too.

    Leave a comment:


  • bcroe
    replied
    Originally posted by bcroe
    direct burial 4/0-4/0-2/0 aluminum cable

    The question then is how to terminate it. Could it come up through conduit, to an
    outside box, then convert to smaller copper to the building?
    I see some things like this AMP B1-T which is rated to connect 4/0 aluminum to
    copper. Drive that wedge in I guess. There are also some big rated larger versions
    of this split bolt available. If these work, what is the prep process and anti oxident to
    use in the process?

    Soldering aluminum can be done, except it may not work for big wire. Comments?

    These wires will not be used at anything like current capacity, the idea is oversize
    to control loss over a long run. Bruce Roe